eepete
Platinum Member
Part of this is the inspectors tell you what you need, but it seemed close. This is an all electric house, let's look at the loads:
3 10KW resistive electric backup for heat pumps: 120 amps
1 five ton and 2 three ton heat pumps: 9KW, 37 amps
2 water heaters (2.5KW each): 20 amps
Cooktop: 20 amps
Dual oven and small oven: 27 amps
Central Vac: 4 amps
Septic Pump: 3 amps
So I'm at 231 amps and still have lights and small appliances left. Now I'll grant you that this would be the holiday throw-down of all time to have all these things going at once, but that's kinda what worst case engineering is all about. And when I build my outbuilding, there will be more power for that too.
Note also that taking two resistive-electric heat pump strips and placing them before the transfer switch makes this worst case load be about 151 amps. Then generator is 45KW --> 180 amps so I have 30 amps left for lights, TVs and computers. It all works out and none one has to think to live in the place- just the way I like it.
3 10KW resistive electric backup for heat pumps: 120 amps
1 five ton and 2 three ton heat pumps: 9KW, 37 amps
2 water heaters (2.5KW each): 20 amps
Cooktop: 20 amps
Dual oven and small oven: 27 amps
Central Vac: 4 amps
Septic Pump: 3 amps
So I'm at 231 amps and still have lights and small appliances left. Now I'll grant you that this would be the holiday throw-down of all time to have all these things going at once, but that's kinda what worst case engineering is all about. And when I build my outbuilding, there will be more power for that too.
Note also that taking two resistive-electric heat pump strips and placing them before the transfer switch makes this worst case load be about 151 amps. Then generator is 45KW --> 180 amps so I have 30 amps left for lights, TVs and computers. It all works out and none one has to think to live in the place- just the way I like it.