How sensitive should the thermostat in the house be? We hired a guy to replace it a few months ago and noticed the temperature never changes. We have a propane fired forced air furnace with central air. The furnace/air-conditioner runs for a very short period of time but it runs many more times per day. It has less than one degree difference from demand to satisfied. Every thermostat I have seen would demand at say, 69 and was satisfied as soon as it reached 71. That's one full degree difference.

The new one has (guessing) half a degree from demand to satisfied.

Is this the best economical way to run a furnace and central air conditioner? Does it cause more wear & tare this way?
 
   / Sensitive thermostat #2  
How sensitive should the thermostat in the house be? Don't know.
Is this the best economical way to run a furnace and central air conditioner? No.
Does it cause more wear & tear this way: Yes.

This range is also referred to as "deadband" and/or "hysteresis". In some thermostats it can be adjustable.
It is probably a little more economical for your furnace to run at operating temp longer than short cycling, and definitely a lot less wear and tear if it's only starting and stopping, heating (expanding) and cooling (contracting) fewer cycles.
 
   / Sensitive thermostat #4  
I generally go no more than 2 degrees in commercial buildings between heat and cool... generally have to make major adjustment twice... going into heating season and going into cooling season.

The reality is many buildings have heat loads and the hospital is no different in the office/administration areas... heat may not be called for all summer and fall...

Neighbor had a new system and it was always on/off... made a change to the blower and heating stages and now it cycles less... biggest change was keeping the blower on low setting to keep air moving which helps to keep it more even temp wise and filtered.
 
   / Sensitive thermostat
  • Thread Starter
#5  
   / Sensitive thermostat
  • Thread Starter
#6  
Update;

Our HVAC guy came out today and changed thermostats. The first new one's deviation was not programmable. It was factory set at .4 degrees. The new one is set at 1 degree. It should be much more economical to run.
 

Tractor & Equipment Auctions

Air Reel (A50774)
Air Reel (A50774)
2015 Ford F-550 4x4 Knapheide Service Truck (A51692)
2015 Ford F-550...
New Holland 939 3 Row Corn Head (A50774)
New Holland 939 3...
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
(10) 28' Continuous Fencing Panels (A50515)
(10) 28'...
2018 FREIGHTLINER CASCADIA TANDEM AXLE SLEEPER (A52577)
2018 FREIGHTLINER...
 
Top