Doesn't glued PVC have a tendency of breaking, up where you are with the frost and all? I normally run the heavy wall black plastic water pipe.Are you confused yet?
I would bury the cable in 2" PVC conduit with 90 degree radius bends on each end to bring the cable up out of the ground. An LB bend (it's a sharp 90 bend with an access plate) is used to then turn the cable and go through the wall of the house and another into the barn.
Use PVC cement (works like ABS cement) for all joins and you shouldn't have a problem with water infiltration. 2" PVC is costing me $2.33 a foot, the bends are around $12 each. That would total about $665.00 in conduit but will last forever, especially if you bury it in sand or at least ensure there are no rocks likely to come in contact with it.
Jon
We have a separate feed to our barn and the base cost, without any usage, is just about the same as the cost of what we do use. Got to love it. We have a our own street light at the barn that stays on all night. To cut cost we have the barn on the night rate plan. You have to be careful here also as the day rate goes up somewhat when you are on the night rate.The high monthly cost to go with the second base is really limiting that option on our region but I can remember when usage cost was less than ONE cent per KW.
I would assume using 3 wire would require 2 ground rods at the new location.One electrician said to use 3 runs of #4 copper wire in 2 in PVC conduit. But with the price of copper being as high as gas, the 2nd estimate recommended that I use (forgive my terminology) 1/O ACSR. It is aluminum wire which has the 3 conductors already wrapped together.
My wife worked as an electrical engineering technician for the local power company when we first met, so she keeps me in line with all the terminology and wire capacities.
RxRatedZ71,
I used the Wire Size Calculator that Tom gave the link to.
Load Calculation
Overhead lights 15 A
Refrigerator circuit 15 A
Space heater circuit 15 A
Circuit for other outlet 15 A.
Total: 60 A at 120V
Solution
You could run a 240 V line (3 conductors plus ground) to your barn from a 30 A 240V breaker in your house panel. The 240V line will actually provide you two 120V lines at 30 A each for a total of 60 A at 120V which is what you need. Put the refrigerator circuit and space heater circuits on opposite 120V legs of the 240V wire to balance your load and to minimize voltage drop. Using the online wire calculator:
120V, 30A, copper, single phase, 265'
Wire Size
You need a #2 size copper line between the house and your barn and you will be fine. If you go with a smaller wire, you will have voltage drop problems at the barn which will cause problems and could damage your equipment (especially the compressor used by the refrigerator). This design does not require an extra meter as you requested. However, doing it this way will have an up-front cost of paying for the large #2 wire.
If you were willing to pay for the extra power company meter at the barn, then you could run a much smaller wire (less cost) to the barn because you would be running a high voltage line which would be stepped down to 240V/120V using a transformer close to the barn.
Note: I have an electrical engineering degree but am not a licensed electrician so get a professional opinion before proceeding.
Good luck with your project,
Obed
Rx. I have about the same uses as you are going to use in your new barn as I do now, and the same distances you are dealing with.. This is what I did and it works fine. Starting at my MDP "main panel" Feed breaker size 70amp. #2 alum. SER.. wire from the breaker to a pvc junction box in the basement where the wire is to go outside. Pipe out the back of the box to an 1-1/2 pvc lb on the outside of the building.. 1 1/2 pvc conduit.. "electrical conduit" to the barn and up into your main breaker in your new barn panel use #2 urd 4 wire in the conduit.
I also ran a black and white #10 copper to the barn for my block heater.. That way a half hour before I go out to plow snow I can turn it and an outside light on before I go out.