    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by aczlan View Post
    FYI, I asked both NYSEG and RG&E about this via their websites and I just heard back from NYSEG. Here is what they had to say:


    Still waiting to hear back from RG&E (who actually owns the meter).

    Aaron Z
    Howdy,
    I am only talking about the style of meter base. My local utility uses horn style ringless. There are many variations of the meter bases. Yes, UL approved, but you need to use the style and type that works with your utility. Yes, the utility will not move forward until the inspection is OK'd.
    Later Mike ~~~
    JD green here
    tractors and implements

  2. #42
    Super Star Member
    Join Date
    Mar 2008
    Posts
    10,088
    Location
    Northern Fingerlakes region of NY, USA
    Tractor
    Kubota L3830GST, B7500HST, BX2660

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by daybreak1998 View Post
    Howdy,
    I am only talking about the style of meter base. My local utility uses horn style ringless. There are many variations of the meter bases. Yes, UL approved, but you need to use the style and type that works with your utility. Yes, the utility will not move forward until the inspection is OK'd.
    Good point. RG&E requires the same. Looks like GE 200 Amp 4-Space 8-Circuit Outdoor Combination Main Breaker/Ringless Meter Socket Load Center TSMR420CSCU at The Home Depot is the one that I would need (TSMR420CSCU). $108ish locally and takes the same interlock.

    Aaron Z
    A human being should be able to change a diaper, plan an invasion, butcher a hog, conn a ship, design a building, write a sonnet, balance accounts, build a wall, set a bone, comfort the dying, take orders, give orders, cooperate, act alone, solve equations, analyze a new problem, pitch manure, program a computer, cook a tasty meal, fight efficiently, die gallantly. Specialization is for insects.
    Robert Heinlein, Time Enough for Love

  3. #43
    Gold Member
    Join Date
    Mar 2009
    Posts
    438

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by daybreak1998 View Post
    Howdy,
    "The interlock"

    The interlock makes it so only 1 breaker can be on. The main panel breaker, or the generator breaker. So, you turn off the main 200amp breaker, slide the metal interlock, and now you can turn on the generator breaker.
    Attachment 272502 click on the picture to see larger, then click again to zoom in.


    Your panel needs to have a interlock kit for it. It usually needs the 2 top right spaces for the generator breakers. If your panel is full, a lot of times you can get half breakers to help make some room.
    I like this option a lot because I'm not spending a lot of money on a temporary transfer switch that would be unneeded some day when I get a generator big enough for the whole house. My thought was use one of these and then flip off all of the breakers I don't want to power before I start the generator. The one problem with this plan is this approach doesn't provide a meter that shows how much load I'm putting on the generator. Is there a way to put a meter on the panel that would be active when the the interlock is flipped and the generator in use?

  4. #44
    Super Star Member
    Join Date
    Mar 2008
    Posts
    10,088
    Location
    Northern Fingerlakes region of NY, USA
    Tractor
    Kubota L3830GST, B7500HST, BX2660

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by MNBobcat View Post
    Is there a way to put a meter on the panel that would be active when the the interlock is flipped and the generator in use?
    I am looking at getting something like this: Gen/Tran Remote Metering Kit RMK-15-I RMK-15-F RMK-15-O and mounting it by the inside panel where I can watch the current usage and balance usage between the legs ahead of time.

    Aaron Z
    A human being should be able to change a diaper, plan an invasion, butcher a hog, conn a ship, design a building, write a sonnet, balance accounts, build a wall, set a bone, comfort the dying, take orders, give orders, cooperate, act alone, solve equations, analyze a new problem, pitch manure, program a computer, cook a tasty meal, fight efficiently, die gallantly. Specialization is for insects.
    Robert Heinlein, Time Enough for Love

  5. #45
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    164
    Location
    Northern Virginia
    Tractor
    Lots of John Deere tractors

    Default Re: Generator Transfer switch connection choices

    Howdy,
    The interlock kit does not have a certain amperage limit. The limit will be the size of dual pole circuit breaker you can find to fit your panel. Most folks use a dual pole 30amp breaker.
    Later Mike ~~~
    JD green here
    tractors and implements

  6. #46
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    164
    Location
    Northern Virginia
    Tractor
    Lots of John Deere tractors

    Default Re: Generator Transfer switch connection choices

    Howdy,
    You can post questions here. That way everyone learns something... I don't mind the PM's, but the questions might be something someone else is thinking too.

    Your service entrance load panel.
    Not all load panels have interlock kits for them.

    You can browse through these vendors (I have never used them, I do not know if they are any good, but the web site shows all the ones which they have interlock kits for)

    National Ram Electronics
    and / or
    GenInterlock

    The dual pole breaker for your generator hook-up can be any size. Standard dual 30amp for 8000w generators or dual 50amp for 10,000w generators, up to whatever size you can find and fit in your panel.
    Later Mike ~~~
    JD green here
    tractors and implements

  7. #47
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    164
    Location
    Northern Virginia
    Tractor
    Lots of John Deere tractors

    Default Re: Generator Transfer switch connection choices

    Howdy,
    Yes, I use the Tiger Power PTO generator 30kw to run the central farm distribution. The connection is with 350amp Anderson ends with 2/0 welding wire. The wire and connections can handle a lot more than what my 30kw puts out. The connection is called a full power plug. The transfer switch can handle 40kw continuous and 48kw peak.

    Tiger Power 30kw PTO generator
    30,000 prime duty running watts, 90,000 surge starting watts
    here is a quick clip running drawing 18.0kw and then dropping to 15.4kw
    https://www.dropbox.com/s/d2g0zdbjdi...%20running.mp4
    Later Mike ~~~
    JD green here
    tractors and implements

  8. #48
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    164
    Location
    Northern Virginia
    Tractor
    Lots of John Deere tractors

    Default Re: Generator Transfer switch connection choices

    Howdy,

    PSP Products makes a few different sized items. I do not know if they are approved in your neck of the woods with your Utility. You would have to check with them. You would then need to talk with PSP Products about what equipment would work for you.

    PSP Products Transconnect switch gear from this page you can see they offer a few styles.

    good luck.
    Later Mike ~~~
    JD green here
    tractors and implements

  9. #49
    Bronze Member bjmsam's Avatar
    Join Date
    Dec 2009
    Posts
    64
    Location
    Maryland
    Tractor
    Kubota L3710 HST

    Default Re: Generator Transfer switch connection choices

    As mentioned here, I have a 400 amp service that feeds two 200 amp main panels.




    I bought a TED 5002 to monitor my energy usage and confirmed that a 15KW PTO generator would suffice.




    I bought two Square D QOCGK2C interlock kits and two 50 amp double-pole breakers to occupy spaces 2 and 4 of each panel:




    I bought a Reliance Controls MB125 50 amp meter box to monitor load balance.




    I bought a GE 50 Amp Twist Lock Power Inlet with L14-50 connector (larger and more robust than the popular Reliance Controls PB50).




    I bought 3/4 in. Flex Aluminum Conduit and 8 gauge THHN wire (rated for 50 amps and much easier to work with than Romex 6/3 with ground).




    I bought a Conntek 1450SS2-15 Temporary Power Cord with NEMA 14-50P Generator Plug to CS6364 Locking Connector.




    Now I am trying to wrap my head around the parallel neutral path that this approach would introduce as discussed at length in this thread. The neutrals are presumably bonded at the meter and to ground at the disconnects between the meter and each panel. I don't yet understand 1) why a secondary neutral is unsafe if it's of the same gauge as the primary, or 2) why it would be unsafe to connect the generator neutral to only one panel to leverage the existing primary neutral connection to the other panel. Worst case I can order another inlet box and associated wiring to connect each panel separately, in which case the parallel neutral path would exist only when the generator is connected via a Y cable. Thoughts?



    Kubota L3710HST MFWD with LA681 loader, blade, hog, scoop, Rip & Dig, PTO generator
    Kubota G1900-S HST AWS with 60" deck

    Previous:
    1984 John Deere 1050 2WD
    1959 John Deere 435 Diesel
    John Deere LX188 V-twin hydro with 48" deck

  10. #50
    Silver Member daybreak1998's Avatar
    Join Date
    Oct 2010
    Posts
    164
    Location
    Northern Virginia
    Tractor
    Lots of John Deere tractors

    Default Re: Generator Transfer switch connection choices

    Quote Originally Posted by bjmsam View Post
    Now I am trying to wrap my head around the parallel neutral path that this approach would introduce as discussed at length in this thread. The neutrals are presumably bonded at the meter and to ground at the disconnects between the meter and each panel. I don't yet understand 1) why a secondary neutral is unsafe if it's of the same gauge as the primary, or 2) why it would be unsafe to connect the generator neutral to only one panel to leverage the existing primary neutral connection to the other panel. Worst case I can order another inlet box and associated wiring to connect each panel separately, in which case the parallel neutral path would exist only when the generator is connected via a Y cable. Thoughts?
    Howdy,
    I see you have been busy. I see exactly what you want to do. But, I am not sure it can be accomplished. That is also one of the reason I have the Transconnect unit. In my meter box, I use the feed thru lugs to feed 2 200amp panels, a 60amp well panel, a 100amp shop panel, and a 100amp barn panel. Being a central farm distribution, I can power whatever is needed when on generator power.

    Because of the complexity of what you want to do. IMHO you should maybe get a local PRO in your area. I do not think you will get the best internet advice to be able to do it correctly and safely.
    Later Mike ~~~
    JD green here
    tractors and implements

Page 5 of 8 FirstFirst ... 2345678 LastLast

Similar Threads

  1. generator whole house transfer switch
    By automech in forum Rural Living
    Replies: 32
    Last Post: 02-14-2014, 09:45 PM
  2. generator/transfer switch connection
    By geneP in forum Rural Living
    Replies: 13
    Last Post: 10-30-2009, 01:48 AM
  3. Generator Generator transfer switch wiring diagram
    By Barneyhunts in forum Attachments
    Replies: 46
    Last Post: 02-29-2008, 10:24 PM
  4. Wiring a Home Generator Transfer Switch
    By RobS in forum Rural Living
    Replies: 38
    Last Post: 01-27-2008, 07:58 PM
  5. Neal's Generator/Transfer setup
    By ns_in_tex in forum Build-It Yourself
    Replies: 43
    Last Post: 10-11-2004, 07:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
© 2014 TractorByNet.com. TractorByNet is a registered trademark of IMC Digital Universe, Inc. Other trademarks on this page are the property of their respective owners.