    Quote Originally Posted by SPYDERLK View Post
    The bigger the ground wire the closer the gen chassis will be to true house/earth ground. Still, either way on that short run were talking very small difference in potential possible even at full current capability. You could feel it with your tongue if you leave neutral bonded at gen because the ground would be effectively sharing the load with the neutral. Isolate neutral at the gen as youve described.
    larry
    Touch potential is not the only hazard. Think about what happens when the neutral and ground are not bonded at the generator and there is a ground fault.

  2. #22
    Bronze Member
    Join Date
    Apr 2012
    Posts
    67
    Location
    Southwest MO
    Tractor
    Kubota L4200-GST 4WD

    Default Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?

    Quote Originally Posted by JPCjr View Post
    Think about what happens when the neutral and ground are not bonded at the generator and there is a ground fault.
    The chassis of the generator will be connected to the house ground rod via a 21ft 6ga ground wire in my connection cord, and a 8ft run of 6ga wire from the inlet box to the breaker panel.
    Does this not function as a ground and wouldn't this be the path of least resistance if the generator had a wiring fault to ground?

    "Neutral floating at generator, neutral not switched at transfer panel. This is a correct configuration. Neutral for the entire system is bonded at the main service panel.
    There will be no ground conductor current. Only live lines are switched with a two pole transfer switch."


    In this case he's talking about using a two pole transfer switch and I'm going to use an interlock, the transfer switch isolates the generator from power lines as does the interlock in my breaker box.
    Electrically they seem the same to me as Neutral is bonded at the panel and Floating at the Generator in both.

    I understand the exposure if the generator is used away from the house but inserting the plug pictured in the first post into a 120v outlet will bond Neutral to Ground for those situations.
    Perhaps he and I are both wrong however, that's why I've asked the question.

  3. #23
    Super Member
    Join Date
    Feb 2006
    Posts
    8,915
    Location
    VA
    Tractor
    JD2010, Kubota3450,2550, Mahindra 7520 w FEL w Skid Steer QC w/Tilt Tatch, & BH, BX1500

    Default Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?

    Quote Originally Posted by JPCjr View Post
    Touch potential is not the only hazard. Think about what happens when the neutral and ground are not bonded at the generator and there is a ground fault.
    I am not sure of the terminology, but I think youre posing a case where a hot goes to ground due some load fault. In that case, and all cases where neutral is bonded to the gen chassis there would always be a small charge on the gen if it is not hard grounded. This is because of load sharing in the n/g leads via the neutral/ground bond at the sevice panel. ... Were the N not bonded at gen there would be no charge on its chassis when there was no fault. -- But in the case of a fault there would be charge on the chassis as much as 4x the potential that would exist in the case of the N/G gen bond addressed first. With 6ga wiring at 20 feet we have low numbers. 4 x ~0 = ~ 0 I dont see any danger short of conductor or hookup connection failure. These are within the purview of the installer-operator.
    larry
    Last edited by SPYDERLK; 09-14-2012 at 09:57 AM.
    This side of 40
    JD2010, Kubota L3450/FEL w SK QC, L2550 w FEL
    Mahindra 7520 [Pinky] /FEL w Skid Steer QC/w Tilt Tatch & BH, BX1500 [Mighty Mouse]
    IH37 Baler, CCM165 Drum Mower, JD Rake
    JD 127 bushog, Flail, SK Tilt Tatch , KK tiller, Rhino rear blade, Post driver, post auger, chipper, pallet fork, Grapple/Loader Buddy, Homemade Splitter/DC Welder

  4. #24
    Silver Member
    Join Date
    Apr 2011
    Posts
    194
    Location
    Marysville, OH
    Tractor
    JD 4300

    Default Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?

    Quote Originally Posted by SPYDERLK View Post
    I am not sure of the terminology, but I think youre posing a case where a hot goes to ground due some load fault. In that case, and all cases where neutral is bonded to the gen chassis there would always be a small charge on the gen if it is not hard grounded. This is because of load sharing in the n/g leads via the neutral/ground bond at the sevice panel. ... Were the N not bonded at gen there would be no charge on its chassis when there was no fault. -- But in the case of a fault there would be charge on the chassis as much as 4x the potential that would exist in the case of the N/G gen bond addressed first. With 6ga wiring at 20 feet we have low numbers. 4 x ~0 = ~ 0 I dont see any danger short of conductor or hookup connection failure. These are within the purview of the installer-operator.
    larry
    As an electrical engineer, but not willing to look it up, I believe that this is the most correct answer. There is a very slim chance of shock, but it is extremely minimal. I personally would not worry about it.

  5. #25
    Veteran Member
    Join Date
    Dec 2010
    Posts
    1,190
    Tractor
    Massey

    Default Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?

    Good debate. I see people debating the pros/cons that I wrote of in my inital post ( #2).

    Situation where JpC junior is correct: if you untie the genny ground from it's neutral at the genny, it doesn't matter how big the gauge ground cable to the house is. during a dwelling ground fault. The current that would run the alternate path of the ground wire in the dwelling has no connection to the gen head any more because you removed the tie. It's only path would be to cross to neutral at the service and run back on the neutral wire of your cord. That's not ideal.

    Where Spy is correct: If you leave the genny neutral tied to ground, 120 volt loads will be flowing current over the connection cable grounding wire during normal genny operation. This is against nec code, and is not ideal.
    Last edited by DarkBlack; 09-14-2012 at 05:40 PM.

  6. #26
    Silver Member
    Join Date
    Apr 2011
    Posts
    194
    Location
    Marysville, OH
    Tractor
    JD 4300

    Default Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?

    Quote Originally Posted by DarkBlack View Post
    Where Spy is correct: If you leave the genny neutral tied to ground, 120 volt loads will be flowing current over the connection cable grounding wire during normal genny operation. This is against nec code, and is not ideal.
    Yes, but if there was a 10 ohm resister in that ground, it would not be flowing any current (still not code). The only reason it would be flowing current is because there is equal resistance. To eliminate the current on the ground you could use a 3 conductor cable 2hots and neutral. And run a separate ground to a separate grounding rod. To me, it's needless.

  7. #27
    Silver Member Victory Pete's Avatar
    Join Date
    Dec 2011
    Posts
    163
    Location
    Rhode Island
    Tractor
    John Deere 2320 and X320

    Default Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?

    Quote Originally Posted by BRBurns View Post
    Yes, but if there was a 10 ohm resister in that ground, it would not be flowing any current (still not code). The only reason it would be flowing current is because there is equal resistance. To eliminate the current on the ground you could use a 3 conductor cable 2hots and neutral. And run a separate ground to a separate grounding rod. To me, it's needless.
    Current will divide itself up in proportion to the resistance of each parallel path.
    You still need the grounding conductor to bond to the service.

    VP

  8. #28
    Silver Member
    Join Date
    Apr 2011
    Posts
    194
    Location
    Marysville, OH
    Tractor
    JD 4300

    Default Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?

    Quote Originally Posted by Victory Pete View Post
    Current will divide itself up in proportion to the resistance of each parallel path.
    You still need the grounding conductor to bond to the service.

    VP
    I didn't mean that a ground was needless. Thanks for noticing my confusing wording. I d that for a temporary setup such as an emergency backup generator. A four conductor cable would be adequate in my book not worrying about separating the neutral from the gen frame. Use your own judgement though and determin wat risks you are willing to take to your own safety vs cost and time.

    Oh and the ten ohm comment was assuming a perfect theorectical zero ohm cable. I was meaning to emphasize that the ground would only be carrying current because the resistance is low, not because the circuitry required it to carry load.
    Last edited by BRBurns; 09-14-2012 at 09:27 PM. Reason: Clarification

  9. #29
    Bronze Member
    Join Date
    Jun 2007
    Posts
    63
    Location
    Pittsboro, NC
    Tractor
    Bobcat CT 450

    Default Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?

    Quote Originally Posted by stonypass View Post
    The chassis of the generator will be connected to the house ground rod via a 21ft 6ga ground wire in my connection cord, and a 8ft run of 6ga wire from the inlet box to the breaker panel.
    Does this not function as a ground and wouldn't this be the path of least resistance if the generator had a wiring fault to ground? .
    No, the grounding electrode (ground rod) has nothing to do with clearning a ground fault.

    Quote Originally Posted by stonypass View Post
    "Neutral floating at generator, neutral not switched at transfer panel. This is a correct configuration. Neutral for the entire system is bonded at the main service panel.
    There will be no ground conductor current. Only live lines are switched with a two pole transfer switch."


    In this case he's talking about using a two pole transfer switch and I'm going to use an interlock, the transfer switch isolates the generator from power lines as does the interlock in my breaker box.
    Electrically they seem the same to me as Neutral is bonded at the panel and Floating at the Generator in both.
    This is correct, but it's assuming that your generator was either manufacutred without the neutral and equipment ground bonded or that there is a removable bonding jumper. Your generator was not manufactured this way and should not be modified. The generator was designed, manufactured, and tested by a third party to ensure that it meets certain safety standards. Modifying the generator changes the system, voids the tests, is prohibited by code (see NEC 90.7, 110.2, and 110.3), and would not be recommended by anyone who understands the hazards involved.


    Quote Originally Posted by stonypass View Post
    I understand the exposure if the generator is used away from the house but inserting the plug pictured in the first post into a 120v outlet will bond Neutral to Ground for those situations.
    Perhaps he and I are both wrong however, that's why I've asked the question.
    The purpose of the neutral to equipment ground bond is to conduct fault current. If you have a fault between the ungrounded (hot) and equipment ground, then all of the faul current must flow through the plug/jumper in the photo. I would not trust that and would not be surprised if the circuit breaker never opened during a fault, as the resistance of this configuration is much higher than a solid connection. That is a fire hazard. Also, if there is a bad connection in the plug/jumper and there was a fault, the chasis of the generator would be energized and you could be shocked or electrocuted. The same is true if you separate the neutral and equipment ground and connect the generator to your premises wiring system the way you describe. A bad connection at the plug will result in shock/electrocution hazard and/or fire hazard if you have a fault between the hot and equipment ground.

  10. #30
    Bronze Member
    Join Date
    Jun 2007
    Posts
    63
    Location
    Pittsboro, NC
    Tractor
    Bobcat CT 450

    Default Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?

    Quote Originally Posted by stonypass View Post
    The chassis of the generator will be connected to the house ground rod via a 21ft 6ga ground wire in my connection cord, and a 8ft run of 6ga wire from the inlet box to the breaker panel.
    Does this not function as a ground and wouldn't this be the path of least resistance if the generator had a wiring fault to ground? .
    No, the grounding electrode (ground rod) has nothing to do with clearning a ground fault.

    Quote Originally Posted by stonypass View Post
    "Neutral floating at generator, neutral not switched at transfer panel. This is a correct configuration. Neutral for the entire system is bonded at the main service panel.
    There will be no ground conductor current. Only live lines are switched with a two pole transfer switch."


    In this case he's talking about using a two pole transfer switch and I'm going to use an interlock, the transfer switch isolates the generator from power lines as does the interlock in my breaker box.
    Electrically they seem the same to me as Neutral is bonded at the panel and Floating at the Generator in both.
    This is correct, but it's assuming that your generator was either manufacutred without the neutral and equipment ground bonded or that there is a removable bonding jumper. Your generator was not manufactured this way and should not be modified. The generator was designed, manufactured, and tested by a third party to ensure that it meets certain safety standards. Modifying the generator changes the system, voids the tests, is prohibited by code (see NEC 90.7, 110.2, and 110.3), and would not be recommended by anyone who understands the hazards involved.


    Quote Originally Posted by stonypass View Post
    I understand the exposure if the generator is used away from the house but inserting the plug pictured in the first post into a 120v outlet will bond Neutral to Ground for those situations.
    Perhaps he and I are both wrong however, that's why I've asked the question.
    The purpose of the neutral to equipment ground bond is to conduct fault current. If you have a fault between the ungrounded (hot) and equipment ground, then all of the faul current must flow through the plug/jumper in the photo. I would not trust that and would not be surprised if the circuit breaker never opened during a fault, as the resistance of this configuration is much higher than a solid connection. That is a fire hazard. Also, if there is a bad connection in the plug/jumper and there was a fault, the chasis of the generator would be energized and you could be shocked or electrocuted. The same is true if you separate the neutral and equipment ground and connect the generator to your premises wiring system the way you describe. A bad connection at the plug will result in shock/electrocution hazard and/or fire hazard if you have a fault between the hot and equipment ground.

Page 3 of 7 FirstFirst 123456 ... LastLast

Similar Threads

  1. Floating neutral generator
    By joshuabardwell in forum Rural Living
    Replies: 21
    Last Post: 09-01-2012, 11:46 AM
  2. Deere 430 Dies when PTO engaged or out of Neutral
    By agildawg in forum Parts/Repairs
    Replies: 0
    Last Post: 07-02-2012, 06:14 PM
  3. 3-Point Hitch PTO won't go into neutral
    By dreece1952 in forum Yanmar
    Replies: 11
    Last Post: 08-09-2010, 09:06 AM
  4. foton 254 pto falling in neutral.
    By domains in forum Chinese Tractors
    Replies: 13
    Last Post: 02-25-2009, 09:30 AM
  5. PTO shaft turning in neutral
    By tnbowhunter in forum Yanmar
    Replies: 7
    Last Post: 02-24-2008, 10:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
© 2014 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.