HVAC puzzle
Our building code requires adjustable LOCKABLE dampers at the boot for all supply registers.
The accepted practice is to put those round dampers in the pipe just before the boot and snug them down. Which is fine for the first floor. My crawlspace will always be accessible for adjustment and locking of the dampers to make seasonal adjustments.
The second floor is another story. The wingnut locks will be in the ceiling so once the drywall goes on there will be no more access to unlock or lock. Which would be OK if my heating and cooling airflow requirements were equal, but they are not. So one must reach down the register and adjust, without backing off the lock or re-locking.
In my last house all dampers were accessible in the basement and seasonal adjustment took a minute. the bedrooms were always cool, winter and summer. Just the way we like em. This arrangement does not meet code.
I rather not install dampers just for the sake of inspection, since they will inhibit seasonal balancing.
So I'm looking for a lockable register or lockable damper for the boot. The lock is simply a lock nut or bolt.
Has anyone seen such a product?Steve
The best things in life are not things.
-
08-26-2012, 03:08 PM #2Silver Member
- Join Date
- Jul 2012
- Posts
- 168
- Location
- ...
- Tractor
- ...
Re: HVAC puzzle
No, but I have to say that is just a bizarre requirement. Any idea what they were thinking?
-
08-26-2012, 03:43 PM #3Member
- Join Date
- May 2012
- Posts
- 34
- Location
- Cincinnati oh
- Tractor
- grillo 85D
Re: HVAC puzzle
Access panels?
-
08-26-2012, 03:47 PM #4Veteran Member
- Join Date
- Oct 2006
- Posts
- 2,438
- Location
- The County, Ontario, Canada
- Tractor
- Kubota, B7100HST-D
Re: HVAC puzzle
Here is the wording;
6.2.4.6. Adjustable Dampers and Balance Stops
(1) All branch supply ducts for residential systems shall be equipped with volume control dampers at the boot to permit balancing or shall be fitted with a diffuser incorporating an adjustable and lockable volume control device that can be set in a fixed position.
Seems to be all about balancing the airflow while standing at the boot. I guess they want a one man operation with no running up and down stairs.
I have also heard various iterations of "dampers must be at the end of the duct to keep the velocity up in the rest of the duct". But flow is flow, so what goes in comes out at the same rate, regardless of where the flow control is. The only difference would be pressure in the duct, but I've not heard that mentioned.
Maybe someone with some HVAC experience can shed some light on this.Steve
The best things in life are not things.
-
08-26-2012, 03:48 PM #5Silver Member
- Join Date
- Jul 2012
- Posts
- 168
- Location
- ...
- Tractor
- ...
Re: HVAC puzzle
Locked wide open dampers above the ceiling (sucks I know) and an accessible damper on the trunk near the air handler/furnace?
Personally, I wouldn't want dampers in unconditioned or inaccessible space. They all leak at the shaft.
-
08-26-2012, 04:00 PM #6Veteran Member
- Join Date
- Oct 2006
- Posts
- 2,438
- Location
- The County, Ontario, Canada
- Tractor
- Kubota, B7100HST-D
Re: HVAC puzzle
Plumbing access panels worked out well. Closet and pantry ceiling.
Only two of the seven upper floor registers would be in places where access panels would work. One in the pantry, another concealed by a kitchen cupboard. The rest would be in the dining, living and master bedroom ceilings.Steve
The best things in life are not things.
-
08-26-2012, 04:16 PM #7
-
08-26-2012, 04:25 PM #8
Re: HVAC puzzle
Could you modify/re-engineer the to-be-buried boots such that the lock-nut is accessible from the register/diffuser? Do some drilling and soldering (assuming metal) to fix the outside bolt head in place?
“It is a great thing to know the season for speech and the season for silence” ― Seneca (4 BC - 65 AD)
-
08-26-2012, 04:33 PM #9Veteran Member
- Join Date
- Oct 2006
- Posts
- 2,438
- Location
- The County, Ontario, Canada
- Tractor
- Kubota, B7100HST-D
Re: HVAC puzzle
These are the dampers used in the duct at the boot.
Don Park | Volume Damper 5 In. | Home Depot Canada
It's pretty flimsy and simple. Bolt is spot welded to the damper. Wingnut and handle go on the outside.
It looks like this when installed;
SPEEDI-COLLAR | 10 in. HVAC Connection Collar with Damper | Home Depot CanadaSteve
The best things in life are not things.
-
08-26-2012, 04:40 PM #10Member
- Join Date
- May 2012
- Posts
- 34
- Location
- Cincinnati oh
- Tractor
- grillo 85D
Similar Threads
-
shop press puzzle
By jmc in forum HydraulicsReplies: 7Last Post: 11-27-2009, 06:24 AM -
Weight puzzle!
By megotatractor in forum John Deere Owning/OperatingReplies: 5Last Post: 01-24-2009, 04:53 PM -
eerie puzzle --
By eric and his rtv in forum Related TopicsReplies: 11Last Post: 02-06-2008, 05:06 PM -
Tractor puzzle
By ERNIEB in forum Related TopicsReplies: 8Last Post: 12-07-2000, 09:18 AM -
Bitterroot fire puzzle
By gordon in forum Related TopicsReplies: 6Last Post: 12-03-2000, 09:08 AM


Reply With Quote
just noticed you're in Canada) we paint them the ceiling color where you have to have them