NEC: 30" of clearance for electrical subpanel?

   / NEC: 30" of clearance for electrical subpanel? #1  

5030tinkerer

Gold Member
Joined
Dec 27, 2005
Messages
457
Location
Iowa
Tractor
Kubota GL3830/GL5030
I am installing a 100 amp subpanel in my home inside a kitchen pantry (no, nothing will be front of it...). Trouble is, I noticed that code says that I need 30" of side to side working space along with 36" deep of space - the wall where I want to put the subpanel is only 28" long. I am not an artist (and you'll have to ignore the dots - they are placeholders to hopefully help everything line up), but the room looks like:

┌───────┐
│           │
│...........│(subpanel on other side of this wall)
└─ .......─┘

entry ↑

hallway ↓
─────────────────────────

The lower right hand wall stub sticks out about 12" from the wall where the subpanel would be placed. Given that a subpanel user would easily have the required 30" (more like 72") width if you took the hallway width into consideration, am I okay codewise?
 
   / NEC: 30" of clearance for electrical subpanel? #2  
That 30" includes the width of the panel so if the panel is 20" wide then you need 5" on either side. So if your wall is only 28" wide then I would say you would not be in compliance with the NEC.
 

Attachments

  • workingclearances.jpg
    workingclearances.jpg
    20.7 KB · Views: 1,294

Tractor & Equipment Auctions

2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
2016 RAM 5500 Bucket Truck - Cummins Diesel - Auto Trans - 4X4 - Terex LT40 Boom (A55218)
2016 RAM 5500...
CATERPILLAR 255 SKID STEER (A52705)
CATERPILLAR 255...
New Holland TS 75 Front Loader Utility Tractor (A53421)
New Holland TS 75...
2005 TerraGator 8104 (A55301)
2005 TerraGator...
UNUSED IRANCH SEMI AUTOMATIC QUICK CHANGER (A54757)
UNUSED IRANCH SEMI...
 
Top