Remote Fused Disconnect 'Melt Down'

   / Remote Fused Disconnect 'Melt Down' #11  
Re: Remote Fused Disconnect \'Melt Down\'

<font color="blue">I'm just curious what would draw 40-50 amps in a hot tub. </font>

Well, the combintaion of the pump and a 4500 plus watt heating element for one.
 
   / Remote Fused Disconnect 'Melt Down' #12  
Re: Remote Fused Disconnect \'Melt Down\'

A fault to ground will trip a fuse in a few seconds, even the slow blow type. That is not nearly enough time to cause a melt down of the connector block. It had to be a bad termination or a corroded termination due the chlorine content of the spa water.

Spa heaters draw a lot. 3000-4500 watts@230 volts is about 20 amps max. Not enough to cause a melt down of a connector. Unless the connector block is compromised with corrosion.
 
   / Remote Fused Disconnect 'Melt Down' #13  
Re: Remote Fused Disconnect \'Melt Down\'

<font color="blue"> Spa heaters draw a lot. 3000-4500 watts@230 volts is about 20 amps max. Not enough to cause a melt down of a connector. Unless the connector block is compromised with corrosion.
</font>

Don't forget to add the motors. My Hot Springs runs as many as 3 motors plus a heating element. One motor is very small, but 2 are probably 1.5 HP each. Those won't run unless its being used typically. If the spa is not protected by a GFI breaker(s), it would be a good time to consider changing out to such a setup <font color="red">if </font> it is approved to do so.
 
   / Remote Fused Disconnect 'Melt Down' #14  
Re: Remote Fused Disconnect \'Melt Down\'

One thing to check. If the "meltdown" was caused by a bad connection, the equipment could be undamaged...............chim
 
   / Remote Fused Disconnect 'Melt Down' #15  
Re: Remote Fused Disconnect \'Melt Down\'

</font><font color="blue" class="small">( Get the tub working again. Nothing like whiskey in the tub. )</font>


/forums/images/graemlins/confused.gif Whiskey in the tub? I don't get it - is it good for the skin or something? Do you just pour a bottle in the water or fill the tub with straight whiskey? Isn't that kind of expensive?

What would you use for a chaser? A beer shower?





/forums/images/graemlins/grin.gif
 
   / Remote Fused Disconnect 'Melt Down'
  • Thread Starter
#16  
Re: Remote Fused Disconnect \'Melt Down\'

Well, so may replies that I don't know where to start.

Here are some random responses:

<font color="blue"> Mrwurm; Was it the line or load side of the fuse that fried? </font>
I don't know if the meltdown occured on the line or load side.
The meltdown is confined to the immediate area around the switch blade contacts.

I have'nt pulled the pump out yet and I can't see the tag with the amp specs.

I wrestled the blades out and don't see any visible corrosion.

<font color="blue"> Sounds like your pump motor went to ground </font>
Well, there was recent event with a broken water fitting that soaked the motor controller area /forums/images/graemlins/confused.gif

I'm in Almont. About 90 miles from Monroe. Thanks for the
offer. My neighbor is retired IBEW member. The only way to NOT get his help is to work under the cover of darkness /forums/images/graemlins/grin.gif

And finally, if not sadly, I'm alergic to Whiskey /forums/images/graemlins/blush.gif
 
   / Remote Fused Disconnect 'Melt Down' #17  
Re: Remote Fused Disconnect \'Melt Down\'

Funny thing, we had a 20amp 250v twistlock cord connector on a table saw catch fire this morning here at work. Table saw was running and being used at the time and the breaker didn't trip and the saw kept running fine til the point where the guy ran over and shut the breaker off. I found a loose connection in the clamping mechanism on one terminal and the other wire was almost burnt off on the other terminal. Saw is still running fine as we speak.

Steve
 
   / Remote Fused Disconnect 'Melt Down' #18  
Re: Remote Fused Disconnect \'Melt Down\'

Sounds like a meltdown form resistance in the blade contacts area. I would replace the disconnect and see what happens. All else might be ok.
Ben
 
   / Remote Fused Disconnect 'Melt Down' #19  
Re: Remote Fused Disconnect \'Melt Down\'

"Whiskey in the tub? I don't get it - is it good for the skin or something? Do you just pour a bottle in the water or fill the tub with straight whiskey? Isn't that kind of expensive?"

OK, whiskey in a glass while sitting in the tub. I only wish I could bathe in the stuff.

Allergic to whiskey? Oh the shame. Almost as bad my living on the puget sound and being allergic to fish.
 
   / Remote Fused Disconnect 'Melt Down' #20  
Re: Remote Fused Disconnect \'Melt Down\'

Like inspector said:

meltdown is more likely from a LOOSE connection, which lets it start to ARC, (albeit very small arcs,) it does not take long to melt stuff even old bake-a-lite controls plastic which is high temp stuff. I would ohm out the motor & heating elements to check them out before simply assuming that the pump died. anyhow if the blade on the disconnect was bumped and pulled slightly out that also will over heat the disconnect. I've been in industrial electricity for years and seen some good ole melt downs, speaking of hich our transformer that powers the indictatherm smelting furnace blew up and caused a nice power outage the other night /forums/images/graemlins/blush.gif only a 100K buck unit hooked dirrectly to the power grid main lines. took out 3/4 of ashland, wanne & richland counties power for a while... /forums/images/graemlins/frown.gif

MakrM
 

Tractor & Equipment Auctions

2015 Kubota KX91-3S2 Mini Excavator (A52377)
2015 Kubota...
2014 Jeep Patriot SUV (A53424)
2014 Jeep Patriot...
2019 FREIGHTLINER M2 26FT NON CDL BOX TRUCK (A54607)
2019 FREIGHTLINER...
2017 GMC SIERRA 1500 (A53843)
2017 GMC SIERRA...
2012 BMW 328i Sedan (A53424)
2012 BMW 328i...
2013 INTERNATIONAL PAYSTAR DAY CAB ROAD TRACTOR (A51406)
2013 INTERNATIONAL...
 
Top