12-27-2012, 11:19 AM #11Gold Member
- Join Date
- Dec 2007
- Posts
- 437
Oh and ours was also required on every outlet. Dad went back and forth with the inspector about that and a few other issues that dad said was inaccurate as far as some national code he was required to follow. There reply was their way or they wouldn't sign off on it.
-
12-27-2012, 11:52 AM #12Silver Member
- Join Date
- Nov 2007
- Posts
- 117
- Location
- Mobile, Al
- Tractor
- 1974 MF135
Re: Shop electrical wiring....
I get that same feeling from this inspector..... so i have decided to cadweld. I found some one shot cadwleds and will be using them. I plan to run from my #4 copper wire to the first ground rod, from there to the second ground rod, and then to the service neutral.
I am now guessing that the service neutral he is speaking of is in the actual meter can? and not in the outside breaker panel. Or do i have that wrong as well?
-
12-27-2012, 01:23 PM #13Veteran Member
- Join Date
- May 2012
- Posts
- 2,259
- Location
- Knoxville, TN
- Tractor
- Bobcat CT225
-
12-27-2012, 02:03 PM #14Veteran Member
- Join Date
- Dec 2003
- Posts
- 1,696
- Location
- NC
- Tractor
- Kubota Grand L3830
-
12-27-2012, 02:20 PM #15Silver Member
- Join Date
- Nov 2007
- Posts
- 117
- Location
- Mobile, Al
- Tractor
- 1974 MF135
Re: Shop electrical wiring....
My shop will have its own meter. So im speaking of the meter and remote service panel that is next to the meter.
-
12-27-2012, 08:38 PM #16Silver Member
- Join Date
- Jan 2006
- Posts
- 166
Re: Shop electrical wiring....
You are correct, that the ground from the rods and breaker panel are connected in the meter box. The ground has to be run from the meter service entrance box uninterrupted to the grounding rods.
-
12-27-2012, 09:57 PM #17Silver Member
- Join Date
- Nov 2007
- Posts
- 117
- Location
- Mobile, Al
- Tractor
- 1974 MF135
-
12-28-2012, 08:07 PM #18Silver Member
- Join Date
- Nov 2007
- Posts
- 117
- Location
- Mobile, Al
- Tractor
- 1974 MF135
Re: Shop electrical wiring....
And while im thinking of it........ how come its code to attach a #4 copper wire to rebar over a 3 foot span with split bolts, but its against code to splice the copper wire with anything that is reversible? The codes says only splices that are irreversible and UL listed for grounding and bonding can be used. I have yet to see anything that a BFH, sawzall, or torch couldnt reverse. **** a pair of cutting pliers can easily "reverse" and splice thats to code on #4 copper wire. The insensibleness of this is what really gets me......
-
12-28-2012, 08:59 PM #19
Re: Shop electrical wiring....
currently own
2011 Kioti DK45SE HST CAB tractor/loader, Jimna 6" - 3 point wood chipper, 60" JD Brush Hog, JD 60" Rototiller, 3 point post hole digger with hydraulic assist, 3 point spring tooth rake, Fimco 55 gallon weed sprayer with 12 foot boom, 3 point hydraulic wood splitter (home built)
Quick Attach 79" loader mount snowblower & rear powerpack
Quick Attach 84" Snow Blade
Quick Attach 42" pallet forks
-
12-28-2012, 09:25 PM #20Silver Member
- Join Date
- Nov 2007
- Posts
- 117
- Location
- Mobile, Al
- Tractor
- 1974 MF135
Similar Threads
-
LS Electrical Wiring Question
By Forfar in forum LS TractorsReplies: 11Last Post: 08-18-2012, 09:35 PM -
Looking for electrical wiring.
By trygta in forum Parts/RepairsReplies: 2Last Post: 04-06-2011, 03:31 PM -
Electrical wiring box
By armyof1 in forum All Other BrandsReplies: 1Last Post: 04-27-2004, 06:40 PM -
Electrical wiring question
By Gary_in_Indiana in forum Rural LivingReplies: 17Last Post: 06-20-2002, 09:15 PM -
Home wiring (non-electrical)
By shade2u2 in forum Rural LivingReplies: 59Last Post: 03-08-2002, 01:54 PM


Reply With Quote