Hi collective experts,
We are building a new house, about 2500 sqft with typical loads, probably not over 200A (not yet fully calculated out). But I'd like to use two separate load centers, one in the basement near the major loads (heat pump system w/2 10kw heat strips, conventional water heater, buzz box welder, 3-5 HP air compressor) - totalling 200A or less, and another load center on the main floor for everyhting else, also 200A or less.
I have my 400A rated meter base with the necessary multiple load-side lugs, and I know that I cannot run the conductors from the meter base more than 2 ft inside the structure with out a fused disconnect, so I plan for two 200A disconnects just inside the foundation wall underneath the meter base. The meter base as supplied by the local EMC has two knockouts in the bottom, each capable of up to 4" conduit. One of these will be the incoming service lateral (underground) which the EMC specifies must be in 3" sch 80 conduit.
So finally, my question(s) - can I run BOTH sets of conductors to the two disconnects for the two load centers in a SINGLE 3" or 4" conduit, and then TEE the conduit inside the structure to the two disconnects? I assume that for NEC purposes, this is considered to be six conductors, right? I plan to mount the two disconnects right beside each other, and then plan to conduit (2") from each disconnect to it's respective load center. The total wire run from meter base to the disconnects will be about 3-4 ft. What ampacity derating will I need to include when figuring my conductor size?
I will sure appreciate advice and guidance that might save me from buying a bunch of disconnects/parts that won't pass inspection!
- Jay
We are building a new house, about 2500 sqft with typical loads, probably not over 200A (not yet fully calculated out). But I'd like to use two separate load centers, one in the basement near the major loads (heat pump system w/2 10kw heat strips, conventional water heater, buzz box welder, 3-5 HP air compressor) - totalling 200A or less, and another load center on the main floor for everyhting else, also 200A or less.
I have my 400A rated meter base with the necessary multiple load-side lugs, and I know that I cannot run the conductors from the meter base more than 2 ft inside the structure with out a fused disconnect, so I plan for two 200A disconnects just inside the foundation wall underneath the meter base. The meter base as supplied by the local EMC has two knockouts in the bottom, each capable of up to 4" conduit. One of these will be the incoming service lateral (underground) which the EMC specifies must be in 3" sch 80 conduit.
So finally, my question(s) - can I run BOTH sets of conductors to the two disconnects for the two load centers in a SINGLE 3" or 4" conduit, and then TEE the conduit inside the structure to the two disconnects? I assume that for NEC purposes, this is considered to be six conductors, right? I plan to mount the two disconnects right beside each other, and then plan to conduit (2") from each disconnect to it's respective load center. The total wire run from meter base to the disconnects will be about 3-4 ft. What ampacity derating will I need to include when figuring my conductor size?
I will sure appreciate advice and guidance that might save me from buying a bunch of disconnects/parts that won't pass inspection!
- Jay