etpm
Veteran Member
So you already had 3 phase, just at a higher voltage. The transformers are not making 3 phase. I have a similar situation in my machine shop. The voltage runs right at the high limit and sometimes goes over. I make my own 3 phase with a rotary phase converter but it does nothing about the high voltage. One of my machines cannot tolerate the over voltage so the spindle drive kept shutting down. I installed a pair of buck/boost xmfrs wired in buck configuration to reduce the voltage to just the one machine. It no longer shuts down.The overhead 22kV line is 3 phase Delta, so with two transformers you get three phase out, but you only need two transformers. (One between A&B, one between B&C, which get you the three 240V Delta phases, two of which, A&B, are 120V to ground) It is called an open delta-open delta configuration. More here on slide #10.
You got it! The house has the two phases that are 240 to each other and 120 to ground. The three phase 240V runs the well to minimize power losses in getting the power to the submersed pump motor which is 600'+ from the pole.
All the best,
Peter
Eric