anyone still using this gen? having problems with one I just got. not putting out enough voltage at 540 rpms. any tips? thanks
You're responding to an old thread.
Do you have adequate PTO HP for the generator? IIRC, you need about 2 PTO HP per Kilowatt (example: a 15kW genny needs 30 PTO HP to drive it). If you do not have adequate PTO HP, you will not get the full output from the generator.
If you do have adequate PTO HP, are you sure you're measuring the output correctly?
If you do have enough PTO HP, and you are measuring the out correctly; don't dig into the generator...you'll void any warranty. Just return it to where you bought it.