Ever since I bought this place I have had a problem with the 110 receptacles in my shed. The lights work, the welder gives me no problem.
The wires are run in conduit with a receptacle every 10' ... 6 on each side of the barn. I have never been able to use a saw, grinder ... not enough power, I can plug in a light or use my chain saw sharpener. (Circuit is 20 amp breaker)
I am getting ready for baby chicks, plugged in a 250 watt heat lamp, when I plug in the second 250 lamp they both become very dim.
Easy fix? I know a little about electricity ... what do ya'll recommend?
Testing for low voltage,, Start with the main panel in the barn,, Take the cover off put your meter on 600v ac check between each hot wire going into your main breaker to the neutral wire you should have around 120v on each,, Then plug in your 2- 250 watt lamps and test again,, If the voltage stays the same then the problem is not outside the panel.. Lets assume all is OK there,, Unplug the 2 lights and check the voltage coming out of your 120 breakers,, " I assume you have more than one? " See if the voltage is still 120v between the breakers and your neutral .. then plug in your 2 lights and check the breakers again...
Start with that and let us know what you find,,