Background;
We had an ERV system built into our heating system when we built the house, Trane AERVR300. But we basically never used it. We have a lot of sq-ft and only two of us in the home. For those who do not know what an ERV is, it's a small air handler that pulls out air from the house and pulls in fresh air. The out going air passes through a heat exchanger to give back energy to the incoming air.
The original duct work was a dedicated duct to pull the stail air out. Then after the ERV runs it through the heat exchanger and pulls in fresh air, it goes back to the main HVAC air handler. It is controlled at the T-stat via to run a preset number of hours. Often refered to as "Percent timer". This was set up as a whole house device.
We want to run it for a new purpose, to clean/freshen the air just in my wife's jewelry making shop in the basement. She uses an oxyacetylene torch with flux fumes she'd like not to breath. So I want to disconnect it from the T-stat and just run it with an "on/off" switch located in her shop.
With most HVAC equipment these days, it's more complicated. When the T-stat starts the ERV, it does 3 things; 1) open a damper on the outside fresh air vent, 2) turn on the main house air handler and 3) turn on the ERV. So as a stand alone unit, we do not want the main house air handler to operate. The T-stat can be set to be ERV=> "off". Or just disconnect to control wires coming in to the ERV.
Questions;
The ERV has just 2 terminal points on the unit. In the schematic, terminal block. In the schematic they are shown on a motor relay at 24 V AC circuit. On these two terminals are only the control wire and the damper wires. So 2 reds on one terminal and 2 whites on the other terminal. My meter shows 24 V AC across the terminals when T-stat is "on". No voltage when T-stat is "off".
So I'm assuming this unit can be wired for stand a lone operation or tied in with an existing HVAC system. If tied in to the HVAC system, the 24 V comes from a separate controller on the air handler. But I assume if run independently, a jumper is used inside the EVR unit to provide the 24 V. I can't find any thing in the instructions on how to switch it back to stand alone.
Last option and maybe most simple, at T-stat set the ERV to run all the time, select no air handler to operate to assist. Then just place a switch on the control wire that signals the unit to come on.
We had an ERV system built into our heating system when we built the house, Trane AERVR300. But we basically never used it. We have a lot of sq-ft and only two of us in the home. For those who do not know what an ERV is, it's a small air handler that pulls out air from the house and pulls in fresh air. The out going air passes through a heat exchanger to give back energy to the incoming air.
The original duct work was a dedicated duct to pull the stail air out. Then after the ERV runs it through the heat exchanger and pulls in fresh air, it goes back to the main HVAC air handler. It is controlled at the T-stat via to run a preset number of hours. Often refered to as "Percent timer". This was set up as a whole house device.
We want to run it for a new purpose, to clean/freshen the air just in my wife's jewelry making shop in the basement. She uses an oxyacetylene torch with flux fumes she'd like not to breath. So I want to disconnect it from the T-stat and just run it with an "on/off" switch located in her shop.
With most HVAC equipment these days, it's more complicated. When the T-stat starts the ERV, it does 3 things; 1) open a damper on the outside fresh air vent, 2) turn on the main house air handler and 3) turn on the ERV. So as a stand alone unit, we do not want the main house air handler to operate. The T-stat can be set to be ERV=> "off". Or just disconnect to control wires coming in to the ERV.
Questions;
The ERV has just 2 terminal points on the unit. In the schematic, terminal block. In the schematic they are shown on a motor relay at 24 V AC circuit. On these two terminals are only the control wire and the damper wires. So 2 reds on one terminal and 2 whites on the other terminal. My meter shows 24 V AC across the terminals when T-stat is "on". No voltage when T-stat is "off".
So I'm assuming this unit can be wired for stand a lone operation or tied in with an existing HVAC system. If tied in to the HVAC system, the 24 V comes from a separate controller on the air handler. But I assume if run independently, a jumper is used inside the EVR unit to provide the 24 V. I can't find any thing in the instructions on how to switch it back to stand alone.
Last option and maybe most simple, at T-stat set the ERV to run all the time, select no air handler to operate to assist. Then just place a switch on the control wire that signals the unit to come on.