Propane tank fitting

   / Propane tank fitting #1  

captainblackmer

New member
Joined
Jan 10, 2018
Messages
10
Location
Columbia Falls
Tractor
LS XG3140
I had a new 1000gal propane tank installed and need to be able to connect my dual fuel generator to it. My generator has a 0-200psi regulator built into it so the 10psi from the 1st stage is well within the means of my generator. Please see attached picture. I need to go from the 3/4" pipe to a QCC that grills use. Does anyone know what that fitting might be called or a link to one?

Any help is greatly appreciated!
 

Attachments

  • IMG_20180625_204345.jpg
    IMG_20180625_204345.jpg
    894.3 KB · Views: 126
   / Propane tank fitting #2  
We’d need to know the BTUs of the generator to properly size the QD. They aren’t all created equal. Most come as a matched set and they typically won’t have 3/4” threads. They will probably have 3/8 or 1/2” threads. The QDs should be UL listed for gas. They are a fairly common item.
 
   / Propane tank fitting #3  
Not trying to not pick but it looks like the install thus far needs some help. The galvanized fittings aren’t the best in a gas system (especially near the QD) and the black pipe should be painted.

In looking at that shutoff on the right a brass or stainless bushing reducer will get you from the 3/4” down to the 1/2 or 3/8” needed for the QD.
 
   / Propane tank fitting
  • Thread Starter
#4  
   / Propane tank fitting #5  
A Qd may not provide enough flow for your generator as most have a smaller orifice than the ID of the hose. What info on this is in the manual with it. You may need to review with the manufactuer of the generator.

I am getting ready to convert my 17.5 KW generator to NG. The kit, for the distance I have to run, takes a 1" pipe. Disconnect will be a union.

Ron
 
   / Propane tank fitting #6  
The manual doesn’t list the BTUs but I’m assuming it’s less than a BBQ- which is typically fairly high....watch me be wrong!
Anyway the “High Pressure” fittings is what you want. The “low pressure” fittings are only rated to 5 PSI.

Low & High Pressure Disconnect Hose, Quick Disconnect Female Socket & Male Plug

Good luck! Give these folks a call. They may have more info for you.
 
   / Propane tank fitting #7  
I had a new 1000gal propane tank installed and need to be able to connect my dual fuel generator to it. My generator has a 0-200psi regulator built into it so the 10psi from the 1st stage is well within the means of my generator. Please see attached picture. I need to go from the 3/4" pipe to a QCC that grills use. Does anyone know what that fitting might be called or a link to one?

Any help is greatly appreciated!

With your generator having a regulator designed to handle tank pressure have you considered that you might be better served by a dedicated high pressure line and connection for the generator and not tee'ing from your primary regulator.
 

Tractor & Equipment Auctions

(2) 200 Gallon Oil Tanks (A47369)
(2) 200 Gallon Oil...
2000 International 3800 Blue Bird School Bus (A46683)
2000 International...
1983 KENWORTH W900B TANDEM AXLE DAY CAB (A45676)
1983 KENWORTH...
Ver-Mac PCMS-3812 (A45336)
Ver-Mac PCMS-3812...
FLARE STACK (A47001)
FLARE STACK (A47001)
2013 Kia Optima SXL Sedan (A46684)
2013 Kia Optima...
 
Top