    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by joshuabardwell View Post
    I just don't see why the NEC would care if I overload and damage my own generator. I must be missing something.
    Howdy,
    They only care about a automatic overload. Circuit breakers are meant to trip when there is a fault/overload. You do not try to run a 30amp ac unit on a 20 amp breaker?

    The generator has a circuit breaker itself. If you load up to much, it should trip.
    Later Mike ~~~
    JD green here
    tractors and implements

  2. #22
    Elite Member
    Join Date
    May 2012
    Posts
    2,966
    Location
    Knoxville, TN
    Tractor
    Bobcat CT225

    Default Re: Generator Transfer switch connection choices

    I'm sorry if I'm being obtuse, and I understand that the answer may be, "Codes are nonsensical sometimes," but I still don't get it. If I install a backfeed breaker with an interlock, then I can use a portable generator to power my whole house by switching individual breakers on and off. But if I install a DPDT switch between the main panel and the meter, my generator must be permanently installed? How does that make sense?

  3. #23
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    163
    Location
    Northern Virginia
    Tractor
    Lots of John Deere tractors

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by joshuabardwell View Post
    I'm sorry if I'm being obtuse, and I understand that the answer may be, "Codes are nonsensical sometimes," but I still don't get it. If I install a backfeed breaker with an interlock, then I can use a portable generator to power my whole house by switching individual breakers on and off. But if I install a DPDT switch between the main panel and the meter, my generator must be permanently installed? How does that make sense?
    Howdy,
    NO, you can use whatever size generator you want.

    Now, if you use a fully automatic transfer switch, the genset is suppose to be big enough to run everything. I mean everything. That is total nonsense. I might run a lot of things, but I am not trying to run a upper and lower electric oven, and electric cooktop, and everything else. (kinda like thanksgiving, cooking going on everywhere)

    But, a transfer switch is pricey, whether it is manual, or automatic. The interlock kit results in the same thing. Safe from backfeeding utility lines. But, the interlock kit, is way cheaper.
    manual transfer switch $800, permit $$, electrician $$, utility pull meter $$

    interlock kit $149, dual pole breaker sized for genset $50, wire sized for amperage to outdoor connection $50, a generator inlet kit $70, and of course your cord to hook from generator to inlet.

    The nice thing is, you use your panel to shut off major power items. For instance, all electric house, turn off water heater, turn off well, turn off oven, turn off stove top, turn off electric heat. you can leave all the lights on, just don't walk around the house and turn every single one of them on. Lites themselves really do not take a lot. Its the big stuff. Then you decide what you want to run while on generator power. Just do not overload your genset. (the generator breaker will trip if overloaded) If you want to shower, turn on the well pump, ok, water pressure is up, ok, turn off well pump, now turn on water heater, after a while, water is hot, now turn off water heater, turn on well pump, take a shower.

    overall concept, is safety. NO BACKFEEDING POWER LINES.
    Later Mike ~~~
    JD green here
    tractors and implements

  4. #24
    Super Star Member RoyJackson's Avatar
    Join Date
    Nov 2001
    Posts
    18,456
    Location
    Bethel, Vermont
    Tractor
    John Deere 4400 MFWD, Deere 855D UTV and assorted implements

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by Steave View Post
    ... but a water heater that was heating at the time of power lost will try to start up when power is reapplied. If your generator is too small to restart your load and you forgot to turn off the breakers there's the potential problem.


    That's a point and if you have an extended power outage, you'll have to consider this kind of thing. As, or more, importantly is to ensure your family knows and understands the procedure/requirements.
    I can tell you now, if I was on the road and we lost power...my wife would just check into the nearest motel that had power... Hopefully, your family will be more responsive and responsible.
    Roy Jackson

    "Any government that does not trust its citizens with firearms is either a tyranny, or planning to become one."
    -Joseph P. Martino

  5. #25
    Silver Member
    Join Date
    Mar 2012
    Posts
    213
    Location
    Taylorsville, GA
    Tractor
    3000 Ford 66' 260A International Backhoe

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by joshuabardwell View Post
    I just don't see why the NEC would care if I overload and damage my own generator. I must be missing something.
    I was just guessing as to their reasoning. I'm not real sure why its required in some areas. It may be a local thing. In every municipality I've worked in there's something always a little different. All towns have to at least meet the requirements of the NEC but they can add their little quirps to it and to get your power turned on you have to abide by them. If you can diy without the need for inspectors (and can do it safely) then I would do it. Around here if you need the power turned off by the power company they will come out and turn it off no problem. After you do your work and call them to turn it back on is when they tell you they can't turn it on without an inspection.
    I've got a cutting torch and a welder sooo YEAH it'll fit!!

  6. #26
    Veteran Member
    Join Date
    Jul 2004
    Posts
    1,628
    Location
    Bancroft, Ontario
    Tractor
    JD4300

    Default Re: Generator Transfer switch connection choices

    Around here, (country) they will turn you off at the street once a year so you can do tree trimming. What ELSE you do is up to you.....

  7. #27
    Silver Member
    Join Date
    Mar 2012
    Posts
    213
    Location
    Taylorsville, GA
    Tractor
    3000 Ford 66' 260A International Backhoe

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by pat32rf View Post
    Around here, (country) they will turn you off at the street once a year so you can do tree trimming. What ELSE you do is up to you.....
    Now that would be the time to get ur done!!

    During storm damage here they are kinda lenient because they get to far behind if they go by the book.
    I've got a cutting torch and a welder sooo YEAH it'll fit!!

  8. #28
    Elite Member newbury's Avatar
    Join Date
    Jan 2009
    Posts
    4,610
    Location
    From Vt, in Va, retiring to MS
    Tractor
    Kubota's - B7610, M4700

    Default Re: Generator Transfer switch connection choices

    In both Northern Virginia and Northeast Mississippi I've had the electric company out in the past few months, they'll drop the power so you can do tree trimming and come back later and rehook it up for free. Just give them a few days notice when they are not busy.
    My rides - '95 Kubota M4700 w/ PEC, LA1001 FEL :'07 B7610, LA352 FEL, Bush Hog SBX 48 box blade, '09 Woods BH70-X w/ 16" bucket and thumb, 3pt pallet forks, Dale Phillips PHD, Jinma 8" chipper, 2 Piranha's, Winco 12KW PTO generator, Howse plow, 5' KK tiller with a 2002 7.3L Ford F350 CC DRW 4x4 and '07 18' Hudson HSE Deluxe trailer - 5 Ton to haul it all

  9. #29
    Silver Member
    Join Date
    Mar 2012
    Posts
    213
    Location
    Taylorsville, GA
    Tractor
    3000 Ford 66' 260A International Backhoe

    Default Re: Generator Transfer switch connection choices

    [QUOTE=daybreak1998;2916641]Howdy,
    Generator transfer switch connection choices.
    For safety of yourself, family, equipment and utility workers, properly connect generators.
    Some methods can be do it yourself to a certain point. Electricians and your Utility will be involved as well.

    Thanks for letting us bounce off your thread. If I were to hook up a genset semi permanent to the house I'd probably go with the interlock system. Even if somebody knows how to cut on and off breakers as needed it only takes a slip of the mine to BOOM! I've been called out to check wiring after power was thrown back onto a ginny, it usually just trips the breaker but... I also seen one at a large plant blow up a $750 breaker in a GE Switchgear.
    I've got a cutting torch and a welder sooo YEAH it'll fit!!

  10. #30
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    163
    Location
    Northern Virginia
    Tractor
    Lots of John Deere tractors

    Default Re: Generator Transfer switch connection choices

    Howdy,
    After looking around at interlock switches... if you have a mainline type panel from either GE or Square D, then the interlock kit is priced around $50 at home depot. Put in the dual pole breaker sized for your genset, proper size wire, and a inlet plug.
    Later Mike ~~~
    JD green here
    tractors and implements

Page 3 of 8 FirstFirst 123456 ... LastLast

Similar Threads

  1. generator whole house transfer switch
    By automech in forum Rural Living
    Replies: 32
    Last Post: 02-14-2014, 09:45 PM
  2. generator/transfer switch connection
    By geneP in forum Rural Living
    Replies: 13
    Last Post: 10-30-2009, 01:48 AM
  3. Generator Generator transfer switch wiring diagram
    By Barneyhunts in forum Attachments
    Replies: 46
    Last Post: 02-29-2008, 10:24 PM
  4. Wiring a Home Generator Transfer Switch
    By RobS in forum Rural Living
    Replies: 38
    Last Post: 01-27-2008, 07:58 PM
  5. Neal's Generator/Transfer setup
    By ns_in_tex in forum Build-It Yourself
    Replies: 43
    Last Post: 10-11-2004, 07:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
© 2014 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.