To have a remote panel (seems like a subpanel), code (NEC) actually does not allow the neutral and common to be bonded in that panel. The reason is quite simple, neutral currents will start to flow through the ground line (since it is effectively paralleled with the ground line). This can cause the ground at the subpanel to have a potential above "real" ground (pipes, earth, concrete, etc). This means that you could feel some voltage between a socket wall plate and the kitchen sink.
There are some who think that grounding the subpanel to a local ground rod is a better way. If this is done and the two grounds are interconnected, additional ground circulating currents can occur, leading to more risk.
For safety and code the bonding should not be done in the subpanel, and only at the main service panel. If you are really worried about ground related surge issues (due to lightning, etc), the proper way is to feed the subpanel from a 1:1 isolation transformer. The sub can than be grounded locally and bonded. Best solution but can be quite expensive.
paul