    Default Length of electrical run to shed?

    I'm putting up a 12x20 shed to hold my lawn and garden gear. Trying to decide if I should run a 20A/120v direct bury cable to it from my home. It's about 250' from the electrical panel in my basement, but to route in a to avoid septic lines, buried electrical service and phone, I'll have to run about 350 feet of cable.

    Any practical reason not to do this? Is it too far for a 120v line?

    EDIT: Sorry, should have specified...usage will be for some LED lighting inside and out side the shed (very low amperage), and for one standard outlet that will be used for battery charging, maybe the occasional power tool up to 10 amps or so.

  2. #2
    Silver Member
    Join Date
    Nov 2013
    Posts
    245
    Location
    reedsville
    Tractor
    7753 bobcat

    Default Re: Length of electrical run to shed?

    You should be able to go over the top of your septic, its not like you "need to go that deep". Conduit going into structure and out 6'. Put it in a ground fault breaker. Plow the 12awg direct burial and be done with it. Then use a 15 amp ground fault breaker. Your not pulling that many amps, so you shouldn't get a voltage drop.

  3. #3
    Veteran Member
    Join Date
    Jul 2014
    Posts
    1,179
    Location
    Guin, AL
    Tractor
    Kubota L3200DT w/LA524, LP RCR 1860 5' Cutter, LP RTA 1258 5' Tiller, LP PFL 2042 Pallet Forks

    Default Re: Length of electrical run to shed?

    I hear what you are saying, but it has been my experience that there will always be wattage creep. Do yourself a favor and go ahead and run 240v NOW and save yourself many more problems later.
    US Air Force Retired (1966-1988)

  4. #4
    Bronze Member rbstern's Avatar
    Join Date
    May 2011
    Posts
    74
    Location
    GA
    Tractor
    Yanmar 2210

    Default Re: Length of electrical run to shed?

    The long route avoids everything. If I go over the septic system, I also have to cross buried phone cables, which might be shallow enough for a problem.

  5. #5
    Gold Member Mendonsy's Avatar
    Join Date
    Nov 2012
    Posts
    349
    Location
    Mendon, NY
    Tractor
    Kubota B7500HST

    Default Re: Length of electrical run to shed?

    Here's a calculator that will tell you what wire size you need to run for the current and distance. The answer seems a bit high, but I tried several different ones and they all came up the same.
    Wire Size Calculator

  6. #6
    Veteran Member Sodo's Avatar
    Join Date
    Apr 2012
    Posts
    2,009
    Location
    Cascade Mtns of WA state
    Tractor
    Kubota B-series & Mini Excavator

    Default Re: Length of electrical run to shed?

    For 350 ft need 8ga to run a 10A tool. Using 12ga you can run about 3 Amps of load. 12ga is plenty good for LED lights or a 30A battery charger. Maybe consider 10ga and run the 10A tool carefully, don't push it too hard.
    Be careful what you wish for, you might get it.

  7. #7
    Bronze Member rbstern's Avatar
    Join Date
    May 2011
    Posts
    74
    Location
    GA
    Tractor
    Yanmar 2210

    Default Re: Length of electrical run to shed?

    Quote Originally Posted by mddorange View Post
    I hear what you are saying, but it has been my experience that there will always be wattage creep. Do yourself a favor and go ahead and run 240v NOW and save yourself many more problems later.
    If I go 240v, direct bury cable is against code and I have more expense and effort to bury the line in conduit. I can live with 120v and limited amps. Any type of work needing more than that will get done near the house.

  8. #8
    Platinum Member dieselcrawler's Avatar
    Join Date
    Jan 2008
    Posts
    651
    Location
    New Martinsville WV
    Tractor
    2013 JD 3005 1974 MF135

    Default Re: Length of electrical run to shed?

    I have been a licenced electrican for nearly 20 years. Anything over 100' from the breaker to the recptical needs to be up sized for the voltage drop. If you are worried about code compliance (not running 120/240v direct bury wire) then the smallest breaker for a general purpose branch circuit alowd by code is 15 amps, you still need at least 10ga wire. I would go with 8-3 w/ground, and be able to get a useable 20 amps 120/240 volts out there. Do it right the first time. But then, I would also run a larger conduit in as straight a line as possible. Hand dig around the phone lines if needed. Code says conduits and wires "should" be 18" below the surface and have warning tape buried 6" below the surface. There may or may not be a type UF wire run to my pool area 3-4" below the surface of my yard. Out here in the country there is only me to make me comply with code.
    Greg AKA DieselCrawler
    2013 JD 3005 4x4 w/loader
    1974 MF135 diesel (dad's)
    Trucks:
    1999 F250 4x4 7.3L diesel 6spd. Sidelined due to motor issues
    2000 F350 4x4, 7.3L diesel, auto, daily driver
    2000 Excursion 4x4 7.3L diesel, wife's ride
    84 Chevy K-30 turbo diesel farm truck, play truck, one ton running gear, locked up, on 39.5" boggers,
    Redheaded wife, 6 kids, buncha rabbits, 4 horses/ponies, 4 cats, 3 dogs

  9. #9
    Super Member grsthegreat's Avatar
    Join Date
    Jan 2011
    Posts
    6,697
    Location
    north idaho
    Tractor
    Kioti DK45SE hst cab

    Default Re: Length of electrical run to shed?

    Is it a local law that forbids 240 direct butial? Its not against NEC rules. After 100 feet derate occures, and it doesn't matter what the use is. Probably doesnt matter if your only using lights, but the derate will play **** with motors like drills, refrigerators, etc.
    currently own
    2011 Kioti DK45SE HST CAB tractor/loader, Jimna 6" - 3 point wood chipper, 60" JD Brush Hog, JD 60" Rototiller, 3 point post hole digger with hydraulic assist, 3 point spring tooth rake, Fimco 55 gallon weed sprayer with 12 foot boom, 3 point hydraulic wood splitter (home built)
    Quick Attach 79" loader mount snowblower & rear powerpack
    Quick Attach 84" Snow Blade
    Quick Attach 42" pallet forks

  10. #10
    Bronze Member rbstern's Avatar
    Join Date
    May 2011
    Posts
    74
    Location
    GA
    Tractor
    Yanmar 2210

    Default Re: Length of electrical run to shed?

    Quote Originally Posted by grsthegreat View Post
    Is it a local law that forbids 240 direct butial? Its not against NEC rules. After 100 feet derate occures, and it doesn't matter what the use is. Probably doesnt matter if your only using lights, but the derate will play **** with motors like drills, refrigerators, etc.
    Going 240v means I've got to go to 24" deep or do conduit.

    I really only have two uses for power at the shed: Battery charging and lighting. I considered going with a solar setup, but I don't want another 12v battery in my life (have too many of those already).

Page 1 of 4 1234 LastLast

Similar Threads

  1. Run in shed
    By glinka in forum Build-It Yourself
    Replies: 5
    Last Post: 08-15-2013, 03:01 PM
  2. Run-in shed for a horse... plans?
    By Anonymous Poster in forum Rural Living
    Replies: 10
    Last Post: 07-23-2012, 10:24 AM
  3. run in shed
    By wv cabin in forum Build-It Yourself
    Replies: 21
    Last Post: 03-13-2009, 07:45 AM
  4. Run In Shed Construction
    By JeremyL in forum Projects
    Replies: 28
    Last Post: 08-25-2008, 11:17 PM
  5. Interesting Horse Run-In Shed Project!