I have a two story building sitting on a 26x36 monolitic slab built this way. All top soil removed, maybe 14 to 16 inches. Then compacted the soil. They about 9 inches of clean gravel added and compacted. Then moisture barrier of plastic. Then rebar and mesh and 7 inches of good grade concrete added. Then sealed with Thourglaze after cutting the concrete to avoid cracking.
Then three high split face blocks and 2x6 construction on the first floor. 2x10 on the second floor in a mansard style. Have a lean to in additon on one end and a raised two story deck on the other. The floor joist on the first floor are 2x10 and on the rafters on the second 2x8. All on 16 inch centers. On the first floor three 2x10s as a beam supporting the second floor on the length, two cross beams under that and those supported by steel posts.
It has been there 23 years and concrete and blocks are good, one hairline crack of about two feet. No heaving, spalling etc. Live in Ohio.
I would like now to turn it into a hunting/vacation cabin for the kids. Add water, electric, heat etc. Bedrooms on second floor for kids. Used occasionally.
Now need zoning permits. It appears they are concerned about frost heave. Never had any so far. Initially they say I will have to excavate the entire perimeter 32 inches deep and put foam insulation up against the same. I should have mentioned that the concrete is 7 inches everywhere except for deeper areas under where the steel supporting posts are.
I have concerns if I excavate to 32 inches the gravel will to some degree come out and leave the concrete to some degree unsupported at that point. It also will be considerable expense and difficult at the deck and somewhat at the lean to. Was wondering if horizontal foam of 6 inches thick might work and even that poses some problems if it has to be covered by 10 inches of dirt.
I would have thought once heat was added to the building there would be less chance of heaving but perhaps not and more.
I am not opposed to the thought of perimeter insulation being good but it will be a difficult procedure at best. Would prefer to use EPS (Exterior Poly Shield) vs. XPS if that is acceptable.
Just hoping there is some way to do this that will work and still meet code. It is an ag storage building now and needed no permits but does if there will be any human overnight use.
Thoughts or guidance are appreciated. Thanks
Then three high split face blocks and 2x6 construction on the first floor. 2x10 on the second floor in a mansard style. Have a lean to in additon on one end and a raised two story deck on the other. The floor joist on the first floor are 2x10 and on the rafters on the second 2x8. All on 16 inch centers. On the first floor three 2x10s as a beam supporting the second floor on the length, two cross beams under that and those supported by steel posts.
It has been there 23 years and concrete and blocks are good, one hairline crack of about two feet. No heaving, spalling etc. Live in Ohio.
I would like now to turn it into a hunting/vacation cabin for the kids. Add water, electric, heat etc. Bedrooms on second floor for kids. Used occasionally.
Now need zoning permits. It appears they are concerned about frost heave. Never had any so far. Initially they say I will have to excavate the entire perimeter 32 inches deep and put foam insulation up against the same. I should have mentioned that the concrete is 7 inches everywhere except for deeper areas under where the steel supporting posts are.
I have concerns if I excavate to 32 inches the gravel will to some degree come out and leave the concrete to some degree unsupported at that point. It also will be considerable expense and difficult at the deck and somewhat at the lean to. Was wondering if horizontal foam of 6 inches thick might work and even that poses some problems if it has to be covered by 10 inches of dirt.
I would have thought once heat was added to the building there would be less chance of heaving but perhaps not and more.
I am not opposed to the thought of perimeter insulation being good but it will be a difficult procedure at best. Would prefer to use EPS (Exterior Poly Shield) vs. XPS if that is acceptable.
Just hoping there is some way to do this that will work and still meet code. It is an ag storage building now and needed no permits but does if there will be any human overnight use.
Thoughts or guidance are appreciated. Thanks