Old 01-07-2007, 03:23 PM   #11 (permalink)
Silver Member
 
Join Date: Sep 2003
Posts: 243
Default Re: 220VAC line burial depth ?

Quote:
Originally Posted by Farwell
Bob,
I like 18 inches for conduit and 24 inches for direct burial but this will vary according to your location.
David B
I believe this is the correct depth according to the NEC. You can always go deeper if you want, but it means moving a lot more dirt, both on the way out and going back in. And it takes a lot longer for the dirt to settle in the trench the deeper you go, so it is your choice. Personally, I go around 2 to 2-1/2 feet with conduit, because it is easy to back fill and settles quickly. 3' isn't too bad, but 4' is moving an great deal of dirt, especially if you are in a sandy area where it tends to cave in easily.
kmdigital is offline   Reply With Quote
Old 01-07-2007, 05:37 PM   #12 (permalink)
Platinum Member
 
Join Date: Oct 2005
Location: N. E. Ohio
Posts: 937
Default Re: 220VAC line burial depth ?

Our area requires 4 foot deep for run from pole to house. It also requires RED tape to be placed one foot above conduit in trench for warning .
__________________
dqdave1; tc-29D; woods 7500 bh; 7308 fel, land pride tiller, land pride rake, gill pulverizer, 60"mmm. , bucket forks , MZ16H
dqdave1 is offline   Reply With Quote
Old 01-08-2007, 04:30 PM   #13 (permalink)
Gold Member
 
Join Date: Sep 2005
Location: Ohio
Posts: 425
Default Re: 220VAC line burial depth ?

42 - 48 " for main line from the road to the house or meter. 18" from there or from the house to an outbuilding.
Ford850 is offline   Reply With Quote
Old 01-08-2007, 05:43 PM   #14 (permalink)
Gold Member
 
GreatWhitehunter's Avatar
 
Join Date: Sep 2006
Location: Eastern CT
Posts: 381
Default Re: 220VAC line burial depth ?

I think you need to rethink your conductor size. A 100Amp service requires #3 copper and #2 aluminum. And after 100FT run you need to factor in voltage drop. As for burial depth I'd go with the NEC since it is the minimum. I'd go with #1 copper for the VD and if your going THHN you'll be good for 130A.The voltage means little to the burial depth. In case your wondering you'd need 2" schedule 40 pvc and you could run 5 #1's you won't be able to use 1-1/2 since you can only get three in there and you should not downsize the neutral. And you need a ground also (bonding conductor).

Matt T.
GreatWhitehunter is online now   Reply With Quote
Old 01-09-2007, 07:25 PM   #15 (permalink)
Gold Member
 
Join Date: Dec 2004
Location: Andice, Texas
Posts: 339
Default Re: 220VAC line burial depth ?

bcarwell,

If you can't get your middle buster to go down as far as you like, the nearest rental place for a Ditchwitch is Cat Trax on Hwy 29. You can get a 3700 (diesel, ride-on) set up for a 4" wide trench that can go down 24". I think a day's rental is around $160 with tax. It comes with a front blade so you can fill the trench back in. If you land is fairly rocky, they also have rock saws but thoese are more like $300 a day. They are nice folks to deal with.

As far as depth goes, I've never put in anything deeper than 24".
__________________
John Deere 5420/4WD/FEL, PwrReverser
8MX Shredder, Belltec TM-48-HTL PHD, WR Long RBG Grapple, 12" Tree Terminator & more...
GaryBDavis is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


All times are GMT -4. The time now is 12:28 PM.


HOME DISCUSSIONS PHOTOS REVIEWS CLASSIFIEDS DEALERS STORE
About TractorByNet.com | Terms of Service | Advertise | © 2008 TractorByNet.com