    Default PTO Generator surge limits

    So I've read through most of the PTO Generator threads, but I'm still a bit unclear how to determine surge/startup power limits for a given tractor/pto generator combination. As I understand it, the 2 PTO HP/KW limit applies mainly to continuous power, but what is the maximum surge/startup wattage available?

    I'm mainly looking into the Tiger Power units, and my tractor is a MF 1532 with 26.5 PTO HP. So using the 2 HP rule of thumb, I should be able to generate up to 13.25 KW of continuous power.

    Looking at the Tiger Power brochure at the 10, 15, and 20 KW units, the 10 KW unit has a surge limit of 25 kVA, the 15 KW unit has a surge limit of 45 kVA, and the 20 KW unit has a surge limit of 60 kVA.

    With the 10 KW, continuous power w/ my tractor will be 10 KW, but will my starting limit be 13.25 KW, or would it be higher (25 kVA would be somewhere between 15 and 25 KW depending on the power factor of the loads).

    If I step up to the 15 KW unit, then my continuous power availability would be 13.25 KW -- will the surge limit be any higher than with the 10 KW unit? How much higher?

    Finally, with the 20 KW unit, again continuous power will still be stuck at 13.25 KW due to tractor HP limitations. Will surge limits be identical to the limit of the 15 KW unit?

    Also, once you hit 20 KW, you've got the option of an 1800 RPM PTO generator (at 10 or 15 KW the only available units are 3600 RPM ones). Will the heavier 1800 watt model make any practical differences in usable power (with only 26.5 HP available), or is the only gain from the 1800 RPM generator an increased service life?

    Of course there's a big price range across these options. From the prices posted at messicks.com, package prices (including pto shaft, trailer, power cord) are $2250 for the 10 KW, $3065 for 15 KW, $3575 for 20 KW at 3600 RPM, and 3950 for 20 KW at 1800 RPM?

    Thanks,
    Scott

  2. #2
    Elite Member dex3361's Avatar
    Join Date
    Aug 2008
    Posts
    3,568
    Location
    N. of Charleston WV
    Tractor
    Kubota L4400-1 HST,FEL, 3x3 remotes, TNT. BX1500 54 mmm

    Default Re: PTO Generator surge limits

    Welcome to TBN
    You have done your homework and have found out it can be confusing. I would go with at least the 15KW generator. This will not allow you to overload your generator. The bigger units would have the same results. The surge capabilities are hard to call but are higher than you might think. A tractor has a lot of rotating mass that will ride past a quick surge. Starting a motor is a short duration surge. An AC motor can pull 6 times the normal full load current(amps).
    Randall



    1Timothy Chapter 2:
    3 For this is good and acceptable in the sight of God our Saviour;
    4 Who will have all men to be saved, and to come unto the knowledge of the truth.
    5 For there is one God, and one mediator between God and men, the man Christ Jesus.
    From: The HOLY BIBLE

  3. #3
    New Member
    Join Date
    Oct 2009
    Posts
    6

    Default Re: PTO Generator surge limits

    Here's a related question -- how much of a difference does getting a 4-pole 1800 RPM PTO generator vs. 2-pole 3600 RPM? With standalone generators it makes a big difference on engine life, as the engine will be spinning at half the speed in the 1800 RPM case (at least for direct drive generators), but for the PTO generator, the tractor engine will be at the same normal PTO speed, so the only difference will be the speed the alternator is turning at. Is the effect mainly one of service life, or will the 4-pole generator provide more stable power or with greater surge capability (although in the 15-20 KW generator case, the tractor HP will be the limiting factor on continuous power)?

  4. #4
    Platinum Member Craig Clayton's Avatar
    Join Date
    May 2009
    Posts
    863
    Location
    Uxbridge Ontario Canada
    Tractor
    L2250 Kubota

    Default Re: PTO Generator surge limits

    What are you trying to power up, surge current is in rush current. Different loads have different currents. Motors across the the line up to 6x FLA. Resistance loads equal to FLA at unity power factor. Moror soft starts are now getting to be affordable. I finished wiring a VFD on Friday.
    Craig Clayton

  5. #5
    Platinum Member atgreene's Avatar
    Join Date
    Aug 2007
    Posts
    849
    Location
    Sebago, Maine
    Tractor
    2005 TB135 Excavator with Thumb, Quick Attach System, Ripper tooth, 3' Hydrauic Tilt Clean-up Bucket, Skeleton Bucket, 1986 Kubota 4150 with Loader and Quick Attach with Woods Forks, JD B, 1963 IH 504

    Default Re: PTO Generator surge limits

    You are much better off at 1800 rpm vs. 3600. The noise alone is reason enough to go with the slower tunring unit. Good luck.
    1986 Kubota 4150 w QA
    2005 Takeuchi 135 excavator
    2005 GMC 5500 10' Boss V
    1963 Oshkosh 1967
    2013 GMC 3500 6.0 w 9-2 Boss V Fisher poly Sander.
    IH 504, JD B, Ford 2n, Gehl 1475 Round Baler, JD 640 rake, Vermeer 2500 Bale Wrapper, Zetor 185 Drum Mower, New Idea 217 manure Spreader, Kuhn 4 star tedder, Farmi 501 winch.
    Local 740 Portland ME
    20 Scottish Highland Beef Cattle, 3 Herefords, 3 Goats, 2 Alpacas, 2 Llama, 72 chickens, and lots of maple trees.
    Facebook: Phillip View Farm

  6. #6
    Epic Contributor Soundguy's Avatar
    Join Date
    Mar 2002
    Posts
    48,358
    Location
    Central florida
    Tractor
    ym1700, NH7610S, Ford 8N, 2N, NAA, 660, 850 x2, 541, 950, 941D, 951, 2000, 3000, 4000, 4600, 5000, 740, IH 'C' 'H', CUB, John Deere 'B', allis 'G', case VAC

    Default Re: PTO Generator surge limits

    the 1800 unit will take less of a phase hit if rpm drops under a load or surge.

    the 3600 is usually cheaper.. etc.

    I'd go for the 15kw unit as well.. you have automatic built in thermal protection for the genny in that you don't have enough pto hp to overwork it..

    soundguy

  7. #7
    New Member
    Join Date
    Oct 2009
    Posts
    6

    Default Re: PTO Generator surge limits

    Quote Originally Posted by Soundguy View Post
    the 1800 unit will take less of a phase hit if rpm drops under a load or surge.

    the 3600 is usually cheaper.. etc.

    I'd go for the 15kw unit as well.. you have automatic built in thermal protection for the genny in that you don't have enough pto hp to overwork it..

    soundguy
    It's too bad the 1800 rpm series from Tiger Power starts at 20kw. The only other sub-20kw PTO generator that turns at 1800 RPM I've seen listed online is Baumalight QC12, but that's 12 kw rather than 15, and at around $6K, it's $2K more expensive than the Tiger Power 20KW 1800RPM generator.

    I'm not sure how much of the noise savings of an 1800 RPM unit applies w/ PTO generators as it does with standalone units, since the engine RPMs are unchanged -- how much of the noise from a tractor+pto generator at full load comes from the alternator vs. from the tractor engine.

  8. #8
    Epic Contributor Soundguy's Avatar
    Join Date
    Mar 2002
    Posts
    48,358
    Location
    Central florida
    Tractor
    ym1700, NH7610S, Ford 8N, 2N, NAA, 660, 850 x2, 541, 950, 941D, 951, 2000, 3000, 4000, 4600, 5000, 740, IH 'C' 'H', CUB, John Deere 'B', allis 'G', case VAC

    Default Re: PTO Generator surge limits

    engine nose from the tractor is the same, as it is turning to make pto rpm.

    only noise difference would be from the pto step up gearbox. on a 3600 rpm unit, the gearbox is stepping up more from the tractor 540 pto.. thus more gear noise.

    personally.. compaired to tractor noise.. the gearbox noise just ain't much.

    i have a 3600rpm northern 12.5kw genny I run behind a 34hp ford gasser from 1955.. or a lil later diesel.. at 30' i can only hear the engine.. not the ptogengearbox..

    soundguy

    Quote Originally Posted by ScottS View Post
    It's too bad the 1800 rpm series from Tiger Power starts at 20kw. The only other sub-20kw PTO generator that turns at 1800 RPM I've seen listed online is Baumalight QC12, but that's 12 kw rather than 15, and at around $6K, it's $2K more expensive than the Tiger Power 20KW 1800RPM generator.

    I'm not sure how much of the noise savings of an 1800 RPM unit applies w/ PTO generators as it does with standalone units, since the engine RPMs are unchanged -- how much of the noise from a tractor+pto generator at full load comes from the alternator vs. from the tractor engine.

  9. #9
    Veteran Member Steve_Miller's Avatar
    Join Date
    Mar 2004
    Posts
    1,242
    Location
    Nova Scotia, Canada
    Tractor
    2006 Kioti CK30HST

    Default Re: PTO Generator surge limits

    I only have one question, what are you trying to start that will need more than a 10KW surge? Just curious.

    Steve

  10. #10
    Super Member
    Join Date
    Feb 2006
    Posts
    8,493
    Location
    VA
    Tractor
    JD2010, Kubota3450,2550, Mahindra 7520 w FEL w Skid Steer QC w/Tilt Tatch, & BH, BX1500

    Default Re: PTO Generator surge limits

    Quote Originally Posted by Steve_Miller View Post
    I only have one question, what are you trying to start that will need more than a 10KW surge? Just curious.

    Steve
    I took a peak current measurement on a 5HP compressor motor. ... 134Amps at startup. Thats about 29kW. The voltage output of the gen takes a real dive in the short term. Til the motor comes to speed . Runnng current was in the mid 20s. A 10 kW gen starts it fine tho - a quick, rather deep, brownout.
    larry
    This side of 40
    JD2010, Kubota L3450/FEL w SK QC, L2550 w FEL
    Mahindra 7520 [Pinky] /FEL w Skid Steer QC/w Tilt Tatch & BH, BX1500 [Mighty Mouse]
    IH37 Baler, CCM165 Drum Mower, JD Rake
    JD 127 bushog, Flail, SK Tilt Tatch , KK tiller, Rhino rear blade, Post driver, post auger, chipper, pallet fork, Grapple/Loader Buddy, Homemade Splitter/DC Welder

Page 1 of 2 12 LastLast

Similar Threads

  1. 4610 PTO stopped working
    By tallyho8 in forum New Holland Owning/Operating
    Replies: 18
    Last Post: 09-26-2008, 08:56 PM
  2. Ford 1715 PTO Trouble. Help please!!
    By freddvm in forum New Holland Owning/Operating
    Replies: 4
    Last Post: 09-07-2008, 03:08 PM
  3. Mahindra 575 PTO shaft
    By Tim Stuart in forum Mahindra Owning/Operating
    Replies: 1
    Last Post: 01-14-2008, 02:56 PM
  4. Mowing TC40A PTO engagement with a rotary mower
    By mundamanu in forum New Holland Owning/Operating
    Replies: 9
    Last Post: 05-31-2007, 08:46 AM
  5. PTO, way too often is undervalued in a purchase
    By Keith_B in forum Buying/Pricing/Comparisons
    Replies: 51
    Last Post: 02-21-2007, 04:16 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
© 2014 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.