I know we have alot of HVAC experts on here, so I figured I'd run my issues by you all while I am waiting on hold for tech support.
This is the geothermal pump I have 4 Ton 2 Stage GeoCool Geothermal Heat Pump
this is the T-stat Pro1 Thermostats | T955WH - Wireless Universal Thermostat
Not really a fan of this t-stat for starters. It seems there is quite a bit of lag built into its temp sensors. IE: I have swing set for 0.7 degrees. So if I have t-stat set for 68......It will turn on the furnace once it gets down to 67.3, and off again once it hits 68.7......or its supposed to. I dont so much have a problem with the on time, as the house cools off slowly, the t-stat is fairly accurate in that regard.
The issue is once the furnace kicks on, the temp in the house climbs fairly quickly. Quite a bit faster than the t-stat registers. the result is....by the time the t-stat "thinks" its at 68.7 and shuts the furnace off, its actually at ~72-73 degrees. Has nothing to do with t-stat calibration, just timing. Cause after the furnace has kicked off, 20-30 minutes later the t-stat has finally caught up to reality and shows its 72 in the house. This causes alot larger temp swings than I would like. So wondering if all digital t-stats are like that ?
But that isnt even my real issue. My issue is a lingering ~18v on wire Y1 coming from the t-stat.....EVEN when the T-stat is off and not calling for heat.
This lingering 18v is NOT enough that it is telling the compressor to run, however it is enough to trick my desuperheater DHW pump into running. Which is one of these:
http://www.bardhvac.com/digcat/volume_3_cd/install_pdf_file/2100-517.pdf
Probably been doing it since I installed the unit back in the spring, but didnt notice it until just now. Was doing some basement remodeling and kept hearing the bard cycling. Reading the description of how it operates, it is only supposed to come on when there is a 24v signal on Y1 (telling the compressor to run). From that point, it will run for 1.5 minutes. At that point it will check the thermistors on the incoming water and outgoing water. If it aint seeing a 2+ degree difference, it shuts off. It moniters the incoming and outgoing water to be sure there is enough temp difference, if not, it shuts off. If signal is lost from Y1, it shuts off.
Well, with Y1 having a lingering 18v on it, every 10 minutes it kicks on and circulates hot water through my desuperheater. EVEN IF the furnace IS NOT running. After 1.5 minutes it shuts off because there is no temp difference (or a negative difference.) 10 minutes later, rinse and repeat.
Any idea why the t-stat is leaving 18v linger on the Y1 wire?
This is the geothermal pump I have 4 Ton 2 Stage GeoCool Geothermal Heat Pump
this is the T-stat Pro1 Thermostats | T955WH - Wireless Universal Thermostat
Not really a fan of this t-stat for starters. It seems there is quite a bit of lag built into its temp sensors. IE: I have swing set for 0.7 degrees. So if I have t-stat set for 68......It will turn on the furnace once it gets down to 67.3, and off again once it hits 68.7......or its supposed to. I dont so much have a problem with the on time, as the house cools off slowly, the t-stat is fairly accurate in that regard.
The issue is once the furnace kicks on, the temp in the house climbs fairly quickly. Quite a bit faster than the t-stat registers. the result is....by the time the t-stat "thinks" its at 68.7 and shuts the furnace off, its actually at ~72-73 degrees. Has nothing to do with t-stat calibration, just timing. Cause after the furnace has kicked off, 20-30 minutes later the t-stat has finally caught up to reality and shows its 72 in the house. This causes alot larger temp swings than I would like. So wondering if all digital t-stats are like that ?
But that isnt even my real issue. My issue is a lingering ~18v on wire Y1 coming from the t-stat.....EVEN when the T-stat is off and not calling for heat.
This lingering 18v is NOT enough that it is telling the compressor to run, however it is enough to trick my desuperheater DHW pump into running. Which is one of these:
http://www.bardhvac.com/digcat/volume_3_cd/install_pdf_file/2100-517.pdf
Probably been doing it since I installed the unit back in the spring, but didnt notice it until just now. Was doing some basement remodeling and kept hearing the bard cycling. Reading the description of how it operates, it is only supposed to come on when there is a 24v signal on Y1 (telling the compressor to run). From that point, it will run for 1.5 minutes. At that point it will check the thermistors on the incoming water and outgoing water. If it aint seeing a 2+ degree difference, it shuts off. It moniters the incoming and outgoing water to be sure there is enough temp difference, if not, it shuts off. If signal is lost from Y1, it shuts off.
Well, with Y1 having a lingering 18v on it, every 10 minutes it kicks on and circulates hot water through my desuperheater. EVEN IF the furnace IS NOT running. After 1.5 minutes it shuts off because there is no temp difference (or a negative difference.) 10 minutes later, rinse and repeat.
Any idea why the t-stat is leaving 18v linger on the Y1 wire?