It
can be a DIY situation - provided you educate yourself properly, and fully
understand the potential hazard, and then use proper care - messing around side that box could get you
dead, if you don't know what you are doing.
Having said that, I'm no electrician ......
but I was inside the 200A panel for our house yesterday, installing a new 50A breaker ..... ahhh .... without the power cut :confused2:
Like I said: I'm no electrician, but I'll take a stab: the item in the middle appears to be main disconnect switch for the item on the right. It (the item in the middle) may well be fused inside the box. I have a similar one (rated at 200A) that is fused, that I need to install to feed the electrical service in our polebarn.
The main disconnect switch would be necessary, from a safety standpoint, since the item on the right does not have it's own main disconnect switch to kill power to itself - a particularly important and useful feature, if one plans on being inside the item on the right, working on it
Either could be applicable I suppose, from a generic/slang perspective.
To be accurate and descriptive, I'd call it a
circuit breaker panel
It may technically be a
sub-panel ... dunno ....
You should make the effort to find out what it feeds - and then at least
label it. This is for safety reasons - maybe not your safety, but perhaps someone elses .....
Thin breaker versus a wide one .... I'm not really sure the reason for the difference (other than saving space and allowing more circuits in a panel ?) .... I believe that the larger one's have higher rating in some respects than the thinner ones, although I may be mistaken.
As long as you understand the particular hazard it poses .....
Seems reasonable ...
Right.
While you are about all of this, here's a couple more fairly simple things you ought to do asap (IMHO):
1. Spend a couple of bucks and at least get a proper weather-proof cover (one that isn't broken) for that 120v outlet on the bottom of the box. Coupla bucks.
As mentioned, ideally, you should throw a GFCI outlet and cover on it .... in an actual weatherproof box .... (I assume that it does rain down there
)
2. Your power feed cable to your well appears to be run thru a set-screw connector for metal conduit. This is
not correct - there is no way to secure the cable and provide strain-relief with the connector being used, and as a result, the cable has actually fallen down out of the box to the point where the outer insulation jacket is below the set-screw connector, allowing the inside wires to rub against the (metal) connector, as well as placing a strain on the wires at the point where they connect to the circuit breaker..
At a minimum replace the set-screw connector with one of these (less than a $1), sliding the cable up into the circuit breaker panel so that the clamp grips the outer insulation jacket, and there is no strain on the wires at the breaker:
Twin Screw Clamp Connector
Easy enough to do ... remove the unused set-screw conduit connector and use the hole to wire in another box and outlet.
Obviously any time you are working inside that circuit breaker panel, you should have
the power to it shut off via the main disconnect switch. (Do as I say, not as I do
)
Dunno - you tell me - what kind of plug/receptacle is on your travel trailer ?
It could be you have a 30A shore power receptacle on the trailer, and then a proper 30A rated cable, and perhaps an
adapter to convert it to either a standard 15A (or 20A) household plug ?
Or you could have a cobbled together cable with a 30A plug on one end (at the trailer) and standard 15A (or 20A) household plug on the other end .....
As KennyG suggests, take a look at the NEMA plug-receptacle configurations he linked and then let us know exactly what you have (pics would be good) on the trailer ..... and on both ends of the cable. And let us know exactly what gauge wire is in the cable.
Correct - as well as a new circuit breaker.
You will need to size the wire for the load - then you need to size the breaker for the wire. The purpose of the breaker is to protect
the wire.
Sorry to hear it
You can do it - assuming you are a person of reasonable intelligence and willing to exercise proper care.
Glad to be of service :thumbsup: