    First off, I know the standard rule that it takes two horsepower per kilowatt of power.
    However, I have a freind with a small (13/11 hp) tractor that wants to adapt a like new generator head that the gasoline engine tossed a rod. Since it was gasoline, I am going to assume that it was a 3600 rpm generator head (straight coupled). He wants to adapt this to his to his pto, which is three speed. Since he would probably use the fastest pto speed, and gear it up(sheaves and belts) to somewhere close to 3600 at close to full throttle(no tach), we are trying to figure out what the available horsepower is going to be, at the generator head.
    Since the diesel engine is rated at 13, and pto is rated at 11, what is normal for the faster speeds to be calculated at, or is it the same, due to horsepower being figured at a rate of speed? Can anybody give a rough estimate what the final horsepower is going to be once it enters the generator head? (or how many kilowatts it may use of the available 8KW?)
    before it over taxes the tractor?
    Thanks in advance,
    David from jax
    A serious accident is one that money won't fix.

  2. #2
    Elite Member dex3361's Avatar
    Join Date
    Aug 2008
    Posts
    3,568
    Location
    N. of Charleston WV
    Tractor
    Kubota L4400-1 HST,FEL, 3x3 remotes, TNT. BX1500 54 mmm

    Default Re: generator horse power requirements

    Still going to be in the 6.5KW (+-)range on a steady basis and it would probably surge the full 8 KW because of the rotating mass of the tractor.
    Randall



    1Timothy Chapter 2:
    3 For this is good and acceptable in the sight of God our Saviour;
    4 Who will have all men to be saved, and to come unto the knowledge of the truth.
    5 For there is one God, and one mediator between God and men, the man Christ Jesus.
    From: The HOLY BIBLE

  3. #3
    Veteran Member
    Join Date
    Aug 2007
    Posts
    1,279
    Location
    Mid-Coast Maine

    Default Re: generator horse power requirements

    Quote Originally Posted by sandman2234 View Post
    Since he would probably use the fastest pto speed, and gear it up(sheaves and belts) to somewhere close to 3600 at close to full throttle(no tach)
    You are going to need to get as close to 3600 rpm for the generator as possible so you have 60Hz on your incoming power. Motors will be happier and your plug in clocks will be more accurate.
    Jim

    - '01 Husqvarna W4814- 48" walk behind lawn mower.
    - '04 John Deere Z-Trac 727A- 54" ZTR
    - '13 Kioti DK40 HST - KL401 loader, DK40 72" QA bucket, LK3054 60" QA bucket, toothbar for 60" bucket, dual rear remotes, 7ft 6 way rear blade, 78" ETA Box Blade, Woods BH-90x backhoe, loaded rear tires, Kioti Canopy.

  4. #4
    Gold Member Mighty Dodge's Avatar
    Join Date
    Jan 2007
    Posts
    491
    Location
    The Hereford Zone, MD
    Tractor
    JD 4200

    Default Re: generator horse power requirements

    As IXLR8 said you'll need to be as close to 3600 as possible. You're lights don't care but motors and electronics do. I use a Lincoln G8000 when the power goes out. Everything in the house works (not all at once) but I have a new washer and dryer with electronic controls that won't even turn on. I guess the power's not clean enough for them.

    M.D.
    2001 JD 4200, 420 loader, HF Quick Hitch, bucket boom, back blade, boom pole, forks, carry-all, moldboard plow, middle buster, receiver hitch, post hole digger.

    My Pics
    http://www.tractorbynet.com/photos/s...0/ppuser/33421

  5. #5
    Elite Member Skyco's Avatar
    Join Date
    Jul 2007
    Posts
    2,718
    Location
    SC/NC

    Default Re: generator horse power requirements

    Quote Originally Posted by Mighty Dodge View Post
    As IXLR8 said you'll need to be as close to 3600 as possible. You're lights don't care but motors and electronics do. I use a Lincoln G8000 when the power goes out. Everything in the house works (not all at once) but I have a new washer and dryer with electronic controls that won't even turn on. I guess the power's not clean enough for them.

    M.D.
    Sometimes electronics are a pain- I bought an inexpensive Mr Coffee drip machine for my camp. Dang thing won't work on my invertor for that first cup of coffee without going out to start the generator. Ripped out the electronics and put in a toggle switch
    Oddly the LCD TV and DirecTV receiver work just fine on the invertor, those are the things I thought I'd have trouble with....

  6. #6
    Silver Member
    Join Date
    Mar 2010
    Posts
    193

    Default Re: generator horse power requirements

    Quote Originally Posted by sandman2234 View Post
    First off, I know the standard rule that it takes two horsepower per kilowatt of power.
    However, I have a freind with a small (13/11 hp) tractor that wants to adapt a like new generator head that the gasoline engine tossed a rod. Since it was gasoline, I am going to assume that it was a 3600 rpm generator head (straight coupled). He wants to adapt this to his to his pto, which is three speed. Since he would probably use the fastest pto speed, and gear it up(sheaves and belts) to somewhere close to 3600 at close to full throttle(no tach), we are trying to figure out what the available horsepower is going to be, at the generator head.
    Since the diesel engine is rated at 13, and pto is rated at 11, what is normal for the faster speeds to be calculated at, or is it the same, due to horsepower being figured at a rate of speed? Can anybody give a rough estimate what the final horsepower is going to be once it enters the generator head? (or how many kilowatts it may use of the available 8KW?)
    before it over taxes the tractor?
    Thanks in advance,
    David from jax

    I think I would go with the larger head like you describe, but be aware that you may not have the horsepower to make it run. I think you can get away with 6500 watts continous and 8kw peak, but you'll likely have only 9 hp to run it. Plan on setting it up for around 3800 RPM, and throttle back slightly to get the right speed. The right speed will likely be around 3675-3700. I think most generators are set up for around 62/63 hz at no load.

  7. #7
    Elite Member Redneck in training's Avatar
    Join Date
    Nov 2008
    Posts
    2,736
    Location
    South Central Iowa
    Tractor
    TYM 330 HST with FEL

    Default Re: generator horse power requirements

    Tractor HP is measured at top governor speed. PTO speed is selected at maximum torque of particular engine. Typically the engine will have the lowest specific fuel concumption (g/kW or gal/HP) at PTO speed. So if you run the tractor faster than rated PTO speed it will have more PTO power. The trade off is higher fuel consumption per kw produced.

  8. #8
    Elite Member jonyyuma's Avatar
    Join Date
    Sep 2010
    Posts
    2,972
    Location
    35 miles North of Memphis,TN
    Tractor
    kubota L3000dt, ford 8n1952

    Default Re: generator horse power requirements

    Quote Originally Posted by Redneck in training View Post
    Tractor HP is measured at top governor speed. PTO speed is selected at maximum torque of particular engine. Typically the engine will have the lowest specific fuel concumption (g/kW or gal/HP) at PTO speed. So if you run the tractor faster than rated PTO speed it will have more PTO power. The trade off is higher fuel consumption per kw produced.
    Okay,So now what happens when you increase load, the gen slows down and there goes your hertz? If load falls then it goes over, pto speed will be constant since you don't have throttle attached to it.I have seen units made for the pto, but the load has to be constant to work, Right?Plus electronics hate surges, and can instantly go belly up. Jy.
    Okay, Legal disclaimer: Old but not senile, definitely do not have the answer to everything!

  9. #9
    Elite Member Redneck in training's Avatar
    Join Date
    Nov 2008
    Posts
    2,736
    Location
    South Central Iowa
    Tractor
    TYM 330 HST with FEL

    Default Re: generator horse power requirements

    Quote Originally Posted by jonyyuma View Post
    Okay,So now what happens when you increase load, the gen slows down and there goes your hertz? If load falls then it goes over, pto speed will be constant since you don't have throttle attached to it.I have seen units made for the pto, but the load has to be constant to work, Right?Plus electronics hate surges, and can instantly go belly up. Jy.
    That was the most obvious question nobody asked yet. Does your tractor have a speed governor? Most tractors do have it. If it does have it the governor will adjust power to keep the rpm constant.

  10. #10
    Platinum Member jas67's Avatar
    Join Date
    May 2008
    Posts
    985
    Location
    Central PA
    Tractor
    Kubota B7610 + Kubota G1800-S

    Default Re: generator horse power requirements

    Quote Originally Posted by Skyco View Post
    Sometimes electronics are a pain- I bought an inexpensive Mr Coffee drip machine for my camp. Dang thing won't work on my invertor for that first cup of coffee without going out to start the generator. Ripped out the electronics and put in a toggle switch
    Oddly the LCD TV and DirecTV receiver work just fine on the invertor, those are the things I thought I'd have trouble with....
    Get a pure-sine inverter. I have a 1KW pure-sine inverter in my camper, and it runs everything except the microwave and the air conditioner. Not only do electronics like it better, but AC induction motors, such as those in normal household fans like it much better too. With my old MSW (modified sine wave) inverter, the fans ran slower, hotter, and made a loud 60 Hz hum. I don't think they would have lasted too long running that way.

    The DirectTV box probably runs on the inverter, because it likely has better power conditioning circuitry than the cheap coffee maker.
    '05 B7610 w/ LA352 FEL
    Everything Attachments Pin-on Pallet Forks, home-made FEL quick attach to swap between these forks and the bucket, Dual rear remotes, CCM Top-N-Tilt, Woods SB60 snowblower, 66" United box blade, 60" back blade (cheapo, old and rusty), 60" KK rake, Woods PHD w/ 9" auger, Yanmar RS1303 3pt tiller, Kubota Ballast box (came with the tractor), Farm Force Carry All.
    '9? G1800S, 48" MMM. 70's Troy Bilt Horse tiller with new 6.5HP briggs engine.

    The means justify the ends.

Page 1 of 2 12 LastLast

Similar Threads

  1. JD 950 Power Steering/Hydaulics Problem
    By DJCohenour in forum Hydraulics
    Replies: 17
    Last Post: 04-19-2009, 07:47 PM
  2. wind power
    By deereman64 in forum Related Topics
    Replies: 56
    Last Post: 02-18-2009, 03:36 PM
  3. Which Tractor to Buy
    By captkel in forum Buying/Pricing/Comparisons
    Replies: 46
    Last Post: 07-25-2005, 04:57 PM
  4. DC to AC power inverter to run electic tools?
    By Bob_Skurka in forum Customization
    Replies: 66
    Last Post: 11-07-2004, 12:03 AM
  5. Goodbye Kubota, Hello Power Trac
    By MChalkley in forum Power Trac
    Replies: 107
    Last Post: 05-20-2002, 04:52 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
© 2014 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.