I submitted for a building permit two weeks ago for a pole barn that is going up in May. It was designed and will be built by CHA Pole Barns from PA. Well, the building inspector had some problems with the plans, listed below with my comments:
1) need roof truss engineering specs with seal of certification
OK, fair enough
2) need specs on species and types of wood used for framing, roof sheathing, and siding
OK, fine, can do, though seems overkill since lumber types were already specified
3) need to add wall diagonal bracing to corner posts to prevent shear
I would think poles set 42" in the ground would be more than enough to resist shear???
4) need to notch 2x12 wall headers into posts, and headers should be laminated together
I have always seen them bolted or spiked onto side of poles (so outer header is inline with wall girts). Not even sure there's enough meat on a 4x6 to notch in double 2x12 headers.
5) need registered engineer to sign off on 16" cookie used for footing in my soil conditions
Great, will cost me $200-250 just to have someone tell me what we already know
I have asked CHA to provide what info they can on items 1-4, and I will handle the footing issue with a local engineer. But I was wondering if anyone else has run into issues like this for pole barns? I thought the construction and design was simple enough to be idiot proof.
For example, item 3 seems odd to me. There are dozens of pole barns along the road to my house, and I am sure I've never seen diagonal braces. The main difference is that those properties are zoned agricultural and the buildings are for agricultural use, so they probably didn't have to mess with permits. My land is also zoned agricultural, but in a residential area and I can't claim agricultural use.
1) need roof truss engineering specs with seal of certification
OK, fair enough
2) need specs on species and types of wood used for framing, roof sheathing, and siding
OK, fine, can do, though seems overkill since lumber types were already specified
3) need to add wall diagonal bracing to corner posts to prevent shear
I would think poles set 42" in the ground would be more than enough to resist shear???
4) need to notch 2x12 wall headers into posts, and headers should be laminated together
I have always seen them bolted or spiked onto side of poles (so outer header is inline with wall girts). Not even sure there's enough meat on a 4x6 to notch in double 2x12 headers.
5) need registered engineer to sign off on 16" cookie used for footing in my soil conditions
Great, will cost me $200-250 just to have someone tell me what we already know
I have asked CHA to provide what info they can on items 1-4, and I will handle the footing issue with a local engineer. But I was wondering if anyone else has run into issues like this for pole barns? I thought the construction and design was simple enough to be idiot proof.
For example, item 3 seems odd to me. There are dozens of pole barns along the road to my house, and I am sure I've never seen diagonal braces. The main difference is that those properties are zoned agricultural and the buildings are for agricultural use, so they probably didn't have to mess with permits. My land is also zoned agricultural, but in a residential area and I can't claim agricultural use.