So, I'm trying to figure out my needs for a potential power outtage, my home is completely electric (house is electric heat pump). I have a small studio in the barn which is heated with a PTAC (thru the wall motel ac/heater). Given the amount of power needed to heat the main house, we'll just move into the studio for a power outtage. My plan at this point is a gasoline portable generator, will make an extension cord for the PTAC (it plugs into an outlet now) and run a couple of 120V extension cords for other stuff. Will have to haul water as the well pump is on the main house panel. My question is the PTAC- it's a heat pump with about a 1500W running but has a 5KW auxillary heater which is what would be most likely running. Rule of thumb suggests 3X running load for startup, but this wouldn't apply to the auxillary heater would it (resistive load)? I'm hoping I can get a genny in the 6500-7500 W range to run stuff- any idea if I'd need moore than the 5000W for the PTAC unit?