Defective
Platinum Member
How about running 240V on that same wire & a 2:1 transformer at the gate? Cut the current (& therefore the line loss) in half. This would give you a total of 16 amps available at 114V with 4.95% loss on a 10 ga. wire.
DieselPower said:Where would he get a single phase of 240 volts? Unless he has 3 phase at his place all he has is two 120 volt leg's in his breaker pannel. Normal house hook up's for 240 volts are two leg's of 120 volts which is more or less 2 phase. If he has 3 phase he would have one leg with a higher voltage but most people don't have 3 phase.
Both should work ok. 15A for a gate is excessive so I assume that is to allow startup surge without flipping the breaker. Voltage to the motor will be a little low, but assuming it starts ok, it will not suffer from the intermitent nature of the usage. The greenhouse is a short enuf run to be quite forgiving in the amt of V sag. All low drains would be fine - lights, fans, motors up to 1/2 horse. - -A microwave ~ probably. Resistance heaters are continuous high drain, but they arent very particular of their power. You just wouldnt get their full rating due wire losses - still useable. In general, Id just be vigilent as to the nature of the power demand on the circuit and its approx balance across the two 110V legs.woodlandfarms said:I have two projects for this spring... Hoped to do them myself... But I wanted to make sure I have everything calculated...
I would like to put up an electric gate on our property. that would place it about 700' from the main house. Can 10 Guage hooked to 110 deliver close to that at 15 Amps. I think the gate is rated at 2 amp draw.
Second, the wife want a green house. There is a 220 line running out to an old well head. I was thinking of tying into that and splitting it to give her two 15Amp 110V legs out there. It is around 200' from the house. The line is newer (past few years, yellow jacket, so I think 10 guage).
I checked a couple of websites and it looks like my drop would be only a few volts. Not sure that anything we are using would be affected.
But, for whatever reason, I seem to remember someone telling me you cannot exceed 100' run.
Love some comments on this before I tell the wife it is a go on the projects.
Carl
woodlandfarms said:Second, the wife want a green house. There is a 220 line running out to an old well head. I was thinking of tying into that and splitting it to give her two 15Amp 110V legs out there. It is around 200' from the house. The line is newer (past few years, yellow jacket, so I think 10 guage).