Old 08-12-2002, 11:21 PM   #1 (permalink)
Silver Member
 
Join Date: Jul 2000
Location: Eastern Kentucky
Posts: 190
Default wire size for welder

My Uncle gave me a lincoln AC stick welder. My brother inlaw dragged in some 8/3 SO wire. I thought about running about 5 ft. from the breaker box in the barn using the 8/3 and installing a plug and using the remaining 50 ft as a movable line with a male and a female end. That way I could have the same set up and move to the shop and other barn when I needed to.
Question one: Is 8/3 so large enough for the 50 amp welder?
Question two: What size breaker would be the best ?

Thanks in advance,
Patrick
poorboy is offline   Reply With Quote
Old 08-13-2002, 12:24 AM   #2 (permalink)
New Member
 
Join Date: Dec 1969
Posts: 0
Default Re: wire size for welder

Unless you are going to be running the welder at max capacity, the 8/3 will work out fine.
DONOTDELETE is offline   Reply With Quote
Old 08-13-2002, 05:21 PM   #3 (permalink)
Silver Member
 
Join Date: Jul 2000
Location: Eastern Kentucky
Posts: 190
Default Re: wire size for welder

Franz thanks for the reply. I wasn't sure about the setup myself so I thought I would ask. I'm still not sure about the breaker size though. Should I use a double 30, 40 or a 50?

Patrick
poorboy is offline   Reply With Quote
Old 08-13-2002, 06:33 PM   #4 (permalink)
 
Join Date: Mar 2002
Location: Frozen North, Michigan
Posts: 116
Default Re: wire size for welder

A double 50 amp breaker works for me.
I use a 10/2 cable 25" long as an extension cord for both the Lincoln 225 and the Millermatic 250, but not at the same time.
justractors is offline   Reply With Quote
Old 08-13-2002, 09:25 PM   #5 (permalink)
Silver Member
 
Join Date: Jul 2000
Location: Eastern Kentucky
Posts: 190
Default Re: wire size for welder

Justractors, I guess thats what I'll go with. Thanks for the info!

Patrick
poorboy is offline   Reply With Quote
Old 08-22-2002, 03:09 PM   #6 (permalink)
 
Join Date: Jun 2001
Location: South Central Oklahoma
Posts: 1,390
Default Re: wire size for welder

I bought a used extension cord about a hundred feet long with 4 conductors. I think it was #6 wire but I don't recall for sure. I cut it into two pieces. One is about 30 something feet long and the other 60 something feet long. I wired up 250 volt 50 amp plugs and sockets. I can run my 50 amp 240 volt welder on either or both (in series) and weld a hundred feet from a dryer type outlet anywhere one can be found. I don't recall the gauge but it does not heat up and the welder works fine at full power. I included 2 duplex 120 volt 20 amp outlets in the box I put the socket/outlet to have power for my 120 volt welder or for grinder, lights, fan, whatever... I paralleled two of the conductors on one leg of the 240 to reduce overall line loss a bit because I wanted to get something out of lugging its weight.

In my shop bld I have a 25 foot coil of two conductor + gnd #4 with a dryer outlet on the end. This lets me have some mobility before I have to drag out the BIG extension cord. I have this circuit on a dual 50 amp breaker.

Happy welding!

Patrick
patrickg is offline   Reply With Quote
Old 08-22-2002, 09:11 PM   #7 (permalink)
Silver Member
 
Join Date: Jul 2000
Location: Eastern Kentucky
Posts: 190
Default Re: wire size for welder

I did end up going with a double fifty and 5 ft of the eight 3 and a female. I also had the guy run 12/2 of a 20 amp breaker in the box that my fencer was connected to. We went into the box and back out into the fencer outlet that was clamped there. This left me with enough wire to attach it to it's own breaker if the ground fault outlet the fencer was plugged into caused any problem in the future. I used all the spare electrical parts I had laying around. This was because the electrician was a good friend that I conned into coming over on a saturday night for a freebee. But my wife has trouble getting excatly what I send her after, she does well though most times and it did save me from a trip into town. I haven't got back to that barn though since I've been finishing the lot fence and baling some second cutting this week after school. Patrick sounds like a good setup for some future projects, have fun.

Patrick
poorboy is offline   Reply With Quote
Old 08-28-2002, 06:25 AM   #8 (permalink)
Bronze Member
 
Join Date: Jun 2002
Location: Rozet, Wyoming
Posts: 53
Default Re: wire size for welder

8 gauge wire has a max. load rating of 40 amps, so you need to use a 40 amp breaker. That should work fine for you.
KWentling is offline   Reply With Quote
Old 08-28-2002, 08:23 AM   #9 (permalink)
ddl
 
Join Date: Apr 2000
Location: Peculiar, MO
Posts: 349
Default Re: wire size for welder

what you mean is that you can use this wire up to 40 amps, you can use less current and fuse lighter, say 30 amp if that is the load. You can not fuse let say for 41 amps. But you can underfuse to match the load. The real question is why would you select wire much larger than neede if you mdid not have it on hand.

Dan L
ddl is offline   Reply With Quote
Old 08-28-2002, 06:39 PM   #10 (permalink)
Gold Member
 
Join Date: Jul 2001
Posts: 432
Default Re: wire size for welder

As stated by others, 8/3 and a 40 amp breaker should be fine - you can go to 6 gauge and 50 amps if your unit requires such, but most don't. BTW, what is the line going to your barn/garage? I had a friend who put in great wiring - 6 gauge - for his new welder, and then discovered the line from his house, a couple of hundred feet away, to his (added on by a previous owner) garage fuse box was 8 gauge (inside a conduit coming up from the floor, so he couldn't easily ascertain such).
cisco is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off
Forum Jump


All times are GMT -4. The time now is 06:28 AM.


HOME DISCUSSIONS PHOTOS REVIEWS CLASSIFIEDS DEALERS STORE
About TractorByNet.com | Terms of Service | Advertise | © 2008 TractorByNet.com