gobbler,
i'm no expert....but in general, the fuse is sized to protect the wiring not the load device. for example a # 14 wire can handle about 15 amps...so you'd want a 15 amp fuse on that wire even if the load is only 7.0 amps. this way, if there is a short, the fuse will blow before the wire heats up enough to burn up !!
for your application, i'd run a # 12 wire ( bigger is better !! ) and start with a 10 amp fuse. if the fuse blows, i'd step up to a 15 amp. you're still safe with that wire size up to 20 amps. slow blow fuses are good for motor loads to help tolerate the high inrush amperage when the motor starts.
good luck !!