Sorry guys, I didn't find an electrical section on TBN, so posting it in welding section.
I'm getting a 160 amp stick inverter DC welder. It's a 110/220 dual voltage, so could run on either. To make a long story short, how would it run on a 20 amp 220v circuit compared to a 20 amp 110v?
Here's the longer story to this:
All my outlets in the garage are on (1) 20 amp circuit, 12 ga wire. All the outlets are gfci's.
One outlet box is now empty, but has wiring in it from the above circuit, but also has a capped-off wire on it's own separate 20 amp circuit. This was originally a switch that ran out to power the shed out back, but is no longer being used.
So what I'm thinking to do is wire a 220 outlet in that box. Yesterday I moved the breakers in the panel next to each other, so now they're on separate hots and I could link the breakers together with a handle tie. But I'm wondering if I'm gaining anything for the welder if I'm still limited to 20 amps?
The panel is far from the garage, it would be a royal pain to run bigger wire out to the garage for 30+ amp breakers, so that's out for now. And in any regard, this would be a whole new wire job, since currently one of those 110v circuits is also powering all the garage outlets...which also brings me to another question, is there an issue with one leg of my proposed 220v circuit also powering a radio and something else some such?
I'm getting a 160 amp stick inverter DC welder. It's a 110/220 dual voltage, so could run on either. To make a long story short, how would it run on a 20 amp 220v circuit compared to a 20 amp 110v?
Here's the longer story to this:
All my outlets in the garage are on (1) 20 amp circuit, 12 ga wire. All the outlets are gfci's.
One outlet box is now empty, but has wiring in it from the above circuit, but also has a capped-off wire on it's own separate 20 amp circuit. This was originally a switch that ran out to power the shed out back, but is no longer being used.
So what I'm thinking to do is wire a 220 outlet in that box. Yesterday I moved the breakers in the panel next to each other, so now they're on separate hots and I could link the breakers together with a handle tie. But I'm wondering if I'm gaining anything for the welder if I'm still limited to 20 amps?
The panel is far from the garage, it would be a royal pain to run bigger wire out to the garage for 30+ amp breakers, so that's out for now. And in any regard, this would be a whole new wire job, since currently one of those 110v circuits is also powering all the garage outlets...which also brings me to another question, is there an issue with one leg of my proposed 220v circuit also powering a radio and something else some such?