Ok, first post says galvanized and the second says cast iron- minor difference in the big picture but it helps me understand. I’m guessing the “rat” is the remodel. The 4” line could have been an old vertical stack that was later abandon in favor of the other vents- this probably occurred with the remodel.
With all those other vents on the roof this vent can’t be serving that much. Verify it’s not serving over 24 fixture units- that’s like 3 full bathrooms, a kitchen and laundry. Just google “plumbing fixture units” if you want to verify the numbers for each fixture. If it’s not over 24 units, cut the cast/galvanized pipe down in the crawl and run a 2” line to the roof from there. Since you have already done roofing I’d switch the roof jack to a 2” as well-going back to 4” isn’t code.
ABS or PVC is fine- I like ABS. Use the correct fittings- 4” no-hub coupling, little piece of 4” ABS, 4” ABS coupling, 4x2 ABS bushing reducer and away you go with the 2” ABS.
As a technicality- I believe your area is using UPC instead of IRC. They have a few differences regarding fixture units. They also have differences with AEVs and island vents. Some of that stuff is hard to change for the inspector.
Yep I mis-typed in the first post...the pipe is cast. I'm thinking i will replace with 4 inch where needed and do all venting with 2 inch. Those no hub couplings are pretty slick...I've used them before. Thanks for the advice.