    Default New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    I ordered a Lincoln 256 Power Mig last week and it should be here this week. I'm trying to get the shop ready for it. Lincoln manual shows a three hole, 60 amp receptacle (see picture). (Machine draws 52 amps wide open) I have not been able to Google a 60 amp. The ones I find are only 50 amps. Question is where do you find a three hole 60 amp receptacle like that or do I really even need one?

    -50-amp-receptacle-jpg

  2. #2
    Elite Member Shield Arc's Avatar
    Join Date
    Jan 2009
    Posts
    4,138
    Location
    Figuring the picking points of jelly donuts.
    Tractor
    John Deere, 4200

    Default Re: New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    This is what I use, I've had my machines at 200 + amps. No problems at all in the 12-years I've been using them.

    Shop Pass & Seymour/Legrand 30/50-Amp 125/250-Volt black 3 wire angle plug at Lowes.com


    Miller Dynasty 300.
    Lincoln V350-Pro w/pulse.
    Lincoln LF-72 wire feeder.
    Lincoln SG Spool gun.

    Lincoln LN-25.
    1937 IdealArc-300.
    Everlast PowerArc 200.
    Everlast PowerArc 300.
    3 Lincoln SA-200s.
    1800 Ellis saw.
    Hypertherm Powermax 1250, CNC table.
    PROFAX Welding Positioner.
    JD2 model 3.

  3. #3
    Advertiser Mark @ Everlast's Avatar
    Join Date
    May 2010
    Posts
    1,889
    Location
    South GA

    Default Re: New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    The confusion likely comes from the fact that the NEC allows a de-rating of input components such as wire and outlet size based off the duty cycle of the welder. Since I don't think the 256 has a 100% duty cycle, it's likely that it has more than enough capacity to handle the derated current (though this is a question better answered by a locally licensed electrician in your area).
    Mark Lugo
    Everlast Welders
    http://www.everlastgenerators.com/

    Need a welder? Give me a call at (877) 755-9353 ext 204!

  4. #4
    New Member
    Join Date
    Sep 2012
    Posts
    12
    Location
    Smithville, mo
    Tractor
    John Deere 4105

    Default Re: New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    I wonder if I should also than use a 50 amp breaker? Didn't notice the note at the bottom of that page of the manual that talks about the welder max input being 52 amps - that is with the welder at 250 amps AND the auxillary 15 amp receptacle at full draw. I should be fine. I won't use both at full draw at the same time.

  5. #5
    Elite Member Shield Arc's Avatar
    Join Date
    Jan 2009
    Posts
    4,138
    Location
    Figuring the picking points of jelly donuts.
    Tractor
    John Deere, 4200

    Default Re: New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    I think my welder and plasma outlets are on individual 60-amp breakers. Never once through a breaker, even when I had my Linde VI-206 Mig welder wide open running 1/16-inch wire.


    Miller Dynasty 300.
    Lincoln V350-Pro w/pulse.
    Lincoln LF-72 wire feeder.
    Lincoln SG Spool gun.

    Lincoln LN-25.
    1937 IdealArc-300.
    Everlast PowerArc 200.
    Everlast PowerArc 300.
    3 Lincoln SA-200s.
    1800 Ellis saw.
    Hypertherm Powermax 1250, CNC table.
    PROFAX Welding Positioner.
    JD2 model 3.

  6. #6
    Silver Member dkhntr04's Avatar
    Join Date
    Sep 2010
    Posts
    169
    Location
    Northern MN
    Tractor
    Deere 3720 Cab

    Default Re: New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    Quote Originally Posted by Mark @ Everlast View Post
    The confusion likely comes from the fact that the NEC allows a de-rating of input components such as wire and outlet size based off the duty cycle of the welder. Since I don't think the 256 has a 100% duty cycle, it's likely that it has more than enough capacity to handle the derated current (though this is a question better answered by a locally licensed electrician in your area).
    Mark, you are correct on that. I read and researched that portion of the NEC a few years ago when wiring my shop.

    OP, use the receptacle in you picture, you should be good to go.

  7. #7
    Super Member Gary Fowler's Avatar
    Join Date
    Jun 2008
    Posts
    7,890
    Location
    Bismarck Arkansas
    Tractor
    2009 Kubota RTV 900, 2009 Kubota B26 TLB & 2010 model LS P7010

    Default Re: New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    I would use the one ShieldArc referenced. I use the same thing on my 300 amp Miller machine with a 50 amp breaker with wire sized accordingly for the amperage. Never had an issue with breaker or plug. It is a much heavier plug than the one you(OP) have pictured and plug and receptacle are available at any hardware store. You can get flush mount or external mount depending on your wiring (wiring ran outside the walls in conduit, just use the external mount type. These plugs are commonly used on electric dryer connections also.
    2010 LS P-7010C 20F/20R gear tractor & FEL, 2009 Kubota B 26 TLB, RTV 900 Kubota,17 foot Lund boat with 70HP motor, 2012-20 ft 12k GVW trailer, 2011- 52" Craftsman ZTR mower, 2013 Ferris Zero Turn, 3 weed whackers, pressure washer, leaf blowers, 7 foot bush hog, 8 foot landscape rake , 8 foot 3 PH disc, 2 row cultivator, 350 amp Miller AC/DC welding machine and all the tools needed to keep them all repaired and running.

  8. #8
    Super Member Gary Fowler's Avatar
    Join Date
    Jun 2008
    Posts
    7,890
    Location
    Bismarck Arkansas
    Tractor
    2009 Kubota RTV 900, 2009 Kubota B26 TLB & 2010 model LS P7010

    Default Re: New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    Quote Originally Posted by kkirt1 View Post
    I wonder if I should also than use a 50 amp breaker? Didn't notice the note at the bottom of that page of the manual that talks about the welder max input being 52 amps - that is with the welder at 250 amps AND the auxillary 15 amp receptacle at full draw. I should be fine. I won't use both at full draw at the same time.
    The breaker size is to protect the wiring so you have to size the wiring according to what size breaker you need, not to the capacity of the machine. It all has to be rated to match. Wire size is somewhat limited to run length also but NEC will give you the minimum size wire for whatever breaker that you decide to put in.
    I have an old 2002 NEC (info should still be applicable) that lists the following regarding sizing of wire and breaker: I think your machine would fall under item 1. Looks like you would need number 6 wire in copper or aluminum to feed this 50 amp circuit.
    (A) Individual Welders. The rated ampacity for conductors
    for individual welders shall comply with the following:
    (1) The ampacity of the supply conductors for a welder
    that may be operated at different times at different values
    of primary current or duty cycle shall not be less
    than 70 percent of the rated primary current for seam
    and automatically fed welders and 50 percent of the
    rated primary current for manually operated nonautomatic
    welders.
    (2) The ampacity of the supply conductors for a welder
    wired for a specific operation for which the actual primary
    current and duty cycle are known and remain
    unchanged shall not be less than the product of the
    actual primary current and the multiplier specified in
    Table 630.31(A) for the duty cycle at which the welder
    will be operated.
    Last edited by Gary Fowler; 03-07-2013 at 12:22 PM.
    2010 LS P-7010C 20F/20R gear tractor & FEL, 2009 Kubota B 26 TLB, RTV 900 Kubota,17 foot Lund boat with 70HP motor, 2012-20 ft 12k GVW trailer, 2011- 52" Craftsman ZTR mower, 2013 Ferris Zero Turn, 3 weed whackers, pressure washer, leaf blowers, 7 foot bush hog, 8 foot landscape rake , 8 foot 3 PH disc, 2 row cultivator, 350 amp Miller AC/DC welding machine and all the tools needed to keep them all repaired and running.

  9. #9
    Silver Member Todd727's Avatar
    Join Date
    Apr 2012
    Posts
    200
    Location
    Holly Springs, MS
    Tractor
    Case CX90, IH 1086

    Default Re: New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    Your machine will come with the plug. You need this receptacle to match: Shop Cooper Wiring Devices 50-Amp 250-Volt Black 3-Wire Plug at Lowes.com

    The manual states to use a 60amp breaker and a minimum of #10 AWG wire. Shop Square D Homeline 60-Amp Double-Pole Circuit Breaker at Lowes.com

  10. #10
    Super Member Gary Fowler's Avatar
    Join Date
    Jun 2008
    Posts
    7,890
    Location
    Bismarck Arkansas
    Tractor
    2009 Kubota RTV 900, 2009 Kubota B26 TLB & 2010 model LS P7010

    Default Re: New Lincoln 256 Power Mig - Manual calls for 60 amp receptacle... hmmmm?

    Quote Originally Posted by Todd727 View Post
    Your machine will come with the plug. You need this receptacle to match: Shop Cooper Wiring Devices 50-Amp 250-Volt Black 3-Wire Plug at Lowes.com

    The manual states to use a 60amp breaker and a minimum of #10 AWG wire. Shop Square D Homeline 60-Amp Double-Pole Circuit Breaker at Lowes.com
    That manual is a POS for advice, #10 wire wont carry a welding machine load of 30 amps much less 60. OP stated the machine rated input load was 52 amps so per NEC you can take that X 70% for the rated wiring and breaker. This is because the machine will never be ran full time at max load due to the duty rating. My 300 AMP Miller CC/CV AC/DC machine only pull 50 amp at full load with a 60% duty cycle. I have it on a 50 amp breaker which is above the code requirements.
    2010 LS P-7010C 20F/20R gear tractor & FEL, 2009 Kubota B 26 TLB, RTV 900 Kubota,17 foot Lund boat with 70HP motor, 2012-20 ft 12k GVW trailer, 2011- 52" Craftsman ZTR mower, 2013 Ferris Zero Turn, 3 weed whackers, pressure washer, leaf blowers, 7 foot bush hog, 8 foot landscape rake , 8 foot 3 PH disc, 2 row cultivator, 350 amp Miller AC/DC welding machine and all the tools needed to keep them all repaired and running.

Page 1 of 2 12 LastLast

Similar Threads

  1. Millermatic 252 or Lincoln Power MIG 256
    By OkieDave in forum Welding
    Replies: 25
    Last Post: 09-22-2012, 09:49 AM
  2. Lincoln 140 mig welder from lowes
    By mcgill72143 in forum Welding
    Replies: 11
    Last Post: 04-07-2011, 09:24 PM
  3. Lincoln MIG-Pak 180
    By dmay in forum Welding
    Replies: 25
    Last Post: 03-31-2011, 02:11 PM
  4. New Lincoln 3200HD 140amp Mig Welder
    By davemhughes in forum Build-It Yourself
    Replies: 6
    Last Post: 02-24-2007, 10:23 PM
  5. Bought new Lincoln mig 140T. Got questions.
    By hz293 in forum Build-It Yourself
    Replies: 14
    Last Post: 11-13-2006, 06:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
© 2014 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.