Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
Floating neutral eh? Not really genny related, but it happened, so I'll tell it.
Ten years ago the power company were changing poles and in so doing rerouted
the above ground feed (2 insulated conductors around an uninsulated carrier conductor.
The reroute was through a thicket of cedar trees.
Two years ago the uninsulated conductor had completely disconnected by a constant
rub that a cedar tree had managed to rug off. Now that is a floating neutral.
The floating neutral voltage to either 120v was totally dependent on the loads
I measured it at 180v-60v. No 240 volt appliance were affected, but it blew th snot out
of the surge protector and fuse of the old built in above stove microwave, and a stereo receiver.
The ballast on the floresent fixture in the laundry room got smoked also..
The nuke runs 'till this day, sans surge protection.
-
09-22-2012, 05:19 AM #64
-
09-30-2012, 10:03 AM #65Bronze Member
- Join Date
- Apr 2012
- Posts
- 51
- Location
- Southwest MO
- Tractor
- Kubota L4200-GST
PTO Generator Now Wired and Tested
After much consideration, I modified the generator to have a Floating Neutral and made up a plug that Bonds Neutral to Ground for standalone usage.
A clamp-on meter from HF was used to test current draw on all my high usage items so I would know what combinations I am able to use with the genset at the same time.
I also mounted a remote 120v outlet on the front of my TSC carry-all for a Kill-A-Watt that can be seen from the tractor seat (or from the ground) for properly setting frequency.
An outlet tester shows proper configuration at 120v outlets in the home when the genset is connected and running, and the generator shows the same in standalone mode when using the bonding plug.
Yesterday I did a full test of the Generator and ran everything in the house, setting the frequency at 62hz with no load and then testing first lights, high usage items then electronics.
My high usage items are a 1.5hp 650ft well pump, electric dryer, range/stove, and a 4 ton central A/C unit.
The generator had no problems with any of these and will easily run the well pump with any other single high usage item along with lights, refrigerator/freezer, TV/Satellite and PC/Internet.
The Kubota has plenty of power with 37 PTO hp and I never saw lights flicker, the rpm vary much or the frequency go below 60hz under the highest loads.
This setup may not suit everyone but will provide emergency power to anywhere in my home and barn which is what I was after.
Thanks to all who responded, your advice was appreciated.
I would like to add a pilot light to the breaker box to tell me when grid power has been restored, if someone can point me to a link for a suitable Neon or LED light and holder that can be hooked to one side of my input power I would appreciate it.Last edited by stonypass; 09-30-2012 at 10:25 AM.
Kubota L4200-GST 4WD, LA680 FEL, 6' Mower, 6' Box Blade, 7' Angle Blade, 12kw 3pt PTO Generator
-
09-30-2012, 11:31 AM #66Platinum Member
- Join Date
- Sep 2008
- Posts
- 614
- Location
- Gainesville, Fl area Gator Country
- Tractor
- New Holland TC40D HST 4WD FEL/BH
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
Yes, I really have three panels.
1) This is the main panel where the meter is on the pole. It used to feed the MH we had install and had a 150 AMP Breaker feeding the MH. When we upgraded to a new MH, the old home was still in place as we were still living in it. This required that we set the new house in a different spot behind the old house. Since we were still going to be using the same power pole and septic system, the new house was positioned at a right angle to the old house just behind the old house and septic tank.
The new house location made it more then 30' from the pole and, according to local code, this required we have a disconnect at the end of the new house. Since the existing power service was wired for 250 AMP service no changes needed to be made to the service pole I just had to install a 200 AMP breaker to feed the new house.
2) We have a panel at the end of the house. This panel was required to be mounted on its own support since local code would not allow it to be mounted to the actual MH. It has its own ground rod. In this panel there is a breaker for the MH, one for the 5 ton A/C-heat pump and another for the heat strips in the A/C unit. There is also a breaker for a 120v receptacle at the pole.
3) There is the panel that came in the house. It has a 200 AMP main and the breakers for the rest of the house. We were required to also install a ground rod for this panel and have that connected to the frame of the house.
Panels number 2 and 3 have un-bonded neutrals as per local code.Mahindra 4525 2WD
Massey Ferguson 240
New Holland TC40D HST 4WD
NewHolland 16LA FEL
Woods BH 70-X Sub-frame Backhoe
Troybuilt Super Bronco w/42" mower
Husqvarna DRT 900 Tiller
Ariens 6.5 HP String Mower
Husqvarna HU625WT String Mower
3 point hitch attachments:
single plow, double plow, 5' & 6' deck mower, tiller, 2 cultivators, planter, fertilizer spreader, disk set, sprayer, and a few homemade attachments
30 acres, 15 acres, 5 acres
-
10-01-2012, 10:40 AM #67Member
- Join Date
- Aug 2012
- Posts
- 41
- Location
- Thousand islands
- Tractor
- 1320 NH
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
Going to show us the "plug" for bonding Stoney? IMHO the only safe way to do this is with welding cable,
one piece, bolted connections at each end. Safety trumps convenience every time. I'd settle with a welding cable extension, the connectors are solid. Put on some kind of lock with a key that's on your
keyring. There should never be a way of that being disconnected without you knowing. Give **** a place to happen and sooner or later, it will.
-
10-01-2012, 11:42 AM #68Bronze Member
- Join Date
- Apr 2012
- Posts
- 51
- Location
- Southwest MO
- Tractor
- Kubota L4200-GST
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
Currently mine looks just like the one below, except I used a 20amp 120v capable plug with a 10ga jumper.
May make up one using a 50amp plug with a 6ga jumper though, since to connect the genset to the house it would have to be removed as my cord uses that receptacle.Kubota L4200-GST 4WD, LA680 FEL, 6' Mower, 6' Box Blade, 7' Angle Blade, 12kw 3pt PTO Generator
-
10-01-2012, 04:17 PM #69Platinum Member
- Join Date
- Oct 2008
- Posts
- 860
- Location
- Mid. Coast Maine
- Tractor
- 7610 hst
Re: Should I change my PTO generator from Bonded Neutral to Floating Neutral?
-
10-01-2012, 05:06 PM #70Platinum Member
- Join Date
- Oct 2008
- Posts
- 860
- Location
- Mid. Coast Maine
- Tractor
- 7610 hst
Similar Threads
-
Floating neutral generator
By joshuabardwell in forum Rural LivingReplies: 21Last Post: 09-01-2012, 11:46 AM -
Deere 430 Dies when PTO engaged or out of Neutral
By agildawg in forum Parts/RepairsReplies: 0Last Post: 07-02-2012, 06:14 PM -
3-Point Hitch PTO won't go into neutral
By dreece1952 in forum YanmarReplies: 11Last Post: 08-09-2010, 09:06 AM -
foton 254 pto falling in neutral.
By domains in forum Chinese TractorsReplies: 13Last Post: 02-25-2009, 09:30 AM -
PTO shaft turning in neutral
By tnbowhunter in forum YanmarReplies: 7Last Post: 02-24-2008, 10:39 PM



Reply With Quote