RonR said:
I have a 22HP tractor and could get a generator matched for that size. I'm sure I'd have to run the tractor at PTO speed to maintain the voltage.
Would it work to buy a smaller generator, which would be belt driven to increase the RPMs, but then I could run the tractor at half throttle.
I'm thinking the generator won't put that much load on the tractor, and if I have to run it very long, I'd just as soon run it at 1800RPM instead of wide open.
Anyone tried this? Your thoughts? THANKS.
Ron
Consider that one HP is about 750 Watts (not exact but close enough for back of the envelope stuff). Actually, considering the various real world losses and inefficiencies don't count on getting much more that 500 Watts out of each developed HP of the tractor engine.
I used the term "developed HP" instead of rated HP for a reason. You may have a 22HP engine in your tractor, but it only develops 22HP at a particular RPM. Slowing the engine below that RPM reduces the maximum HP it will develop. Likewise, running it above that RPM also reduces the maximum HP it will develop. The actual maximum HP developed at any given RPM depends on the characteristic HP vs RPM curve for your particular engine. But, whatever it might be, that is the maximum HP developed at the RPM you want to run the tractor and is all that is available to run the generator
With that said, you should be able to run the tractor at whatever engine RPM you desire if you:
1) Size the generator at no more than about 500 Watts Continuous per "developed HP" at the RPM you want to run.
2) Figure the actual PTO RPM as the ratio of 540 X (Running RPM/Engine RPM for 540 PTO RPM)
3) Fabricate/purchase some sort of power transmission to increase the actual PTO RPM to provide 540 RPM to the input shaft of the generator. Be sure to size the transmission to handle the "developed HP" (with the appropriate safety factor) from 1) above.
Now, about the generator not being much of a load on the tractor. I'll agree that the tractor frame, wheel bearings, etc aren't stressed by the generator load. However, it that generator is requiring 22HP from the tractor to satisfy the electrical load on the generator, the tractor engine is working just as hard, under no less load, than if it were developing 22HP to drag a plow through the ground or a rotary cutter through the brush.
OK, bottom line. Yes, you can engineer a solution to do what you want to do.
Should you do it? Probably not.
My opinion on what you should do?
Figure the electrical load based on what circuits you want to power and the electrical load and duty cycle on those circuits paying particular attention to the size of any motors fed by those circuits. Electric motors drink a lot of amperage until they come up to design speed. Take the total wattage and motor starting requirements and look for a generator that satisfies that load. If you need more than about an 11 to 12.5KVA generator, you have too small a tractor and need to scale back on what circuits you expect to power.
When you've identified a generator size that adequately supports the electical load and doesn't overload the tractor, hook it up direct to the PTO and run the tractor at the 540 PTO speed. The tractor was designed to run for hours on end at that speed. You really aren't going to be doing it a favor by running those hours in an "off design point" state.
Just my opinion, take it for whatever you think it's worth.