Thats true, but 2” pvc conduit is rated to carry 4 runs of 4/0 wire without issues.
I'm not, repeat not, an electrician.Maybe the code has changed lately, or there’s some regional variations on the NEC standard being mentioned here. This installation sounds like a pole meter loop to me. That panel on the pole, probably feeds only the new house. It’s effectively acting as a disconnect with one downstream load.
I disagree with calling and treating the new house main service panel, a sub-panel.
I also disagree with the need or desire , to run a grounding conductor from the pole to the new house.
The first panel in the house is the main service panel. There should be a grounding rod at the house, same as every other house. This is where your main panel will bond the neutral with ground . If you ran a ground wire from the pole, your ground and neutral would be connected at both ends, and that defeats the purpose, and you certainly don’t want to not physically ground at the house entrance, and rely on a little ground wire running 150 to a pole meter
For that long of a run, you will need to upsize the wire that you run due to voltage drop. If it were me, id run a longer primary utility run towards the house instead of a huge secondary wire required for a 260’ run.Do you recall what section of code that is in? I knew about sub panels but wasn't aware of the 1st breaker turning my cabin into a sub. I have this (picture) getting ready to happen by the end of summer. I do have a Coop breaker right before the pole month meter that i think is 400amp. A bit overkill. I plan to meet with a Coop guy soon next time I'm over there. Ideally I would like for them to run about 100+ of triplex and set another pole. If I have them put a 2nd service right by my cabin that's another $500+ a year for at least one meter mostly at idle. into a sub panel.
View attachment 3519356