frankc
Bronze Member
The setting: Cabin 8 miles from any public power source. So, there is little chance in my life that public electric will ever be available. SO, when I wired the cabin, I set up the electric service box just as I would if it was being served from a power company, and bonded the Neutral and Ground bars together, then run to an external ground rod. I supply power to the box via a 240V 50Amp breaker wired from a 6-gauge 2wire plug. (2 hots, 1 ground std welders plug).
This has worked just fine no problems.
THE QUESTION: I just got a new generator that has a 4 wire plug on it, (2 hots, seperate neutral, ground). I know the right answer is to spend the money and change my setup from the current 2/1wire to a 3/1 wire setup, but given the expense of that heavy wire and that I need 25ft of it, I'm wondering since the neurtral and ground are bonded in the box(thus they both go to ground), why can't I just buy the appropriate 4-prong plug to plug into the generator but jump the nuetral to the ground in the plug there, thus I could still use my current wiring.
Basically I'm just wondering why I can't pass the neutral to the ground in the plug at the generator since that's whats basically happening in the main electric box????
This has worked just fine no problems.
THE QUESTION: I just got a new generator that has a 4 wire plug on it, (2 hots, seperate neutral, ground). I know the right answer is to spend the money and change my setup from the current 2/1wire to a 3/1 wire setup, but given the expense of that heavy wire and that I need 25ft of it, I'm wondering since the neurtral and ground are bonded in the box(thus they both go to ground), why can't I just buy the appropriate 4-prong plug to plug into the generator but jump the nuetral to the ground in the plug there, thus I could still use my current wiring.
Basically I'm just wondering why I can't pass the neutral to the ground in the plug at the generator since that's whats basically happening in the main electric box????