2" PVC Conduit Generator 2-2-4 end piece? LB?

   / 2" PVC Conduit Generator 2-2-4 end piece? LB? #1  

fidowanttobe

Platinum Member
Joined
Aug 7, 2014
Messages
700
Location
Mandan ND
Tractor
Jinma 284 2007 Massey Harris 44 Special
I am burying 2" PVC conduit for my generator permanently under a concrete pad so it pops up through the slab 2 feet from the wall. The generator is 3x8 foot and where the wires go into it is a 90 degree, approximately 10" from the floor. Not ideal. So, . . all I can think of using is a 2" LB PVC Conduit Body.
Again, not ideal. Would prefer something better for vibration. Please help with suggestions. Thanks.
1662644348691.png
 
   / 2" PVC Conduit Generator 2-2-4 end piece? LB? #2  
Sealtight. Liquidtite. Whatever it's called in your area. And the associated connectors at the rigid pipe and generator frame. Use straight connectors and let the flex conduit make the bend. The connection to the generator needs to be flexible.

Liquid-tight Flexible Conduit Now Available |Library.AutomationDirect
 
   / 2" PVC Conduit Generator 2-2-4 end piece? LB? #3  
I agree wholeheartedly with the liquid tight flex conduit but also suggest an LR or an LL so the top is not getting the rain. It's the same basic L connector with an opening on the left or right side instead of the back.
 
   / 2" PVC Conduit Generator 2-2-4 end piece? LB?
  • Thread Starter
#4  
Thanks guys. Exactly the info I needed.
Now I just need to find a supplier that will sell me 2 lousy feet of 2"!
 
   / 2" PVC Conduit Generator 2-2-4 end piece? LB? #5  
Any electrical wholesale house will usually sell it and the 2 fittings
 

Tractor & Equipment Auctions

Deer Feeder (A50860)
Deer Feeder (A50860)
71061 (A49346)
71061 (A49346)
19008 (A48082)
19008 (A48082)
WHITE CI-7 DRAW WORKS POWERED BY TWIN DETROIT 12.7S (A50854)
WHITE CI-7 DRAW...
2016 Chrysler 200 Limited Sedan (A48082)
2016 Chrysler 200...
2019 Nissan Rogue SUV (A50860)
2019 Nissan Rogue...
 
Top