Toolguy
Platinum Member
I recently found a deal on a used 3HP heavy-duty air compressor. I have it hooked up in my shop now and it works OK buts it really draws the amps when starting. I may not have enough electrical capacity to run it the way it should. While running it draws about 18 amps on both legs and the voltage is good at 115 to 118. However, when it starts up it draws 68 amps and the voltage drops to 104 momentarily. The 20A breakers do not trip. This seems excessive to me and I am worried that this might hurt the motor over the long haul. I know that magnetic or capacitor starters are needed on some motors. Does anyone know if a starter of some type would help? I have 125ft of 8ga wire running from my main electrical panel to the breaker box. From there it is another 50ft to the compressor. I only have 12ga wire from the breaker box to the compressor but I ran a parrallel set of 12ga wire to the compressor as a test to see if it made a difference with more wire capacity. It did not change the amp and voltage readings. I am stumped at this point. Any help would be greatly appreciated. Thanks.
P.S. The compressor has an unloader so it is not starting under pressure. It does have a huge cast iron pulley/fan on the pump. I am thinking it probably draws a lot of power to get that thing turning.
P.S. The compressor has an unloader so it is not starting under pressure. It does have a huge cast iron pulley/fan on the pump. I am thinking it probably draws a lot of power to get that thing turning.