    Default Re: Generator Transfer switch connection choices
    Quote Originally Posted by daybreak1998 View Post
    If you look over the choices I have listed, if your main panel has a option for the interlock kit, that really is going to be the easiest and cheapest solution.
    Yeah. I have checked my main service panel, and I have no breaker locations free. But I hear you can get piggyback breakers to address that problem. My current generator is 5000W continuous, so I would need something like 20 amps at 240v or 40 amps at 120. If I understand correctly a pair of 20 amp 120v breakers backfed from the generator with an interlock would do the trick. Is that right?
  2. #12
    Gold Member Todd727's Avatar
    Join Date
    Apr 2012
    Posts
    378
    Holly Springs, MS
    CaseIH Maxxum 115
    Quote Originally Posted by joshuabardwell View Post
    Hmm... so if codes are involved, it wouldn't be possible to hook up a portable generator and then only activate circuits as needed? But if I install an interlock setup with a backfeed breaker, then that's fine? What's the logic there?
    Codes are always involved.
  3. #13
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    218
    Northern Virginia
    Lots of John Deere tractors
    Howdy,
    "The interlock"
    The interlock makes it so only 1 breaker can be on. The main panel breaker, or the generator breaker. So, you turn off the main 200amp breaker, slide the metal interlock, and now you can turn on the generator breaker.
    Generator Transfer switch connection choices-2011-10-20_13-12-11_726-a click on the picture to see larger, then click again to zoom in.
    Your panel needs to have a interlock kit for it. It usually needs the 2 top right spaces for the generator breakers. If your panel is full, a lot of times you can get half breakers to help make some room.
    Later Mike ~~~
    JD green here
    tractors and implements
  4. #14
    Platinum Member Steave's Avatar
    Join Date
    Mar 2012
    Posts
    844
    Taylorsville, GA
    3000 Ford 66' 260A International Backhoe, Belarus 250AS
    Some codes don't seem logical sometimes. I would guess their thinking would be once the transfer switch was thrown if the generator isn't large enough to carry what ever load it needs it would cause a problem with the generator struggling to keep up.
    Sometimes it don't make sense to me. When the power goes off things like a clothes dryer which pulls a lot of power does not start back up automatically, but a water heater that was heating at the time of power lost will try to start up when power is reapplied. If your generator is too small to restart your load and you forgot to turn off the breakers there's the potential problem.
    Not all Local codes call for the permanent ginny but most do.
    I've got a cutting torch and a welder sooo YEAH it'll fit!!
  5. #15
    Join Date
    Mar 2012
    Posts
    844
    Taylorsville, GA
    Use a 30 amp double pole breaker for the backfed breaker. Using a double pole if you get a fault on a 120 volt circuit it will trip all the power from the ginny. Much safer. Same price.
  6. #16
    Join Date
    Oct 2008
    Posts
    1,184
    Mid. Coast Maine
    7610 hst
    What if you do overload your generator,, It has it's own breaker to protect it's self .. As for the DPDT switch after the meter,, you need a breaker or fuses before it.. so at that point it could be DIY...
  7. #17
    Platinum Member TerryR's Avatar
    Join Date
    Jan 2009
    Posts
    567
    Boone, NC
    JD 870
    I don't understand why I can't just put a 200A DPDT break-before-make switch in between the meter and the main panel, and have the generator plug into that.
    We did exactly that when we had our house built 15 years ago, though our generator is hard-wired into the switch. The inspector didn't raise any objection, so I assume it passed local code then at least. No meter collar was required because the switch is between the meter and the main panel.
    One downside is you then have no indication of when utility power is restored (unless you have nearby neighbors you can see), so we had an LED indicator wired into the utility side to tell us.
    This system works great for us, but it doesn't include automatic transfer (nor is our generator auto-start) so it doesn't work while were are away.
    Terry
  8. #18
    Veteran Member sparc's Avatar
    Join Date
    Oct 2011
    Posts
    1,086
    NJ
    JD 4410, NH TC-25, Bobcat M610, JD X534, Dig-It Model 158, JD Ztrak 737. 6X4 Gator
    Here's another possibility for a whole house transfer switch.
    Honda HP2S Portable Power Systems: Universal Transfer Switch
  9. #19
    Elite Member
    Join Date
    May 2012
    Posts
    2,972
    Knoxville, TN
    Bobcat CT225
    Default
    Quote Originally Posted by Steave
    I just don't see why the NEC would care if I overload and damage my own generator. I must be missing something.
  10. #20
    Join Date
    Mar 2008
    Posts
    599
    I wired in the ProTran 10 circuit model. Works great... no problems. Got to use it for 4 hours a couple weeks ago when the power went out. The Honda 5500 fired up instantly, never missed a beat. Great setup.
Similar Threads
  1. generator whole house transfer switch
    By automech in forum Rural Living
    Last Post: 02-14-2014, 10:45 PM
  2. generator/transfer switch connection
    By geneP in forum Rural Living
    Last Post: 10-30-2009, 02:48 AM
  3. Generator Generator transfer switch wiring diagram
    By Barneyhunts in forum Attachments
    Last Post: 02-29-2008, 11:24 PM
  4. Wiring a Home Generator Transfer Switch
    By RobS in forum Rural Living
    Last Post: 01-27-2008, 08:58 PM
  5. Neal's Generator/Transfer setup
    By ns_in_tex in forum Build-It Yourself
    Last Post: 10-11-2004, 08:34 AM
Posting Permissions
  • You may not post replies
  • You may not edit your posts
© 2017 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.