Question on a branch circuit

   / Question on a branch circuit #1  

lzicc

Platinum Member
Joined
Jul 20, 2009
Messages
723
Location
Pittsburgh, Pa
Tractor
Kubota B2650
I am going to be installing new LED shoplights in my garage. I am going to tap off a 20 amp plug circuit. Since these are for lights only, can I run 14/2 wire for the lights? Nothing else will be in the branch other than these LED shoplights.
 
   / Question on a branch circuit #2  
Although nothing you install will be, a circuit protected by a 20A breaker should have 12Ga wire downstream in case someone else taps off the branch you install
 
   / Question on a branch circuit
  • Thread Starter
#3  
If the end of the branch circuit ends inside the last shop light, I wouldn't think anyone would think about tapping into it. Is it safe if that is the case? I can use 12/2 wire, but it is so much thicker than 14/2 for lights, especially for LED shoplights since they are so narrow to begin with. I am going to be installing 4 of them on the same circuit and want to put them on a wall switch.
 
   / Question on a branch circuit #4  
Code requires 12awg wire if it is protected by a 20a breaker. If this is a code question, that's the answer.
If you are simply asking what will "work" I would only recommend following code as that is best accepted practice.
 
   / Question on a branch circuit #5  
Code requires 12awg wire if it is protected by a 20a breaker. If this is a code question, that's the answer.
If you are simply asking what will "work" I would only recommend following code as that is best accepted practice.

Correct: The code requires you protect #14awg wire with a 15 amp breaker
(read here)
even though it has a rated ampacity of either 20amps (w/ cable insulation
(read here)
and terminations having a 75 deg C rating), or
(read here)
25 amps (w/ 90 deg C rating).
(read here)
If you're adding (say) 360 Watts of LED lighting, the lights will draw 3 amps.
(read here)
People aren't going to explicitly advise you to ignore the code.
 
   / Question on a branch circuit #6  
You can change the breaker to 15 amps,, and use 14 gauge wire,,,
 
   / Question on a branch circuit #7  
Correct: The code requires you protect #14awg wire which has a rated ampacity of 20amps (if cable insulation
(read here)
and terminations have a 75 deg C rating), or 25 amps (if 90 deg C rated) with a 15 amp breaker.
(read here)
If you're adding (say) 360 Watts of LED lighting, the lights will draw 3 amps.

Not sure what where this is going. OP is talking 12/2 vs 14/2- these are common terms for what the code calls NM- commonly called Romex.

If OP turns this into another type of wire I'd be happy to offer advice about that. Until then it's 12/2.

Btw- don't forget OCPD min wire size in 240.4D. It's more than just the chart.......14awg copper- no matter the type- is 15a OCPD, 12awg- 20a etc
 
   / Question on a branch circuit #8  
Yes. The code requires you to use a 15 amp breaker to protect a cable that is likely rated for 25amps and may have a load of (say) 3 amps on it.
I don't disagree.

Why, did you read something else between the lines? ;)
 
   / Question on a branch circuit #9  
There is one loophole to the general rule that the wire has to be the same size throughout: the wire between an outlet and a device can be smaller.

Install an outlet box. Put a plug cord on the lights and plug it into the outlet.
 
   / Question on a branch circuit
  • Thread Starter
#10  
That is what I am thinking about doing.

There is one loophole to the general rule that the wire has to be the same size throughout: the wire between an outlet and a device can be smaller.

Install an outlet box. Put a plug cord on the lights and plug it into the outlet.
 

Tractor & Equipment Auctions

AGT MX-CRT23 (A46443)
AGT MX-CRT23 (A46443)
1989 Beall BA16 Pneumatic Dry Bulk Trailer (A46878)
1989 Beall BA16...
Woods BW15.60 15ft Batwing Mower (A46878)
Woods BW15.60 15ft...
Kivel 48in Pallet Fork Attachment (A47809)
Kivel 48in Pallet...
Dock-Master Pads (A47484)
Dock-Master Pads...
2025 Wolverine PFA-11-3300G Hydraulic Pallet Fork (A47484)
2025 Wolverine...
 
Top