    "I put the tester across the fuse itself as it comes through the wall from the pole and also put it across the switch on the wall farther down the line. I guess that's the load side. I get 30v. "

    Now I'm confused. Are you saying you put one probe of the tester on one end of the fuse, and the other probe of the tester on the other end of the fuse and got 30 volts?

    When you say "across the switch" and got 30V, what did you put the probes across?
    JD5075E, Frontier RC2084 Rotary Cutter, Wallenstein FX65 Skidding Winch

  2. #12
    Platinum Member jefwyn's Avatar
    Join Date
    Mar 2012
    Posts
    576
    Location
    Western NY
    Tractor
    Mahindra 3616 hst cab

    Default Re: Electrical Problem in old garage/shed

    I'm sure you are not doing this, but just in case, I'll put this out there. I have seen guys, and might have done it myself, read the voltage, not noticing that it was milivolts.

  3. #13
    Platinum Member Pete Judd's Avatar
    Join Date
    Aug 2010
    Posts
    980
    Location
    The Thin Gravy Ranch in The wet PNW
    Tractor
    Yanmar 186d, JD 314

    Default Re: Electrical Problem in old garage/shed

    Jefwyn, I also have a high end auto ranging meter and you can't watch that decimal point. Bit me a couple of times.
    Yanmar 186D 1981
    5 foot Unknown brush hog.
    5 foot HF Finish mower.
    5 foot J-Bar back blade.
    HF Quick Hitch.
    Home made land leveler.
    Countyline Middle Buster.

  4. #14
    Gold Member uglyboywith11fingers's Avatar
    Join Date
    Sep 2011
    Posts
    357
    Location
    Georgetown, Ontario
    Tractor
    2007 BX24TLB, 1998 TG1860G

    Default Re: Electrical Problem in old garage/shed

    I'd be suspect of a 30 volt reading across the fuse...
    if the fuse is good, there should be essentially zero voltage drop across it, current flow or not.
    if the fuse is blown, there should be 120 volts across it if the rest of the circuit is complete, ie. switch is on, bulb is good. if circuit is not complete, should read close to zero across the fuse.

    you need to read the voltage between the 2 wires that come into the building.

  5. #15
    Veteran Member KennyG's Avatar
    Join Date
    Jan 2011
    Posts
    1,123
    Location
    SW Michigan
    Tractor
    John Deere 2320

    Default Re: Electrical Problem in old garage/shed

    Quote Originally Posted by uglyboywith11fingers View Post
    I'd be suspect of a 30 volt reading across the fuse...
    if the fuse is good, there should be essentially zero voltage drop across it, current flow or not.
    if the fuse is blown, there should be 120 volts across it if the rest of the circuit is complete, ie. switch is on, bulb is good. if circuit is not complete, should read close to zero across the fuse.

    you need to read the voltage between the 2 wires that come into the building.
    I thought he meant across the lines AT the fuse. We're all guessing at this point aren't we.

  6. #16
    Super Member grsthegreat's Avatar
    Join Date
    Jan 2011
    Posts
    6,443
    Location
    north idaho
    Tractor
    dk45se hst cab

    Default Re: Electrical Problem in old garage/shed

    Need to remove fuse and run a ohm test on the fuse.

    Or do as Mace suggests and test real voltage between neutral and line side of fuse. (thats the incoming power before the fuse)

    In the past i have gotten fake ---low--- readings like 30 volt or 60 volt on systems that had lost the neutral, but got a partial return voltage thru the ground . This voltage disappeared when i removed all light bulbs from their sockets, and unplugged all outlets. After the neutrals were repaired..all was well again.

    Also you need to check voltage where power originates at main panel or house.
    currently own
    2011 Kioti DK45SE HST CAB tractor/loader, Jimna 6" - 3 point wood chipper, 60" JD Brush Hog, JD 60" Rototiller, 3 point post hole digger with hydraulic assist, 3 point spring tooth rake, Fimco 55 gallon weed sprayer with 12 foot boom, 3 point hydraulic wood splitter (home built)
    Quick Attach 79" loader mount snowblower & rear powerpack
    Quick Attach 84" Snow Blade
    Quick Attach 42" pallet forks

  7. #17
    Super Member radioman's Avatar
    Join Date
    May 2008
    Posts
    5,539
    Location
    Ontario, NY
    Tractor
    Kubota BX24

    Default Re: Electrical Problem in old garage/shed

    first of all -- you have what its called a voltage drop. either using too much or too far. you need to pull the fuse and measure the voltage at line in connection at box in garage. 120? good. you know line from garage to second pole is likely good. this likely means you have a burnt line or plug or short in extension or fuse connection issues. do you see any deformed or wrinkled appearance of metal fuse connectors? no? with fuse pulled - check ohms resistance of line going to rest of garage. is it open or closed? closed? I'd start investigating the lines in garage and unplug everything in sockets and pulling bulbs and recheck. still closed? then you got bigger issues. its time for a rewire IMHO. I bet once you replace the wiring to everything in the garage- you will find the culprit and you will prevent any future fires from other wiring.
    One other thing to check - do you have any junction boxes in your garage? with fuse pulled - I'd start checking and retighten the junction connectors or find a way to eliminate it. A loose wirenut can cause same issue you are having.

  8. #18
    Veteran Member
    Join Date
    Dec 2005
    Posts
    1,041
    Location
    Kentucky
    Tractor
    B2920

    Default Re: Electrical Problem in old garage/shed

    Along the line of checking any junction boxes for loose connectors - are there any splices in the lines between the house and the shed? A lot of the old splices amounted to twisting the wires together and taping over them. Very easy to have corrosion build up in them and weaken he conductivity.

  9. #19
    Elite Member Mace Canute's Avatar
    Join Date
    Nov 2006
    Posts
    4,412
    Location
    Saskatoon, Saskatchewan

    Default Re: Electrical Problem in old garage/shed

    Quote Originally Posted by Gunny View Post
    Along the line of checking any junction boxes for loose connectors - are there any splices in the lines between the house and the shed? A lot of the old splices amounted to twisting the wires together and taping over them. Very easy to have corrosion build up in them and weaken he conductivity.
    X 2.

    I wish the OP would come back and give us some more information on what he found.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Started Garage/Shed this week
    By efam3300 in forum Projects
    Replies: 14
    Last Post: 07-27-2012, 10:27 PM
  2. Shed roof garage addition
    By Ugarte in forum Projects
    Replies: 7
    Last Post: 04-09-2012, 12:51 PM
  3. Pole shed or garage??
    By kevinwak in forum Projects
    Replies: 10
    Last Post: 09-30-2011, 05:40 PM
  4. picutres of you tractor in the garage or shed wanted
    By deereboy72 in forum Owning/Operating
    Replies: 66
    Last Post: 12-10-2009, 09:17 PM
  5. Questions on 48x24 Garage/Tractor Shed
    By volunteer in forum Projects
    Replies: 2
    Last Post: 07-22-2007, 08:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
© 2014 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.