Running Welders off Generators

   #1  

Furu

Platinum Member
Joined
Nov 20, 2009
Messages
981
Location
.
Tractor
.
I know that the newer style Inverter Welders should only be run off "clean" pure sine-wave generator power.
I know that one specific poster has had great luck and loves his Honda EU2000I generators and that is not what I am asking about as they are only 120volt capable.

My question is about 240 volt 10 KW generators that have a modified sine-wave output and older welders that have transformers in them not the inverter technology.

Is there a problem running transformer welders off this not pure sine-wave output?

Maybe Mark will chime in as I think he has specific knowledge in this area.
 
   #2  

MinnesotaDaveChalmers

Platinum Member
Joined
Jun 13, 2012
Messages
659
Location
Big Lake/Monticello, MN
Tractor
WD Allis Chalmers
If you find out the THD and call the welder manufacturer they should be able to give a definitive answer.
I have an older Generac 5000/6250 and Miller told me it was fine to run my Maxstar 150s off it.
It ran great on 240v (likely due to power factor correction in the welder smoothing out the power)

Lincoln told me not to run my Invertec v250-s off that source as the voltage fluctuated out of the welders +/- for input voltage.

My older 120v migs ran terrible off that power source (an old Craftsman/Century and a small Lincoln flux core only machine)
I didn't dare plug in my millermatic 210 and try that - too expensive :)
 
  
  • Thread Starter
#3  
OP
F

Furu

Platinum Member
Joined
Nov 20, 2009
Messages
981
Location
.
Tractor
.
If you find out the THD and call the welder manufacturer they should be able to give a definitive answer.
I have an older Generac 5000/6250 and Miller told me it was fine to run my Maxstar 150s off it.

Without an O-scope I don't know if I could get that. I do not have an O-scope either. Generac manuals and specs that I have seen do not seem to present that data. Either they do not want the consumer to have it or they do not think it is anything that the consumer is interested in.
 
   #4  

Sodo

Elite Member
Joined
Apr 21, 2012
Messages
3,142
Location
Cascade Mtns of WA state
Tractor
Kubota B-series & Mini Excavator
Funny you posted this a couple hours before my generator post. These two posts are different but may have some overlap.

It is my understanding that a transformer could not care less about the power it receives, it just transforms whatever it gets. But that's not to say the 'weld' doesn't care - I can't offer any knowledge about that part. Also a generator that creates electricity by a turning armature is (almost by definition) outputs a "pure sine wave", but the frequency is determined by the gas motor's RPM. So if the motor pulls down, the frequency reduces accordingly.

I got a little nervous from your note (I have an inverter welder MultiMatic200) so I called MillerWeld Tech suppt. They said the MM200 is generally not affected by dirty power, so good news for me anyway.
 
Last edited:
   #5  

MinnesotaDaveChalmers

Platinum Member
Joined
Jun 13, 2012
Messages
659
Location
Big Lake/Monticello, MN
Tractor
WD Allis Chalmers
Without an O-scope I don't know if I could get that. I do not have an O-scope either. Generac manuals and specs that I have seen do not seem to present that data. Either they do not want the consumer to have it or they do not think it is anything that the consumer is interested in.

The Generac XP series is the one with low Total Harmonic Distortion <5%

Most companies I've seen in recent years have been listing THD (only if it's good) since there are so many sensitive electronics being run now days.

They will tell you if you ask since companies would rather you not wreck electronics and then blame them :)
 
   #6  

nova3930

Gold Member
Joined
May 5, 2014
Messages
258
Location
North Alabama
Tractor
Yanmar 2420D
I can't speak in general, but specifically I have yet to be able to get a good penetrating weld on anything with my older coleman 7.5kw generator and the old miller thunderbolt buzzbox I have.
 
   #7  

MinnesotaDaveChalmers

Platinum Member
Joined
Jun 13, 2012
Messages
659
Location
Big Lake/Monticello, MN
Tractor
WD Allis Chalmers
I can't speak in general, but specifically I have yet to be able to get a good penetrating weld on anything with my older coleman 7.5kw generator and the old miller thunderbolt buzzbox I have.

Buzz boxes are real power hogs when it comes to Inrush Current.

Check out what Lincoln says about running their version off a generator:
Question: It appears that a 5000 or 6000 watt 230 VAC generator is large enough to operate my AC/DC 225/125 welder using a 1/8 inch diameter E6010. Please confirm.

Response: It does appear (if you do the math) that you should be able to use 1/8 in. and smaller diameter electrodes with an AC/DC 225/125 powered by a 5000 or 6000 watt generator. Unfortunately, the design of the transformer on the AC/DC 225/125 is not efficient enough to be powered by a small generator. If you try and weld with this combination you will most likely experience the electrode being hard-to-strike and also the electrode frequently sticking to the work.

If you are fortunate to establish an arc, the arc will tend to pop out frequently. Also, there will not be adequate heat input to the work, resulting in low weld quality (poor fusion), and poor bead appearance.

To successfully run your AC/DC 225/125 welder you would need a minimum of a 15,000 watt AC generator.
 
   #8  

nova3930

Gold Member
Joined
May 5, 2014
Messages
258
Location
North Alabama
Tractor
Yanmar 2420D
Buzz boxes are real power hogs when it comes to Inrush Current.

Check out what Lincoln says about running their version off a generator:

You just confirmed what I had suspected but had never properly investigated. Even a 1/8" 6013 is a nightmare to get to strike on the generator and has even worse penetration than normal. Plug it into wall power and it burns like crazy.
 
  
  • Thread Starter
#9  
OP
F

Furu

Platinum Member
Joined
Nov 20, 2009
Messages
981
Location
.
Tractor
.
The Generac XP series is the one with low Total Harmonic Distortion <5%

Most companies I've seen in recent years have been listing THD (only if it's good) since there are so many sensitive electronics being run now days.

They will tell you if you ask since companies would rather you not wreck electronics and then blame them :)

I have a Generac 10000EXL that I have owned since 1999. It is not the XP series which is much newer than mine.

It is interesting that if different volt meters are hooked up to an outlet at the same time you can get different voltage readings because different volt meters calculate/measure voltage differently. Thus I know the waveform is not pure.
 
   #10  

MinnesotaDaveChalmers

Platinum Member
Joined
Jun 13, 2012
Messages
659
Location
Big Lake/Monticello, MN
Tractor
WD Allis Chalmers
You just confirmed what I had suspected but had never properly investigated. Even a 1/8" 6013 is a nightmare to get to strike on the generator and has even worse penetration than normal. Plug it into wall power and it burns like crazy.

That would be frustrating to the point of pushing the welder down a hill and lighting it on fire....:mur:

I was pleasantly surprised how nicely my little maxstar worked on a generator - new technology makes me uneasy...and I still consider inverters to be black magic voodoo ;)

My favorite welder is my 1963 Airco stick/tig - 900 lbs of awesome!! :D
 
   #11  

MinnesotaDaveChalmers

Platinum Member
Joined
Jun 13, 2012
Messages
659
Location
Big Lake/Monticello, MN
Tractor
WD Allis Chalmers
I have a Generac 10000EXL that I have owned since 1999. It is not the XP series which is much newer than mine.

It is interesting that if different volt meters are hooked up to an outlet at the same time you can get different voltage readings because different volt meters calculate/measure voltage differently. Thus I know the waveform is not pure.

That is very interesting, never tried that before. Do they read the same when plugged into the same house outlet?

....I'm gonna have to start trying that now :)
 
   #12  

nova3930

Gold Member
Joined
May 5, 2014
Messages
258
Location
North Alabama
Tractor
Yanmar 2420D
That would be frustrating to the point of pushing the welder down a hill and lighting it on fire....:mur:

Oh it was. I'm no master welder, not by a long shot, but prior to I could always strike and weld metal with a 6013. The things are darn near idiot proof even if they don't penetrate well.

But I was in the position of having broken my skid steer forks in the middle of the land we were clearing for our new house, with no power and had to get them back together. After fighting with it for a hour, the neighbor moseys over and informs me that he's got a nice Millermatic 252 MiG and oh BTW he welds professionally at the United Launch Alliance rocket plant up the highway and would be happy to weld them up for me. :mur:

I promptly carried the forks across the street to his place and let him go to work while I went for an after-the-job-is-done 6 pack. :drink:
 
   #13  

Big Barn

Super Member
Joined
Aug 20, 2013
Messages
6,923
Location
Victoria, B C
Tractor
More than 40 over the years. Ten at any one time. Mostly Ford and New Holland
I promptly carried the forks across the street to his place and let him go to work while I went for an after-the-job-is-done 6 pack. :drink:




That without a doubt is the best welding post I've read today

Terry
 
   #15  

nova3930

Gold Member
Joined
May 5, 2014
Messages
258
Location
North Alabama
Tractor
Yanmar 2420D
LOL, I'm not too proud to admit when it's time to pay the man rather than fumble through as an amateur, even if payment is a frosty adult beverage.
 
  
  • Thread Starter
#16  
OP
F

Furu

Platinum Member
Joined
Nov 20, 2009
Messages
981
Location
.
Tractor
.
That is very interesting, never tried that before. Do they read the same when plugged into the same house outlet?

....I'm gonna have to start trying that now :)

Yes down to the 0.1 volt decimal point. As was explained to me it is because of the method of measurement. Cheap voltmeters vs not so cheap voltmeters.

V (rms) vs V (pep) Cheap AC voltmeters will just measure the peak voltage, and scale the reading as if it were a perfect sine wave. More to it than that but that is the general idea.

I also find on my Honda Inverter generators EU2000I that they read the same voltage on each(because it is a pure sine wave)
 
   #17  

dragoneggs

Super Star Member
Joined
Jun 9, 2013
Messages
14,596
Location
Seabeck, Washington
Tractor
Kubota BX-25D, Kubota Z122RKW-42
Great topic Furu! I am also wondering what I can manage with my Honda EU3000iS which I use for backup power to the house for the essentials. I have a mechanical interlock so I can directly feed my service panel. Absolutely love this generator and it can be paired with another for a total of 6000watts. Dang expensive but by far the best generator I have used. Wondering if anyone has an idea of material thickness I could weld with 3000watts and 6000watts??? Oh and yes it is only 110v as far as I know.
 
   #18  

Soundguy

Old Timer
Joined
Mar 11, 2002
Messages
52,238
Location
Central florida
Tractor
RK 55HC,ym1700, NH7610S, Ford 8N, 2N, NAA, 660, 850 x2, 541, 950, 941D, 951, 2000, 3000, 4000, 4600, 5000, 740, IH 'C' 'H', CUB, John Deere 'B', allis 'G', case VAC
Buzz boxes are real power hogs when it comes to Inrush Current.

Check out what Lincoln says about running their version off a generator:

I have a 12.5k northern tool pto generator mounted on a carry all / platform, and have had my hobart 235XL AC mounted with it when I was building the farm up before we had power run out here. I used to to weld on gates and such or power up the well. Never tried high settings.. but 6011 at 100a or so and on 1/8 rods ran just like it was on line power. I realize much of that has to do with the tractors governor ability to maintain rpm stability under load too... and not so much the generator itself or the welding machine..e tc.

just tossing that out as an observation of what i have experienced on my farm for light welding and water pump / power tool usage ( skill saws, 1/2" drills, etc.. ), and not a endorsement of any other specific suitability for use.. etc.
 
   #19  

Sodo

Elite Member
Joined
Apr 21, 2012
Messages
3,142
Location
Cascade Mtns of WA state
Tractor
Kubota B-series & Mini Excavator
Great topic Furu! I am also wondering what I can manage with my Honda EU3000iS which I use for backup power to the house for the essentials. I have a mechanical interlock so I can directly feed my service panel. Absolutely love this generator and it can be paired with another for a total of 6000watts. Dang expensive but by far the best generator I have used. Wondering if anyone has an idea of material thickness I could weld with 3000watts and 6000watts??? Oh and yes it is only 110v as far as I know.

I think 3000iS has a 230v outlet. Miller Tech said to weld 3/8" with the MultiMatic200 I'd need 7200W. I don't know how the 211 would behave. My pair of Honda EU2000i can weld on the 3/16" preset, but the generator overspeeds to get it going - tells me it's over the limit. I suspect with a single 3000iS you will be in the 14ga range maybe more(?) On 6000W it sounds like you might get to 5/16. A 2nd 3000iS is a lot of money, and another 76 lbs too but they are quiet!
 
   #20  

jwmorris

Platinum Member
Joined
Oct 3, 2007
Messages
766
I have ran my maxstar (inverter welder) off of two different generators, the way I made sure they were close enough to 60 cycles was hooking one leg of the power from the generator and another leg off of "land" power, going to an incondesent light bulb.

If the cycles are off the light will "pulse" when they are balanced it will function as normal.

Adjust the speed of the engine and go "high" and "low" then set in the middle.

It worked for me and I didn't have to get out an oscilloscope.
 
   #21  

dragoneggs

Super Star Member
Joined
Jun 9, 2013
Messages
14,596
Location
Seabeck, Washington
Tractor
Kubota BX-25D, Kubota Z122RKW-42
I think 3000iS has a 230v outlet. Miller Tech said to weld 3/8" with the MultiMatic200 I'd need 7200W. I don't know how the 211 would behave. My pair of Honda EU2000i can weld on the 3/16" preset, but the generator overspeeds to get it going - tells me it's over the limit. I suspect with a single 3000iS you will be in the 14ga range maybe more(?) On 6000W it sounds like you might get to 5/16. A 2nd 3000iS is a lot of money, and another 76 lbs too but they are quiet!
Thanks Sodo... yeah I definitely love how quiet it is and that was very important to me for power outages... not quite portable as your 2000 but I wanted just one for the house and rare off site use. Now that I am welding and could use (wish list) more backup house power... a second one has sounded appealing but should be low on the need list. I never ever see these things on the used market. They are keepers for sure!
 
   #22  

Sodo

Elite Member
Joined
Apr 21, 2012
Messages
3,142
Location
Cascade Mtns of WA state
Tractor
Kubota B-series & Mini Excavator
I have ran my maxstar (inverter welder) off of two different generators, the way I made sure they were close enough to 60 cycles was hooking one leg of the power from the generator and another leg off of "land" power, going to an incondesent light bulb.

If the cycles are off the light will "pulse" when they are balanced it will function as normal.

Adjust the speed of the engine and go "high" and "low" then set in the middle.

It worked for me and I didn't have to get out an oscilloscope.

Hmmmm. Very Interesting. I would expect that to synchronize two 60Hz waveforms would require a microprocessor control system that makes adjustments to the phase (correcting phase errors far in excess of 60 times per second). I can't imagine an engine (and subjected to intermittent loading) could hold such a steady RPM. Am I missing something?

I would expect that connecting 2 separate sources of AC, that if the phases drifted even slightly out of sync there will be smoke & fire. Are you sure this is possible?
 
   #23  

SoGeorgia

Silver Member
Joined
Aug 16, 2013
Messages
154
Location
South Georgia
Tractor
Ford 600, Ford 3000, Allis Chalmers B
Not exactly the same, but same concept using an incandescent bulb to run generators in parallel.

 
Last edited:
   #24  

CNC Dan

Veteran Member
Joined
Sep 27, 2012
Messages
1,212
Location
north shore MA.
Hmmmm. Very Interesting. I would expect that to synchronize two 60Hz waveforms would require a microprocessor control system that makes adjustments to the phase (correcting phase errors far in excess of 60 times per second). I can't imagine an engine (and subjected to intermittent loading) could hold such a steady RPM. Am I missing something?

I would expect that connecting 2 separate sources of AC, that if the phases drifted even slightly out of sync there will be smoke & fire. Are you sure this is possible?

Possable. But for small homeowner size gensets, not likly.
But the honda inverter gensets have a way to sync two units together.

But you can use the lightbulb trick to compare a gensets frequancy with a known frequancy.
 
   #25  

Oliver1655

Gold Member
Joined
Jun 25, 2010
Messages
251
Tractor
Oliver 1655
My Miller 35 mig welder runs fine on a 5k generator.
 
   #26  

Texasmark

Elite Member
Joined
Apr 24, 2012
Messages
3,452
Location
N. Texas
Tractor
Ford: '88 3910 Series II, '65 3000; '07 6530C Branson with FEL, 2020 LS MT225S. All Diesels
If you are referring to this Mark I can't help you there. My generators are 5500 and 6500w and are magnetic induction...rotor connected directly to the engine drive shaft. My Blue Miller 240v ac-dc stick welder is transformer controlled. I have no problem with the 6500w generator running a 6011 or 7018 in 3/32 diameter.

HTH,
Mark
 
   #27  

Sodo

Elite Member
Joined
Apr 21, 2012
Messages
3,142
Location
Cascade Mtns of WA state
Tractor
Kubota B-series & Mini Excavator
Not exactly the same, but same concept using incandescent bulb to run generators parallel.

Awesome vid. The segment with the lightbulb next to the O-Scope was great!. Nice industrial gensets, and that dude knows some stuff! However, he did not say what happens if one of the motors has a hiccup, would the phase shift? Or if the motors don't have exactly equal power?

If a 'device' existed to combine the outputs of any 2 'normal' generators that could be a useful item if not so expensive. I suspect it would have to convert to DC, combine and invert back to AC.
 
   #28  

Farmerford

Platinum Member
Joined
Dec 9, 2006
Messages
733
Location
Columbus, Georgia
Tractor
Kuborta B2400, L2900, L4330; Caterpillar D3B, John Deere 455D
I have an 11KW PTO generator driven by an 18pto hp tractor and have no problem doing maintenance welding with a Miller AC/DC Thunderbolt 300 amp transformer type stick welder with 6010. My standards are not very high, but I don't think any of the welds have failed. Don't recall going over about 200 amps though.
 
   #29  

Sodo

Elite Member
Joined
Apr 21, 2012
Messages
3,142
Location
Cascade Mtns of WA state
Tractor
Kubota B-series & Mini Excavator
Farmerford, regarding 200A,,, what size rod are you using?

My Blue Miller 240v ac-dc stick welder is transformer controlled. I have no problem with the 6500w generator running a 6011 or 7018 in 3/32 diameter.

Appreciate the data point TXmark, thx for the genuine experience. Miller tech said 7200W (for 1/8 rod, with (150A) inverter welder). Anyway since I need to buy one, I'm thinking that 8000W is a good target for my uses.
 
   #30  

Soundguy

Old Timer
Joined
Mar 11, 2002
Messages
52,238
Location
Central florida
Tractor
RK 55HC,ym1700, NH7610S, Ford 8N, 2N, NAA, 660, 850 x2, 541, 950, 941D, 951, 2000, 3000, 4000, 4600, 5000, 740, IH 'C' 'H', CUB, John Deere 'B', allis 'G', case VAC
I have an 11KW PTO generator driven by an 18pto hp tractor and have no problem doing maintenance welding with a Miller AC/DC Thunderbolt 300 amp transformer type stick welder with 6010. My standards are not very high, but I don't think any of the welds have failed. Don't recall going over about 200 amps though.

keep in mind that you are likely not getting more than 9kw use out of that 18hp engine. ( yeah, i know. math it out and it's higher.. but real world rule of thumb is about 2hp per kw ). still. 9kw is a good bit of juice to work with.
 
   #31  

Shield Arc

Super Member
Joined
Jan 24, 2009
Messages
6,111
Location
Port Orchard, WA.
Tractor
John Deere, 4200
All this money spent on generators to run a welding machine?:confused::confused3::confused3::confused3: $200.00 spent 300-amps capacity.:thumbsup:
 

Attachments

  • New.JPG
    New.JPG
    238.3 KB · Views: 88
   #32  

Sodo

Elite Member
Joined
Apr 21, 2012
Messages
3,142
Location
Cascade Mtns of WA state
Tractor
Kubota B-series & Mini Excavator
Waiting for another one of those to turn up for $200 might be awhile.
 
   #35  

MinnesotaDaveChalmers

Platinum Member
Joined
Jun 13, 2012
Messages
659
Location
Big Lake/Monticello, MN
Tractor
WD Allis Chalmers
All this money spent on generators to run a welding machine?:confused::confused3::confused3::confused3: $200.00 spent 300-amps capacity.:thumbsup:

While the true finished cost on your machine is "a little" higher than that ;) - small gas engine welders (like the Lincoln weldanpower 150) are often found around $600 or less near me.

For a running stick welder with approx 5000 watt generator, pretty tough to beat :)

I have one, it's a cool little toy - only $300 for it (it's so small it's almost cute)

....just occurred to me I never tried the little mig on its generator...something for me to play with this weekend ;)
 
  
  • Thread Starter
#36  
OP
F

Furu

Platinum Member
Joined
Nov 20, 2009
Messages
981
Location
.
Tractor
.
All this money spent on generators to run a welding machine?:confused::confused3::confused3::confused3: $200.00 spent 300-amps capacity.:thumbsup:

Yes that is very nice and your bad influence may get me in trouble some day.:D
It is not as if you don't have one or two or more to spare but you well know why I asked the question.

Of course that question, for me at least, is totally without a purpose now.:thumbdown::thumbdown:
 
   #38  

aczlan

Super Star Member
Joined
Mar 7, 2008
Messages
17,809
Location
Northern Fingerlakes region of NY, USA
Tractor
Case 480F LL, Kubota L3830GST, B7500HST, BX2660
Awesome vid. The segment with the lightbulb next to the O-Scope was great!. Nice industrial gensets, and that dude knows some stuff! However, he did not say what happens if one of the motors has a hiccup, would the phase shift? Or if the motors don't have exactly equal power?
If a 'device' existed to combine the outputs of any 2 'normal' generators that could be a useful item if not so expensive. I suspect it would have to convert to DC, combine and invert back to AC.
If they are a little out of phase or the current dips more on one, the "slow" or "low" generator will do less work and the other will have to pickup the slack. If they are too far out of phase, bad things happen and the magic smoke gets let out.

Aaron Z
 
   #39  

sparc

Veteran Member
Joined
Oct 2, 2011
Messages
1,093
Location
NJ
Tractor
JD 4410, NH TC-25, Bobcat M610, JD X534, Dig-It Model 158, JD Ztrak 737. 6X4 Gator
Waiting for another one of those to turn up for $200 might be awhile.

Good luck finding one in that condition for $200
 
   #40  

jwmorris

Platinum Member
Joined
Oct 3, 2007
Messages
766
Not exactly the same, but same concept using an incandescent bulb to run generators in parallel.


That is pretty much it but you are not using two power sources just matching a generator to "wall" power. I have only done it with a 3500 watt and 4500 watt generators. I have never had a need to run any of my inverters off of my 30kw power station but if I did I would likely test it the same way.
 

jgayman

Platinum Member
Joined
Apr 2, 2011
Messages
825
Tractor
John Deere 2720
I have a Honda EU6500I inverter generator that I use for whole-house emergency power. I recently rigged up an adapter power cable so that I could power my Longevity StickWeld 250 from it. With the welder set to 100A I was pulling around 3300 watts from the generator. With the welder set to 150A and using a 1/8" E6013 I was pulling 6500 watts from the generator.

I used the combination last weekend for a repair project located where I would otherwise not have had 220V available and it worked very well.

I'm comfortable knowing I can now weld anywhere albeit with a 150A limit.
 

dragoneggs

Super Star Member
Joined
Jun 9, 2013
Messages
14,596
Location
Seabeck, Washington
Tractor
Kubota BX-25D, Kubota Z122RKW-42
I have a Honda EU6500I inverter generator that I use for whole-house emergency power. I recently rigged up an adapter power cable so that I could power my Longevity StickWeld 250 from it. With the welder set to 100A I was pulling around 3300 watts from the generator. With the welder set to 150A and using a 1/8" E6013 I was pulling 6500 watts from the generator. I used the combination last weekend for a repair project located where I would otherwise not have had 220V available and it worked very well. I'm comfortable knowing I can now weld anywhere albeit with a 150A limit.
That is a nice generator and setup!
 

brain55

Veteran Member
Joined
Jan 19, 2008
Messages
1,796
Location
Brentwood, CA
I have a Honda EU6500I inverter generator that I use for whole-house emergency power. I recently rigged up an adapter power cable so that I could power my Longevity StickWeld 250 from it. With the welder set to 100A I was pulling around 3300 watts from the generator. With the welder set to 150A and using a 1/8" E6013 I was pulling 6500 watts from the generator.

I used the combination last weekend for a repair project located where I would otherwise not have had 220V available and it worked very well.

I'm comfortable knowing I can now weld anywhere albeit with a 150A limit.

Great generator, I've put over 4000 hrs on mine. I've never used it for welding power since I have a welder/generator and wire feed I use for welding. I've wondered what it would be capable of though.

Brian
 

Texasmark

Elite Member
Joined
Apr 24, 2012
Messages
3,452
Location
N. Texas
Tractor
Ford: '88 3910 Series II, '65 3000; '07 6530C Branson with FEL, 2020 LS MT225S. All Diesels
Farmerford, regarding 200A,,, what size rod are you using?



Appreciate the data point TXmark, thx for the genuine experience. Miller tech said 7200W (for 1/8 rod, with (150A) inverter welder). Anyway since I need to buy one, I'm thinking that 8000W is a good target for my uses.

As you can see Miller tech is right on. Agree with your sizing decision. Once you spend the money it will be gone forever but you will have the satisfaction of having a reliable workhorse that will do the job for you.

Mark
 
 