there are hundreds of thousands of subpanels done this way..
2005 code said you could bond the neutral to the can and drive the new ground rod, so long as you were not bonded some other way with the original structure, through water lines, phone lines, etc.. Basically treating it as a new service, with the incoming power from your house panel, acting just like the incoming feed from the utility if you will.
Code says that beyond service entrance (main panel) the neutral and ground are not to be bonded..
I have managed an electrical supply house for several years here in Texas. I can tell you that here in the "country" we still do it per 2005 code..
No reason to waste the wire necessary to run the 4th conductor to a subpanel 100+ feet away.. JMHO... So take my opinion, and the current code, and decide which way you wanna do it.. Glad to help.
2005 code said you could bond the neutral to the can and drive the new ground rod, so long as you were not bonded some other way with the original structure, through water lines, phone lines, etc.. Basically treating it as a new service, with the incoming power from your house panel, acting just like the incoming feed from the utility if you will.