Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
The chassis of the generator will be connected to the house ground rod via a 21ft 6ga ground wire in my connection cord, and a 8ft run of 6ga wire from the inlet box to the breaker panel.
Does this not function as a ground and wouldn't this be the path of least resistance if the generator had a wiring fault to ground?
"Neutral floating at generator, neutral not switched at transfer panel. This is a correct configuration. Neutral for the entire system is bonded at the main service panel.
There will be no ground conductor current. Only live lines are switched with a two pole transfer switch."
In this case he's talking about using a two pole transfer switch and I'm going to use an interlock, the transfer switch isolates the generator from power lines as does the interlock in my breaker box.
Electrically they seem the same to me as Neutral is bonded at the panel and Floating at the Generator in both.
I understand the exposure if the generator is used away from the house but inserting the plug pictured in the first post into a 120v outlet will bond Neutral to Ground for those situations.
Perhaps he and I are both wrong however, that's why I've asked the question.
-
09-14-2012, 09:33 AM #23Super Member
- Join Date
- Feb 2006
- Posts
- 6,768
- Location
- VA
- Tractor
- JD2010, Kubota3450,2550, Mahindra 7520 w FEL w Skid Steer QC w/Tilt Tatch, & BH, BX1500
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
I am not sure of the terminology, but I think youre posing a case where a hot goes to ground due some load fault. In that case, and all cases where neutral is bonded to the gen chassis there would always be a small charge on the gen if it is not hard grounded. This is because of load sharing in the n/g leads via the neutral/ground bond at the sevice panel. ... Were the N not bonded at gen there would be no charge on its chassis when there was no fault. -- But in the case of a fault there would be charge on the chassis as much as 4x the potential that would exist in the case of the N/G gen bond addressed first. With 6ga wiring at 20 feet we have low numbers. 4 x ~0 = ~ 0 I dont see any danger short of conductor or hookup connection failure. These are within the purview of the installer-operator.
larryLast edited by SPYDERLK; 09-14-2012 at 09:57 AM.
This side of 40
JD2010, Kubota L3450/FEL w SK QC, L2550 w FEL
Mahindra 7520 [Pinky] /FEL w Skid Steer QC/w Tilt Tatch & BH, BX1500 [Mighty Mouse]
IH37 Baler, Hesston Haybine, JD Rake
Bushog, Flail,
SK Tilt Tatch
, KK tiller, Rhino rear blade, Post driver, post auger, chipper, pallet fork, Grapple/Loader Buddy, Homemade Splitter/DC Welder
-
09-14-2012, 05:23 PM #24Silver Member
- Join Date
- Apr 2011
- Posts
- 179
- Location
- Marysville, OH
- Tractor
- JD 4300
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
-
09-14-2012, 05:24 PM #25Gold Member
- Join Date
- Dec 2010
- Posts
- 278
- Tractor
- Massey
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
Good debate. I see people debating the pros/cons that I wrote of in my inital post ( #2).
Situation where JpC junior is correct: if you untie the genny ground from it's neutral at the genny, it doesn't matter how big the gauge ground cable to the house is. during a dwelling ground fault. The current that would run the alternate path of the ground wire in the dwelling has no connection to the gen head any more because you removed the tie. It's only path would be to cross to neutral at the service and run back on the neutral wire of your cord. That's not ideal.
Where Spy is correct: If you leave the genny neutral tied to ground, 120 volt loads will be flowing current over the connection cable grounding wire during normal genny operation. This is against nec code, and is not ideal.Last edited by DarkBlack; 09-14-2012 at 05:40 PM.
-
09-14-2012, 08:03 PM #26Silver Member
- Join Date
- Apr 2011
- Posts
- 179
- Location
- Marysville, OH
- Tractor
- JD 4300
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
Yes, but if there was a 10 ohm resister in that ground, it would not be flowing any current (still not code). The only reason it would be flowing current is because there is equal resistance. To eliminate the current on the ground you could use a 3 conductor cable 2hots and neutral. And run a separate ground to a separate grounding rod. To me, it's needless.
-
09-14-2012, 08:09 PM #27
-
09-14-2012, 09:23 PM #28Silver Member
- Join Date
- Apr 2011
- Posts
- 179
- Location
- Marysville, OH
- Tractor
- JD 4300
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
I didn't mean that a ground was needless. Thanks for noticing my confusing wording. I d that for a temporary setup such as an emergency backup generator. A four conductor cable would be adequate in my book not worrying about separating the neutral from the gen frame. Use your own judgement though and determin wat risks you are willing to take to your own safety vs cost and time.
Oh and the ten ohm comment was assuming a perfect theorectical zero ohm cable. I was meaning to emphasize that the ground would only be carrying current because the resistance is low, not because the circuitry required it to carry load.Last edited by BRBurns; 09-14-2012 at 09:27 PM. Reason: Clarification
-
09-15-2012, 03:26 AM #29Bronze Member
- Join Date
- Jun 2007
- Posts
- 63
- Location
- Pittsboro, NC
- Tractor
- Bobcat CT 450
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
No, the grounding electrode (ground rod) has nothing to do with clearning a ground fault.
This is correct, but it's assuming that your generator was either manufacutred without the neutral and equipment ground bonded or that there is a removable bonding jumper. Your generator was not manufactured this way and should not be modified. The generator was designed, manufactured, and tested by a third party to ensure that it meets certain safety standards. Modifying the generator changes the system, voids the tests, is prohibited by code (see NEC 90.7, 110.2, and 110.3), and would not be recommended by anyone who understands the hazards involved.
The purpose of the neutral to equipment ground bond is to conduct fault current. If you have a fault between the ungrounded (hot) and equipment ground, then all of the faul current must flow through the plug/jumper in the photo. I would not trust that and would not be surprised if the circuit breaker never opened during a fault, as the resistance of this configuration is much higher than a solid connection. That is a fire hazard. Also, if there is a bad connection in the plug/jumper and there was a fault, the chasis of the generator would be energized and you could be shocked or electrocuted. The same is true if you separate the neutral and equipment ground and connect the generator to your premises wiring system the way you describe. A bad connection at the plug will result in shock/electrocution hazard and/or fire hazard if you have a fault between the hot and equipment ground.
-
09-15-2012, 03:26 AM #30Bronze Member
- Join Date
- Jun 2007
- Posts
- 63
- Location
- Pittsboro, NC
- Tractor
- Bobcat CT 450
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
No, the grounding electrode (ground rod) has nothing to do with clearning a ground fault.
This is correct, but it's assuming that your generator was either manufacutred without the neutral and equipment ground bonded or that there is a removable bonding jumper. Your generator was not manufactured this way and should not be modified. The generator was designed, manufactured, and tested by a third party to ensure that it meets certain safety standards. Modifying the generator changes the system, voids the tests, is prohibited by code (see NEC 90.7, 110.2, and 110.3), and would not be recommended by anyone who understands the hazards involved.
The purpose of the neutral to equipment ground bond is to conduct fault current. If you have a fault between the ungrounded (hot) and equipment ground, then all of the faul current must flow through the plug/jumper in the photo. I would not trust that and would not be surprised if the circuit breaker never opened during a fault, as the resistance of this configuration is much higher than a solid connection. That is a fire hazard. Also, if there is a bad connection in the plug/jumper and there was a fault, the chasis of the generator would be energized and you could be shocked or electrocuted. The same is true if you separate the neutral and equipment ground and connect the generator to your premises wiring system the way you describe. A bad connection at the plug will result in shock/electrocution hazard and/or fire hazard if you have a fault between the hot and equipment ground.
Similar Threads
-
Floating neutral generator
By joshuabardwell in forum Rural LivingReplies: 21Last Post: 09-01-2012, 11:46 AM -
Deere 430 Dies when PTO engaged or out of Neutral
By agildawg in forum Parts/RepairsReplies: 0Last Post: 07-02-2012, 06:14 PM -
3-Point Hitch PTO won't go into neutral
By dreece1952 in forum YanmarReplies: 11Last Post: 08-09-2010, 09:06 AM -
foton 254 pto falling in neutral.
By domains in forum Chinese TractorsReplies: 13Last Post: 02-25-2009, 09:30 AM -
PTO shaft turning in neutral
By tnbowhunter in forum YanmarReplies: 7Last Post: 02-24-2008, 10:39 PM



Reply With Quote