Gas Grill Propane Tank

   / Gas Grill Propane Tank #11  
I had the exact same problem with my new tank last year. It is most likely over-filled, as mine was. Just keep trying to use it. Let it thaw out when it frosts, and try it again. Just a few more times and it'll work just fine. At least it worked for me!

Corm
 
   / Gas Grill Propane Tank #12  
Sounds like the tank is overfilled, causing liquid to get to the regulator. Open the grill valve and pour a little water over the regulator each time it frosts up. As soon as you bleed off enough propane, it'll be OK.
 
   / Gas Grill Propane Tank #13  
Billy, I think you've gotten closer to the cause than anyone. The new tanks are supposed to have a float to automatically shut off the fill before they are overfilled, as Egon mentioned, but that's not foolproof. The fools are supposed to still use a scale to be certain the tank is not overfilled; the auto shutoff is supposed to be a backup. But, some dispensers may have gotten lazy and depend on the shutoff float, and if it gets stuck, the tank is overfilled.

That's the only way I could explain a frozen regulator. Like Billy said, eventually the problem will correct itself, although if it is liquid at the regulator, it could damage the diaphragm.

In the old days, you simply could have taken the tank out in the back yard and let some of the gas out until there was enough expansion room for the vapor (that's why they are never filled more than 80%). But, with the new OPD tanks, an appliance has to be connected to the tank, or the check valve will not open and allow the gas to exit. Thus, the only way to drain a new OPD tank is to use a purge valve. This has the black plastic nut to screw on the tank and a brass center, like your grill connection, but unlike the grill, the brass center is drilled wide open and allows the tank to empty. Screwing on the connector, either for a grill or the purge valve, forces the check valve to open.

As for turning it on too quickly, here's the heart of that problem. As a further safety measure, all new grills built since the OPD valve went into effect on the tanks must use a safety valve in the connector to shut off the flow of the gas if there is a potential leak.

This safety valve is located in the brass part of the connector on the grill, not on the tank. Thus, it is part of the grill, not of the tank. It is inside the brass part that is inside the plastic hand nut, where the grill connects to the tank. It is actually a tiny slub with a needle shape at one end (a fat needle valve) and a spring.

What happens is this: When you turn on your tank, the immediate pressure from the tank forces the needle valve to close against the spring, and shut off the flow of gas. If there is sufficient pressure in the hose and regulator, the residual pressure left there from the last time you used your grill, that back pressure will force the needle valve to open again, and the gas will flow normally from the tank to the grill.

If there is no residual pressure in the hose and regulator, the needle valve stays in the shut position, and very little gas gets to your grill.

That needle valve is designed to allow a trickle of gas to get past it, about 10% of normal flow. If there is no pressure in the hose/regulator, that 10% flow will fill them up (in about 30 seconds) and allow the needle valve to be opened. Because it only flows about 10%, your grill may light, but with a very tiny flame. Because you are using all of the reduced flow, the pressure will never build up, the needle valve will never get pushed open, and the flow will never increase.

WHEN THIS HAPPENS, THE FIX IS VERY SIMPLE. Shut off the grill at the control valves. Shut off the tank at the main tank valve. Open the tank valve again. Wait 30 seconds for the pressure to build up in the hose/regulator before you try to turn on the grill. Then, turn on the grill valve and light in your normal manner. It should be working just fine.

The logic behind this safety valve is simple. If your hose/regulator/grill valve has developed a leak, then allowing the full flow of gas into the system so it will leak, is not a good idea. If there is a leak, cutting the flow to 10% is a Good Thing.

OK, you say, but I don't have a leak! Why don't I have the residual pressure required to open the safety valve? (It's actually called an Excess Flow valve -- my senior memory prevented me recalling the name until just now /forums/images/graemlins/blush.gif). There are a couple of ways.

One could be the way you shut off the grill the last time you used it. If you are in the habit of shutting off the tank first, so all the gas can drain out of the hose and regulator, then shutting off the grill valves -- well, there you have it, your hose and regulator is empty! There is no residual pressure! You can keep up that habit if you like, you'll just have to turn on your tank and wait 30 seconds before turning on the grill every time you use it! Or, learn to turn the grill off first, then the tank. The amount of residual gas in the hose and regulator is not enough to cause any harm.

The second cause could be that when starting up your grill, you opened the grill valve before you opened the tank valve. Usually, that happens something like this: 1) turn on the grill. 2) try to light the grill. 3) slap yourself upside the head because you just remembered it won't light because the tank is still closed. 4) open the tank. Of course, at this point, your grill valve is still open, and -- Guess What! That's a Leak! The safety valve is doing exactly what it was intended to do, prevent excess flow from a leak!

The simple way to prevent this is to always remember to turn on the tank before the grill. Of course, if you're like most, you'll forget, in which case go back up to the paragraph, "THE FIX IS VERY SIMPLE".

And, once again, I'm maintaining my reputation of telling you more than you want to know about propane tanks and grills! /forums/images/graemlins/grin.gif /forums/images/graemlins/grin.gif /forums/images/graemlins/laugh.gif
 
   / Gas Grill Propane Tank #14  
GARY: i did the same thing last may , went to PHOENIX to vist my daughter and out her a new grill, had the guy do the same thing, purge before filling the first time. also i have heard that some of the old regulators don;t work right with the new tanks(don't know if this is true or not)
 
   / Gas Grill Propane Tank
  • Thread Starter
#15  
Don, good to hear from you in light of your weather situation. I somehow knew you'd have the story here. Yes, it does sound like it's overfilled. I'll play with that tomorrow and hope to be in business. If not, it's back to the campground.

Thanks and hope all turns out well for you /forums/images/graemlins/smile.gif
 
   / Gas Grill Propane Tank #16  
<font color="blue"> purge before filling the first time.</font>

As Bird has mentioned, this was always supposed to have been done, but it was a lot more hit-or-miss before the OPD tanks came out. Essentially, it involves getting the air out of the tank so there will be 100% propane (or as close as possible) inside. The air is what is trapped inside when the tank is closed up at the manufacturer, plus what is used to pressure test the tank before it's shipped. Moisture can also be a problem, but the manufacturers have gotten pretty good about dehumidifying the air in the factory, and many use nitrogen instead of compressed air to do the pressure test. So, moisture is much less of a problem than it used to be, unless the tank has suffered some temperature extremes before filling and condensation results. Even then the amount is tiny.

In the old days, all we had to do to purge was put some propane vapor in the tank, then set the tank aside, open the valves, and let the propane vapor blow out the air. This works because propane vapor is heavier than air, settles to the bottom of the tank, and pushes the air out. Once the pressure has equalized (propane inside, atmospheric pressure outside), no more air can ever get back into the tank unless it's forced in under pressure.

There were some crazy theories. One of my competitors swore that the best way to purge was to put in the propane vapor, then turn the tank upside down and open the valve. Of course, because the propane was heavier, all he accomplished was to let the propane back out, retaining the air in the tank. I tried to clue him in, but he was stubborn, so I just used the facts to convince my customers that I knew a heck of a lot more about what I was doing than did my competitor. /forums/images/graemlins/laugh.gif

With the advent of the OPD tanks and their check valves and tiny orifices, purging became a lot more difficult. The recommended method was to put in some vapor, let it out, and repeat 4 or 5 times. Because it takes forever for the vapor to exhaust through the orifice, purging properly could take up to 20 minutes. For the first time, we started to charge for the purge, simply because of the time it took.

Then, my local state LP gas inspector (who was a good friend, mostly because he knew he would never have any problems with my operation), who was an innovator, suggested that I set up a vacuum purge. Now, they sell vacuum purging rigs that cost hundreds of dollars. But, we had a good air compressor on site. I plumbed the air out to the fill station, then rigged up an air-powered vacuum pump I got from Harbor Freight for less than $20. It works on the venturi theory, in that rushing air past a venturi sucks air from whatever it's hooked to. Also in the rig were some shutoff valves and a regulated feed from a normal 20# grill tank to apply vapor.

The process was to hook up a connector to the tank, close all the valves except the vacuum, turn on the vacuum pump and suck out all the air. The pump would pull down to 28.3" of mercury. good enough according to all the tank mfr. specs, in about 2 minutes. Then we closed the vacuum valve, holding the vacuum inside the tank, and opened the propane vapor valve. Nature abhors a vacuum, so the pro pane, pressurized anyway at around 15 psi, did a lickety-split job of rushing into the tank and displacing the vacuum. Job done quickly and very thoroughly, and we still got to charge a fee for the purge, with the excuse that our sophisticated equipment had to be paid for. Truth is, the most sophisticated part of the who rig was a dual vacuum/pressure guage we picked up for about $24 that normally belonged on the low pressure side of an auto A/C recharging unit. We had no guilty feelings about the fee, because we knew the customer was getting a better purge, and was paying us for our expertise (we charged $3 for the purge).

<font color="blue"> also i have heard that some of the old regulators don;t work right with the new tanks</font>

The regulators are the same. Where the problem comes in is the connection. The old grills and regulators will still work with a new style tank, but the new grills will not work with an old style tank. The reason is because all propane tanks, old and new, have internal threads with a left-hand (backwards) thread. This is because ASME long ago declared that non-flammable gases like oxygen and nitrogen would have right-hand threads, and flammable gases like propane and acetylene would have left hand threads. I think they did this to prevent you from hooking up propane to Grandma's oxygen tent.

The old grills, and all other propane appliances, use what's known as a POL connector. Some say the POL stands for the original mfr, Prest-O-Lite; others insist it means Put On Left-handed. The problem that happened with grills is that they have to be frequently hooked up and unhooked by the great unwashed and untrained masses, most of whom don't even know a left-hand thread exists, and the vast majority of whom don't have a properly sized wrench. The result was lots of leaks from improperly attached tanks, and lots of damage from the leaks.

The first answer was to introduce quick disconnect fittings to the tanks and regulators. Weber and Ducane, and a few very-high end grills, adopted this. The rest of the industry (primarily Charbroil; they own most of the low cost brand names) didn't go along with this because the quick disconnect system was comparatively very expensive (it had to be a lot better quality than the Q/D systems used on air compressors).

The Italians actually figured out a good work-around. It was adopted here and is called the Type I QCC (Quick Connect Coupler). While it was required that the tanks still have the internal left-handed threads, no one said you couldn't add some external threads to the tank nozzle. Since they are in addition to the standard threads, they can be righty-tighty. And, by using a coarse acme-type thread, the connector nut can be large enough to be turned by hand, no longer requiring a wrench. By using an internal O-ring, the connector nut didn't even have to be particularly tight to seal.

This system was just marginally more expensive than the old POL connectors, and was a heck of a lot safer. It became adopted in 1995. There is an additional, very neat safety factor. A check valve was incorporated into the tank nozzle, which has to be forced open by connecting an appliance for the gas to flow. If the connector is the more modern plastic hand nut described above, it has a thermal-sensitive ring that holds it together. If there is a fire under the grill, that ring will melt, the connector assembly will come apart, the center portion will pop out thus allowing the check valve to close, and the gas in the tank will no longer feed the fire. This is very cool!

Interestingly, the OPD tanks actually has little to do with the QCC, which was adopted several years earlier. OPD stands for Overfill Prevention Device, and is the float inside the tank that works like a toilet float. When the liquid propane reaches 80% of the tank's capacity, the float rises and shuts off the flow, thus preventing overfilling. Overfilling is dangerous because if there is not sufficient room for the vapor to expand with temperature increases, the vapor will be exhausted from the pressure relief valve on the back of the tank valve assembly. Of course, the vapor that is released is flammable, and if there's a source if ignition near by, you'll have a Floomph. With a full tank (filled to normal 80%) and enough temperature increase (inside a very hot car trunk or closed garage), even a tank that has not been overfilled will exhaust excess vapor, which is why they say not to store a tank inside, or keep it in a hot trunk more than, say, 2 hours.

Sorry for writing another book, but heck, I'm just sitting here waiting for a hurricane. What else do I have to do? /forums/images/graemlins/confused.gif
 
   / Gas Grill Propane Tank #17  
Thank you for the Book.

Best to all of you for when the big wind and rain hit.

Egon
 
   / Gas Grill Propane Tank #18  
A semi related question for you if you have the time between trees falling /forums/images/graemlins/crazy.gif (hope you're safe)

anyway, I have several tanks I use for our propane fireplace. They connect using the left hand threads (internal).

When you tighten those, do you "snug" them, or do you crank them down?

I've had a tank that I feared had a leak at that connection, then I thought perhaps I just didn't tighten it enough, yet I then feared over tightening it.

how tight is tight?

/forums/images/graemlins/confused.gif
 
   / Gas Grill Propane Tank #19  
Richard, I've use propane enough on RVs that I always had a properly sized wrench. It's had to say whether "snug" or "cranked down" is best because those terms may not mean the same thing to everyone. I'd say snug, but I also found it's no big deal to keep a small squirt bottle with about one-fourth to one-third liquid dishwashing soap and the rest water to quickly check for leaks with just a squirt or two. With the older tanks using the left handed internal threads, some (not all) of the fittings on the end of the hose had a rubber o-ring on them, so I didn't tighten them as much.
 
   / Gas Grill Propane Tank #20  
Don, I appreciate the detailed explanation. Of course, all my RVs used the old style left-handed threads, and that's all that existed when I had my very limited experience with pumping propane. Of course now all I have is the CharBroil grill and two 20# bottles. The only time I ever had a propane bottle overfilled was once in Alaska at an RV park. They charged by the pound for the propane and she charged for, and said she put, 4 pounds more than the capacity of my tank. I didn't have any scales myself, but got the definite impression that she didn't know what she was doing was probably did overfill it, so I bled some off before hooking it up.
 

Tractor & Equipment Auctions

2005 Big Tex 10PI 16ft T/A Pipe Top Utility Trailer (A45336)
2005 Big Tex 10PI...
2016 FREIGHTLINER CASCADIA TANDEM AXLE SLEEPER TRUCK (A45676)
2016 FREIGHTLINER...
2022 Bullet 330BHS Bunkhouse Travel Trailer (A45336)
2022 Bullet 330BHS...
2017 KENWORTH T680 SLEEPER TRUCK (A45677)
2017 KENWORTH T680...
2008 UTILITY VS2RA 53FT REEFER TRAILER (A45677)
2008 UTILITY VS2RA...
2003 VIKING TRAILER CEMENT MIXING TRAILER (A47001)
2003 VIKING...
 
Top