    Default Tool and equipment wiring question for the electricians

    I know there are some electricians out there, so I'm hoping someone can help me with this:

    we all know you can attach multiple receptacles to a single 120V circuit, providing the breaker and wire are sized to satisfy the sum of everything attached. This would be like having a drop light plugged in to one, a fan running on another, and then using a drill on another. The sum of all of these would be less than the 15A (assumed) circuit.

    Can you do anything similar with 240V circuits and satisfy code? Say you have an existing 240V/40A circuit: is there any way to attach two separate 230V/8A tools to it? I'm trying to figure a way to avoid having to plug and unplug these, as it is sometimes awkward having to crawl around to do this. I don't want to run another circuit because the building is all wired and the inside is sheathed. I'll stick to the plug and unplug method if I have to, but logic would say that it should be able to be done.

  2. #2
    Gold Member
    Join Date
    Jan 2006
    Posts
    350
    Location
    Stone Mountain, GA
    Tractor
    Case 1210, Mitsubishi D2050

    Default Re: Tool and equipment wiring question for the electricians

    As long as the wire is sized adequately (#8 CU or #6 AL wire probably depending on the run) and all receptacles are sized for the circuit capacity, then you are good. For 40 amp circuits, 50 amp receptacles and cord sets (to the devices) are most commonly used.

  3. #3
    Platinum Member
    Join Date
    Mar 2010
    Posts
    790
    Location
    Maine

    Default Re: Tool and equipment wiring question for the electricians

    Quote Originally Posted by ThomasH View Post
    As long as the wire is sized adequately (#8 CU or #6 AL wire probably depending on the run) and all receptacles are sized for the circuit capacity, then you are good. For 40 amp circuits, 50 amp receptacles and cord sets (to the devices) are most commonly used.
    the circuit is capable of carrying 40A - I had an extra length of 8-3 wire, so when i put the box in, i ran the extra circuit for some sort of future expansion. i actually used a 30A breaker and 30A dryer style receptacle so it wouldn't be confused with the 50A welder circuit. There is currently a double width box in the wall with the 30A receptacle and I'd like to change it over to hold two small receptacles. I haven't looked, but whatever the smallest receptacle is that will take a #8 wire is what I'd like to use, if there is anything that will fit that way.

  4. #4
    Platinum Member
    Join Date
    Mar 2010
    Posts
    790
    Location
    Maine

    Default Re: Tool and equipment wiring question for the electricians

    I think I found the answer to my question. I found images for a 6-20 duplex receptacle. The only issue would be the wires. Can you crimp ring / spade terminals on a wire in order to connect to the receptacle? I doubt a #8 wire can connect directly to a 20A receptacle. I'd change the breaker to a 20A too, of course.

  5. #5
    Member Murfster3's Avatar
    Join Date
    Jan 2013
    Posts
    29
    Location
    Goshen
    Tractor
    Mahindra

    Default Re: Tool and equipment wiring question for the electricians

    The one thing you have to keep in mind is what ever size the breaker that's the smallest size receptacle amperage wise. Example 120v circuit 20amp breaker all recepts 20amps. 240v 40 amp circuit nothing smaller than 40amp recepts you can go bigger but if you go smaller you have no protection

Similar Threads

  1. Emergency generator question for you electricians
    By HCJtractor in forum Welding
    Replies: 19
    Last Post: 04-04-2011, 08:15 AM
  2. Question for the tractor electricians
    By RFB in forum Customization
    Replies: 38
    Last Post: 02-21-2008, 05:50 PM
  3. Wiring gurus... a question about wiring factory work lamps
    By bxowner in forum John Deere Owning/Operating
    Replies: 3
    Last Post: 12-01-2007, 09:49 AM
  4. Replies: 55
    Last Post: 06-19-2006, 12:31 AM
  5. Northern Tool and Equipment
    By DaveNH in forum Related Topics
    Replies: 11
    Last Post: 10-23-2001, 03:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
© 2014 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.