I have metal tipped quality extinguishers but they have set for 10 years. Will tapping be OK or replace them?
If yours are serviceable, they need to be done. contact your local extinguisher company.
Six-Year Maintenance
Every 6 years, stored pressure fire extinguishers that require a 12-year hydrostatic test (e.g. dry chemical extinguishers) must be emptied and proper maintenance procedures performed [see NFPA10(98), Sec. 4-4.3]. The exception to this rule is nonrechargeable extinguishers, which are required to be removed from service 12 years from the date of manufacture. Again, this maintenance must be performed by an approved extinguisher servicing company.
Hydrostatic testing At certain intervals, fire extinguishers are required to be pressure tested using water or some other noncompressible fluid to help prevent unwanted failure or rupture of the cylinder [see NFPA 10(98), Chapter 5]. This is called hydrostatic testing and includes both an internal and external examination of the cylinder. Because this testing requires special training and equipment, it needs to be performed by an approved extinguisher servicing company.
Hydrostatic testing intervals for fire extinguishers are outlined in NFPA 10(98), Sec. 5-2 and Table 5-
2. Test intervals for some of the most commonly found extinguishers are as follows:
Pressurized water, carbon dioxide and wet chemical extinguishers every 5 years
Dry chemical extinguishers every 12 years
As mentioned earlier, the exception to the rule
for hydrostatic testing is nonrechargeable
stored pressure extinguishers (e.g. dry chemical extinguish
ers), which are required to be removed from service 12 years from the date of manufacture.