    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by daybreak1998 View Post
    Howdy,
    After looking around at interlock switches... if you have a mainline type panel from either GE or Square D, then the interlock kit is priced around $50 at home depot. Put in the dual pole breaker sized for your genset, proper size wire, and a inlet plug.
    Link
    Search Results for interlock*at The Home Depot
    appear to be very panel specific.
    My rides - '95 Kubota M4700 w/ PEC, LA1001 FEL :'07 B7610, LA352 FEL, Bush Hog SBX 48 box blade, '09 Woods BH70-X w/ 16" bucket and thumb, 3pt pallet forks, Dale Phillips PHD, Jinma 8" chipper, Winco 12KW PTO generator, Howse plow, 5' KK tiller with a 2002 7.3L Ford F350 CC DRW 4x4 and '07 18' Hudson HSE Deluxe trailer - 5 Ton to haul it all

  2. #32
    Platinum Member
    Join Date
    Sep 2004
    Posts
    583
    Location
    south/central Va.
    Tractor
    Deutz Fahr Agrofarm 100, Stoll loader, bucket, forks & root grapple

    Default Re: Generator Transfer switch connection choices

    I use a PTO generator rated at 50 amps. I got a mechanical interlock for the service panel. It's 200 amp and GE brand. I put that in back in 1983. Couldn't find the slide interlock for that style as they have changed over the years. I got measurements and kept looking at different interlocks till I found one that was close enough to use. Had to mill it in the slots to extend the length a little and cut the tab that blocks the generator breaker to make it fit. It works good.
    Charolais

  3. #33
    Bronze Member
    Join Date
    Apr 2012
    Posts
    55
    Location
    Southwest MO
    Tractor
    Kubota L4200-GST

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by Charolais View Post
    It's 200 amp and GE brand. I put that in back in 1983. Couldn't find the slide interlock for that style as they have changed over the years. I got measurements and kept looking at different interlocks till I found one that was close enough to use. Had to mill it in the slots to extend the length a little and cut the tab that blocks the generator breaker to make it fit.
    Does your panel have a vertical Main Breaker?
    Our house was built in 1994 and we have a GE PowerMark Plus 200amp 30 space load center.

    I'm looking for an interlock to fit it but the GE model THQLLX1 appears to be for PowerMark Gold models.
    Generator Interlock Kit from GE | The Home Depot - Model THQLLX1

    If yours is similar to mine could you post pic's and a link to which interlock you started with?

    Thanks.
    Attached Thumbnails Attached Thumbnails -p1010242-jpg   -p1010244-jpg  
    Kubota L4200-GST 4WD, LA680 FEL, 6' Mower, 6' Box Blade, 7' Angle Blade, 12kw 3pt PTO Generator

  4. #34
    Platinum Member
    Join Date
    Sep 2004
    Posts
    583
    Location
    south/central Va.
    Tractor
    Deutz Fahr Agrofarm 100, Stoll loader, bucket, forks & root grapple

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by stonypass View Post
    Does your panel have a vertical Main Breaker?
    Our house was built in 1994 and we have a GE PowerMark Plus 200amp 30 space load center.

    I'm looking for an interlock to fit it but the GE model THQLLX1 appears to be for PowerMark Gold models.
    Generator Interlock Kit from GE | The Home Depot - Model THQLLX1

    If yours is similar to mine could you post pic's and a link to which interlock you started with?

    Thanks.
    I bought mine in 1984. It's 40 space load center. Looks similar to yours but has one extra slot at the top on each side that says not to remove and has a vertical main breaker like yours. I used an interlock that was for a SquareD K5410 and modified it.

    I used Generator InterLock Kit and look at Generator InterLock Kit - General Electric Kits K-8110 that perhaps will fit your panel.
    Charolais

  5. #35
    Platinum Member
    Join Date
    May 2004
    Posts
    863
    Location
    Harpers Ferry WV
    Tractor
    Kubota L4330, 6 rear remotes

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by daybreak1998 View Post
    Howdy,
    NO, you can use whatever size generator you want.

    ...

    you use your panel to shut off major power items. For instance, all electric house, turn off water heater, turn off well, turn off oven, turn off stove top, turn off electric heat. you can leave all the lights on, just don't walk around the house and turn every single one of them on. Lites themselves really do not take a lot. Its the big stuff. Then you decide what you want to run while on generator power. Just do not overload your genset. (the generator breaker will trip if overloaded) If you want to shower, turn on the well pump, ok, water pressure is up, ok, turn off well pump, now turn on water heater, after a while, water is hot, now turn off water heater, turn on well pump, take a shower.

    overall concept, is safety. NO BACKFEEDING POWER LINES.
    Some breakers are SW rated, and meant to be used as switches as described ...others, not so much. Just a thought

  6. #36
    Veteran Member
    Join Date
    Jun 2006
    Posts
    1,890
    Location
    West Cascades Washington State
    Tractor
    PT 422

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by JoeL4330 View Post
    Some breakers are SW rated, and meant to be used as switches as described ...others, not so much. Just a thought
    That's good to know.

  7. #37
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    144
    Location
    Northern Virginia
    Tractor
    JD 6430Prem, JD 6400, JD 5500, JD4710, 955, 455

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by JoeL4330 View Post
    Some breakers are SW rated, and meant to be used as switches as described ...others, not so much. Just a thought
    Howdy,
    Circuit Breaker Switches?

    Out of maybe 6 times a year needing to run on generator power, you think a circuit breaker can't handle being shut off 1 day and maybe being turned on a day later when normal power is back on.

    I have not heard of any circuit breakers not being able to switch off and on a few hundred times.

    between having GE panels and breakers, Milbank panel and breakers, Murray panel and breakers, Square D panel and breakers, and some siemens breakers out there also. Standard breakers, GFCI breakers and such, I have never had failure with a circuit breaker. But, I am not flipping them off and on 20 times a day either.
    Later Mike ~~~
    JD green here
    tractors and implements

  8. #38
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    144
    Location
    Northern Virginia
    Tractor
    JD 6430Prem, JD 6400, JD 5500, JD4710, 955, 455

    Default Re: Generator Transfer switch connection choices

    Howdy,
    This was brought up in another thread which showed some products with good prices from local sources.
    GE Power Mark Gold 200 Amp Main Breaker 4-Space 8-Circuit Meter Socket Load Center -ge-pm200-jpg and the matching GE PowerMark Gold Generator Interlock Kit -ge-interlock-jpg really is a nicely priced outdoor NEMA 3R meter base with generator interlock ability. With this being at the meter, you can control it with this service disconnect and then still have your main panel inside with service disconnect as well.

    NOTE: always check with your Utility service to see if this is acceptable for service. They have the say so since it holds the meter.
    Later Mike ~~~
    JD green here
    tractors and implements

  9. #39
    Super Member
    Join Date
    Mar 2008
    Posts
    9,486
    Location
    Northern Fingerlakes region of NY, USA
    Tractor
    Kubota L3830GST, B7500HST, BX2660

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by daybreak1998 View Post
    NOTE: always check with your Utility service to see if this is acceptable for service. They have the say so since it holds the meter.
    FYI, I asked both NYSEG and RG&E about this via their websites and I just heard back from NYSEG. Here is what they had to say:
    Quote Originally Posted by Greg from NYSEG
    After reading through the request I just calling to advise you that the inspectors are ultimately the ones that make the decision on whether or not your work is performed up to code, so if there indicating to you that the equipment that you're choosing to use is acceptable, it is okay to go with the inspectors advice. They're the ones that are going to inspect the service and submit the U L certificate to us to let us know what was done up to code and done safely and we just accept that from them. If we were go by and we were to find something that was grossly un safe that they didn't notice, certainly we would make you make corrections to that but ultimately the inspectors our our final word as far as whether or not the service is unacceptable.
    Still waiting to hear back from RG&E (who actually owns the meter).

    Aaron Z
    A human being should be able to change a diaper, plan an invasion, butcher a hog, conn a ship, design a building, write a sonnet, balance accounts, build a wall, set a bone, comfort the dying, take orders, give orders, cooperate, act alone, solve equations, analyze a new problem, pitch manure, program a computer, cook a tasty meal, fight efficiently, die gallantly. Specialization is for insects.
    Robert Heinlein, Time Enough for Love

  10. #40
    Platinum Member
    Join Date
    Oct 2008
    Posts
    998
    Location
    Mid. Coast Maine
    Tractor
    7610 hst

    Default Re: Generator Transfer switch connection choices

    FYI Ring type meters are not allowed in some states...

Page 4 of 6 FirstFirst 123456 LastLast

Similar Threads

  1. generator whole house transfer switch
    By automech in forum Rural Living
    Replies: 32
    Last Post: 02-14-2014, 09:45 PM
  2. generator/transfer switch connection
    By geneP in forum Rural Living
    Replies: 13
    Last Post: 10-30-2009, 01:48 AM
  3. Generator Generator transfer switch wiring diagram
    By Barneyhunts in forum Attachments
    Replies: 46
    Last Post: 02-29-2008, 10:24 PM
  4. Wiring a Home Generator Transfer Switch
    By RobS in forum Rural Living
    Replies: 38
    Last Post: 01-27-2008, 07:58 PM
  5. Neal's Generator/Transfer setup
    By ns_in_tex in forum Build-It Yourself
    Replies: 43
    Last Post: 10-11-2004, 07:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
© 2013 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.