Good points. I'll look around for a small pto unit. See what the cost is.
I was thinking in terms of a direct mount using a type of "bell housing" much the same as an engine is attached to a generator to make a genset. Tractors aren't designed for this type of setup so it would require some design and fabrication for sure. A flex coupling such as Lovejoy would probably be needed if perfect alignment of the two PTO shafts wasn't possible.You really don't want that type of connection. Attachments move around vibrate and bounce up and down, you want a flexible link to prevent that from being transmitted to the gearbox.
There must be a reason why a PTO generator can't be run direct mounted to the tractor PTO but if would make a cleaner setup by eliminating the PTO shaft.
There must be a reason why a PTO generator can't be run direct mounted to the tractor PTO but if would make a cleaner setup by eliminating the PTO shaft.
For calculating power needs, I suppose I need to look at the actual motors and such, not just the amperage of the circuits, right?
Yes but there's more. Look on the motor to see the power it uses (as a rough estimate you can use 746 watts = 1 HP and divide down; for example 1/3 hp motor will be about .33 x 746 or about 250 watts). You also have to take into account starting load on motors. For this take the motor power and multiply it by 3, so our 1/3 HP motor requires about 750 watts to start.