Welder / Wiring for Small Garage
   / Welder / Wiring for Small Garage #41
For small wire sizes it is easy to remember if you just add 10 amps starting with #12 being 20. Then #10 is 30 amps , #8 is 40 amps and #6 is 50 amps. Wire length and temperature rating will change the amperage. Just a rule of thumb for the lower temperature. A larger welder could be used on the 30 amp circuit but it would limit how high of setting you could use and the duty cycle.
   / Welder / Wiring for Small Garage #42
JUst use receptacle that matched power cord on welder, don't cut off plug of welder cord and graft on something different, this is no brainer because receptacles is not a problem.... And the NEMA 6-50 plug/receptacle combination has become industry standard (in most cases) .... Now all you have to do is determine wire size and breaker amperage.....
As a side note if you are using a 120/240 volt machine manufacture's recommend not cutting off plug on welder cord and grafting on something different....Will probably also void warranty...
   / Welder / Wiring for Small Garage #43
pulled a page from the owners manual 24 amps on 240 volt so that is 80% of a 30amp circuit breaker so you will need a 30 amp CB and #10 wire unless it is a really long run.
Copied and pasted this note from your attachment.
4-4. Unit Specifications For 230 VAC
Do not use information in unit specifications table to determine electrical service requirements. See Sections 5-8 and 5-12 for information on con-
necting input power.
   / Welder / Wiring for Small Garage #44
Most 120/240 machines include an adapter. Some machines cone with a 4 wire plug and I have one that is 3 phase also.
   / Welder / Wiring for Small Garage #45
Copied and pasted this note from the your attachment.
that is interesting, did not read that but then again we are not sizing a service we are sizing a feeder and the specified current draw is exactly what is used for that calculation.
   / Welder / Wiring for Small Garage #46
You shouldn't use 8/3 for a 30 amp breaker, the coded size for 30 amp is # 10 wire, any size larger than that with a 30 amp breaker could cause a problem. It would take longer for a breaker to trip
Huh??? You can use any larger size wire, it's just a waste of money. If you are depending on losses in the wiring to trip the breaker, you have some serious problems.
   / Welder / Wiring for Small Garage #47
#12 is 20 amp rated not 30.
I'm guessing that a #12 extension cable would be OK to use on a 30 amp welder because of the duty cycle. I think it would be frowned on for the building wiring because of the potential of hooking up a constant 30 amp load.
   / Welder / Wiring for Small Garage #48
The only limitation on larger size wire is getting it to fit into the breaker or receptacle. Nothing to do with load.
   / Welder / Wiring for Small Garage #49
All, question on wiring and breaker for my personal use small garage.
I have a 50 amp circuit from my house to the garage on 6/3 wire (black, red, white and ground).
I planned to wire a 30 amp circuit for welding with 8/3 wire, but is that enough for say a Hobart Handler 210MVP or a Mult-Handler 200 Multiprocess? I wouldn’t ever need to weld anything thicker than 3/8”.
Handler® 210 MVP™ MIG Welder | HobartWelders
Multi-Handler 200 Multiprocess Welder | HobartWelders
Will a 30 amp circuit with 8/3 work?
Electric works on demand .. so 6/3 run into a small panel and a 50 amp welder fed from that should be plenty for one person using one piece of equipment at a time. If you have a/c or compressor etc, switch them off if welding a long spell.
   / Welder / Wiring for Small Garage #50
cords are considered manufactures wiring and falls under different jurisdiction, usually UL.