eepete
Platinum Member
First off, follow the rule "if it's anything with electronics, put it on a filtered surge suppressor strip."
Next, realize that you can't just wish energy off the face of the earth, it has to go somewhere. So a good ground system is critical to the surge suppressors working. The power co. and telcos put in a 4' to 8' single ground rod. You probably want three or four 8' copper clad ground rods. They do better when in damp soil, so look at where you put it. A ground rod where the flow from the gutter comes out is great. Space the ground rods more than 7' apart. If you have buried service, know where it it is or call the location service before you pound the ground rods in.
The worst I've seen is a 4' copper plated (not copper clad) ground rod in the disturbed soil of the house under an overhang.
Now that you have a good ground, put in a whole house suppressor at the main panel.
Also consider the advantages of buried power to your house in high lightning areas. Pay me now, pay me later...
I had a problem once. I got a line voltage monitor, and when the power co. came out, they saw 130V all the time. They put recorder on for a week. They agreed there was a problem.
The solution was to replace an old regulator. Regulators are often used in distribution systems to try to regulate the voltage alone a long feed. You might have a regulator every 5 miles or so. It took time for the power co. to schedule the replacement, as these things are not cheap.
Ken, this doesn't adress what you asked , but these ideas can help cut down on problems. They are also things most people on this forum can do.
Pete
Next, realize that you can't just wish energy off the face of the earth, it has to go somewhere. So a good ground system is critical to the surge suppressors working. The power co. and telcos put in a 4' to 8' single ground rod. You probably want three or four 8' copper clad ground rods. They do better when in damp soil, so look at where you put it. A ground rod where the flow from the gutter comes out is great. Space the ground rods more than 7' apart. If you have buried service, know where it it is or call the location service before you pound the ground rods in.
The worst I've seen is a 4' copper plated (not copper clad) ground rod in the disturbed soil of the house under an overhang.
Now that you have a good ground, put in a whole house suppressor at the main panel.
Also consider the advantages of buried power to your house in high lightning areas. Pay me now, pay me later...
I had a problem once. I got a line voltage monitor, and when the power co. came out, they saw 130V all the time. They put recorder on for a week. They agreed there was a problem.
The solution was to replace an old regulator. Regulators are often used in distribution systems to try to regulate the voltage alone a long feed. You might have a regulator every 5 miles or so. It took time for the power co. to schedule the replacement, as these things are not cheap.
Ken, this doesn't adress what you asked , but these ideas can help cut down on problems. They are also things most people on this forum can do.
Pete